Old 12-07-10, 02:28 PM   #391
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by dremd View Post
Mad congrats on the leak free loop field!

How about hooking It up to your sanyo for temporary use?
Thanks for the congrats!

Even easier than the Sanyo is the homemade heat pump I already built...


I just need to check it to see if it is still working. I was pretty low on the learning curve when I built it, and it may need to be re-charged.

More soon...

-AC_Hacker

AC_Hacker is offline   Reply With Quote
Old 12-07-10, 02:42 PM   #392
Daox
Administrator
 
Daox's Avatar
 
Join Date: Aug 2008
Location: Germantown, WI
Posts: 5,525
Thanks: 1,162
Thanked 374 Times in 305 Posts
Default

Congrats on the successful test AC Hacker! Thats a LOT of hard work validated.
__________________
Current project -
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.



To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
&
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
Daox is offline   Reply With Quote
Old 12-07-10, 03:31 PM   #393
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by dremd View Post
Mad congrats on the leak free loop field!

How about hooking It up to your sanyo for temporary use?
Thanks for the congrats!

Even easier than the Sanyo is the homemade heat pump I already built...


I just need to check it to see if it is still working. I was pretty low on the learning curve when I built it, and it may need to be re-charged.

More soon...

-AC_Hacker
AC_Hacker is offline   Reply With Quote
Old 12-07-10, 03:42 PM   #394
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by Daox View Post
Congrats on the successful test AC Hacker! Thats a LOT of hard work validated.
...indeed, a lot of hard work...


And thank YOU for seeing this meandering odyssey through.

...but wait! There's more to come!

(* ...to be continued... *)

-AC_Hacker
Attached Thumbnails
Click image for larger version

Name:	odyssey.gif
Views:	3507
Size:	75.5 KB
ID:	1125  

Last edited by AC_Hacker; 12-07-10 at 03:45 PM..
AC_Hacker is offline   Reply With Quote
Old 12-07-10, 06:19 PM   #395
dremd
Need More Eco
 
dremd's Avatar
 
Join Date: Sep 2008
Location: Scott, La
Posts: 172
Thanks: 2
Thanked 6 Times in 6 Posts
Send a message via AIM to dremd
Default

But wont that require you installing pex in your floors, or am I missing something?

I sooooo appreciate your work on this project, I hope to do similar myself (but mostly for cooling)
dremd is offline   Reply With Quote
Old 12-07-10, 07:49 PM   #396
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by dremd View Post
But wont that require you installing pex in your floors, or am I missing something?
I was initially opposed to radiant floor heating because forced air is so widespread and it works well. Then I started studying radiant floor heating and I learned that it is better for several reasons:
  • Because it utilizes the principle of radiation, temperature stratification is greatly reduced. This solves the problem of too-hot air at the ceiling and too-cold air at the floor.
  • Because people need more heat when they are relaxing and 'laying about', radiant-floor heat is advantageous because the heat source (the floor) is closer to where people are when they need the most heat.
  • Because heat pumps reach greater efficiency when the difference (AKA: delta T) between the source temperature (ground loop) and the sink temperature (temperature of the water in the floor loop) is smaller. With a radiant floor heating system, the radiating area is very large, so the temperature of the water in the loop can be lower to achieve the required heat output. For instance, a working fluid temperature of around 90 degrees or even lower, is common for working fluid in floors, while working fluid temperatures of 120 and greater is common for working fluid temperatures in forced air heat exchangers.

The reduced delta-T issue and heat pumps is at play when you do a ground source heat pump. It is also at play when you do a radiant floor.

So, yes I have been planning to do a radiant floor all along.

It's not going to be easy, because I live in a very old house and a two-inch thick concrete suspended floor is just not in the cards. But I am looking into ways of getting a high efficiency floor that doesn't weigh as much as two inches of concrete.

Right now, I'm favoring a built-up floor made of layers of Wonderboard brand tile-backer board. I have done some preliminary tests on various materials and Wonderboard looks better than Durock and Hardybacker board.

I have also done some experiments with unusually high thermal transfer aggregate for concrete, but so far, no love. Nevertheless I still think it has promise.

AC_Hacker
AC_Hacker is offline   Reply With Quote
Old 12-08-10, 07:01 PM   #397
pick1e
Helper EcoRenovator
 
Join Date: Nov 2010
Location: Michigan, USA
Posts: 57
Thanks: 0
Thanked 0 Times in 0 Posts
Default

Quote:
Originally Posted by AC_Hacker View Post
Bathroom & kitchen remodel, it is mentioned in the thread.
I remember now, sorry. The thread is long. I thought you had your floor loops installed.

I didn't see you mention how you were calculating your CoP in that graph. Can you explain it a little more as far as where your sensors were, etc.

Also if you separated the data into different graphs I think it would be more accurate i.e. when you multiply your COP by 10 you also multiply error by 10. If you still have your original data I would be interested to see them separated and axes identified, I for one would find it much more informative.

Last edited by pick1e; 12-08-10 at 08:22 PM..
pick1e is offline   Reply With Quote
Old 12-09-10, 11:21 AM   #398
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by pick1e View Post
I remember now, sorry. The thread is long. I thought you had your floor loops installed.

I didn't see you mention how you were calculating your CoP in that graph. Can you explain it a little more as far as where your sensors were, etc.

Also if you separated the data into different graphs I think it would be more accurate i.e. when you multiply your COP by 10 you also multiply error by 10. If you still have your original data I would be interested to see them separated and axes identified, I for one would find it much more informative.
The test and the graph produced by the test was meant as a first-pass test-of-concept. For that reason alone I'm not inclined to de-construct the entire methodology.

Quote:
My burden is heavy, my dreams are beyond control.
-Bob Dylan, Dear Landlord
> ...how you were calculating your CoP...

COP is energy out divided by energy in.
You will need to capture the amount of energy going into your system.

You will also need to capture the amount of energy coming out of your system.

...then divide the latter by the former.
If you want specific assistance in setting up your own test, please tell me exactly what you need to know in order to proceed, and I'll try to assist.

I wish you the best in your own project, don't forget the photographs.

-AC_Hacker

Last edited by AC_Hacker; 12-09-10 at 11:46 AM..
AC_Hacker is offline   Reply With Quote
Old 12-09-10, 07:04 PM   #399
pick1e
Helper EcoRenovator
 
Join Date: Nov 2010
Location: Michigan, USA
Posts: 57
Thanks: 0
Thanked 0 Times in 0 Posts
Default

Quote:
Originally Posted by AC_Hacker View Post
The test and the graph produced by the test was meant as a first-pass test-of-concept. For that reason alone I'm not inclined to de-construct the entire methodology.



> ...how you were calculating your CoP...

COP is energy out divided by energy in.
You will need to capture the amount of energy going into your system.

You will also need to capture the amount of energy coming out of your system.

...then divide the latter by the former.
If you want specific assistance in setting up your own test, please tell me exactly what you need to know in order to proceed, and I'll try to assist.

I wish you the best in your own project, don't forget the photographs.

-AC_Hacker
Please don't be so defensive, I'm simply being curious.

I would be neat to use your test results as a baseline comparison for my setup when I get there. But it's impossible to compare when I don't know what exactly you were testing. Looking at some dots on a graph doesn't tell me a lot if I don't know what it represents.

I understand that "heat" and "chill" were temperature measurements of the two barrels. I have only guessed that "LS temp" and "HS temp" were readings at the heat exchangers, "HS press" and "LS press" were refrigerant pressures at the heat exchangers, and "super heat" and "sub cool" were measurements of the water leaving the exchangers but before mixing with the barrel water.

And for COP I assume you were using a temperature approximation (Th/(Th-Tc) and not volumetric heat gain/loss, but I have no idea whether you were using the barrel temps or the heat exchanger temps or pre-barrel output temps, etc.

If you could elucidate that would be helpful/informative.
pick1e is offline   Reply With Quote
Old 12-09-10, 07:52 PM   #400
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by pick1e View Post
I understand that "heat" and "chill" were temperature measurements of the two barrels.
That is correct, I had thermometers in the water of both barrels. Since the water was vigorously swirling, I assumed uniform temperature.

Quote:
Originally Posted by pick1e View Post
I have only guessed that "LS temp" and "HS temp" were readings at the heat exchangers
LS temp was measured on the 'Low Side' (cold side) refrigerant line coming from the evaporation heat exchanger. HS Temp was measured on the 'High Side' (hot side) refrigerant line coming from the condensing heat exchanger. These values were used to calculate Sub Cooling and Super Heating, respectively.

Quote:
Originally Posted by pick1e View Post
"HS press" and "LS press" were refrigerant pressures at the heat exchangers
Yes, I kept my manifold gauges attached when I ran the tests, and recorded the readings every five minutes.

Quote:
Originally Posted by pick1e View Post
and "super heat" and "sub cool" were measurements of the water leaving the exchangers but before mixing with the barrel water
No, this is not correct. I used the 'LS press' reading to refer to a PT chart for R-290 to see what the temperature should have been at that particular pressure (actually I did a curve fit on the PT chart for R-290 and derived the formula for the entire PT chart in order to save myself from interpolating every value). Then I subtracted the actual temperature from the calculated temperature to determine Sub Cooling.

Ditto Super Heating. I derived values for Sub Cooling and Super Heating, to be used in system tuning. Since the only fine adjustment I could make was refrigerant pressure. I used an excessively high Sub Cooling value to discover that I needed to lower my refrigerant pressure. I did adjust that, and the efficiency increased accordingly.

Quote:
Originally Posted by pick1e View Post
And for COP I assume you were using a temperature approximation (Th/(Th-Tc) and not volumetric heat gain/loss, but I have no idea whether you were using the barrel temps or the heat exchanger temps or pre-barrel output temps, etc.
Not quite. I used a power meter to determine power into the compressor for each time interval. I also knew the volume, and thus the weight of the water for each time period. Knowing this and knowing the temp change per period, I could calculate the power that was causing the change.

Then COP = power-out / power-in

I calculated this for each time interval.

-AC_Hacker


Last edited by AC_Hacker; 12-09-10 at 08:03 PM..
AC_Hacker is offline   Reply With Quote
Reply


Tags
air conditioner, diy, gshp, heat pump, homemade


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments