Whoo! What an added wrench thrown into the works with the DHW option!

OK, so with the previous design considerations, you have a lineset running into your equipment closet that is being used as-is right now. The air handler has its own metering device indoors connected the coil with a check valve. Due to site constraints, it was decided not to mess with existing runs of water or refrigerant lines. All the mods can be done outdoors, where the outdoor unit sits. You also have your DX loop and compressor for the HPWH situated right next to where the HVAC unit is now.

As far as DHW being generated off of the GSHP, the simplest and most reliable method would be a desuperheater HX in between the compressor discharge and the reversing valve. That way, it is always heating, regardless of mode, without extra components. The main issue with this approach is now you have two heating loops that have to run through the water heater. It doesn't matter whether you use a refrigerant-to-water exchanger at the GSHP or at the tank, you would still have to run some sort of piping to the tank.This translates to heat loss of some sort.

Also, the little DX rig seems to be serving you well in its current configuration. The added water heating loop would definitely have an effect on that system, and would vary between heating and cooling modes of the GSHP. Also translates to heat loss somewhere.

jeff5may is offline   Reply With Quote
Old 02-25-16, 03:58 PM   #212
MEMPHIS91
Journeyman EcoRenovator
 
MEMPHIS91's Avatar
 
Join Date: Apr 2015
Location: Oxford, MS USA
Posts: 496
Thanks: 69
Thanked 87 Times in 61 Posts
Default

Yes I will be changing out the cap tubes in the existing air handler with a TXV. So all the work can be done outside. Meaning I will have to insulate the water coils outside.

So maybe the water heater idea is too much? I guess if the house thermostat didn't call for heat for a few days I would have to add a call in from the water heater to turn the compressor on at like 35%. Maybe I should just stay with what I got.

Thanks Jeff
__________________
שְׁמַע יִשְׂרָאֵל ה' אֱלֹהֵינוּ ה' אֶחָד
MEMPHIS91 is offline   Reply With Quote
Old 10-18-16, 12:16 PM   #213
lubaka
Lurking Renovator
 
Join Date: Oct 2016
Location: Bulgaria
Posts: 4
Thanks: 0
Thanked 2 Times in 2 Posts
Default

Hello! The heat pump is 1ton.
Drilling 36 meters.
The heat pump is factory production.
What should be the diameter of the two tubes in dry drilling?
lubaka is offline   Reply With Quote
Old 10-18-16, 12:25 PM   #214
lubaka
Lurking Renovator
 
Join Date: Oct 2016
Location: Bulgaria
Posts: 4
Thanks: 0
Thanked 2 Times in 2 Posts
Default

Quote:
Originally Posted by lubaka View Post
Hello! The heat pump is 1ton.
Drilling 36 meters.
The heat pump is factory production.
What should be the diameter of the two tubes in dry drilling?
DX cooper pipe?
lubaka is offline   Reply With Quote
Old 10-18-16, 04:32 PM   #215
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

lubaka,
Welcome to the forums!

Check out the document in this post:

http://ecorenovator.org/forum/45385-post116.html

In that thread, Memphis used 1/4 inch tubing in a 30 foot borehole. Barely big enough for a 4000 BTU rig. Still works like magic after thousands of hours worth of hot water production.

Last edited by jeff5may; 10-19-16 at 07:46 AM..
jeff5may is offline   Reply With Quote
Old 10-19-16, 04:36 AM   #216
lubaka
Lurking Renovator
 
Join Date: Oct 2016
Location: Bulgaria
Posts: 4
Thanks: 0
Thanked 2 Times in 2 Posts
Default dx heat pump pipe

This is my machine.
Is it suitable for vertical mounting of the copper pipe?
Do I need a special model for vertical mounting in drilling?
The instruction stated only horizontal installation in three circuits 60 m / 196 ft / tube 3/8.
I suggest tube 3/8 liquid and 1/2 for returning gas to the machine / two tubes in drilling /.
In the uploaded file I did not see anything about DX installation?
Thanks!
Attached Thumbnails
Click image for larger version

Name:	eco natura 1.jpg
Views:	574
Size:	237.6 KB
ID:	7315   Click image for larger version

Name:	eco natura 2.jpg
Views:	551
Size:	248.2 KB
ID:	7316  

Last edited by lubaka; 10-19-16 at 07:23 AM..
lubaka is offline   Reply With Quote
The Following User Says Thank You to lubaka For This Useful Post:
stevehull (10-19-16)
Old 10-19-16, 04:44 AM   #217
lubaka
Lurking Renovator
 
Join Date: Oct 2016
Location: Bulgaria
Posts: 4
Thanks: 0
Thanked 2 Times in 2 Posts
Default

Instructions GSHP
Attached Files
File Type: pdf avis technique Eco.pdf (318.6 KB, 748 views)
lubaka is offline   Reply With Quote
The Following User Says Thank You to lubaka For This Useful Post:
jeff5may (05-18-19)
Old 05-14-19, 07:04 AM   #218
Fordguy64
Journeyman EcoRenovator
 
Join Date: Oct 2011
Location: Cincinnati ohio
Posts: 338
Thanks: 40
Thanked 35 Times in 31 Posts
Default

http://earthlinked.com/technical-man...234dd66ca5c800

found this interesting related to dx systems

hopefully it hasent already been posted in this thread, its been a while since i have read it
Fordguy64 is offline   Reply With Quote
The Following User Says Thank You to Fordguy64 For This Useful Post:
jeff5may (05-18-19)
Old 05-29-19, 04:50 PM   #219
kiromaru
Lurking Renovator
 
Join Date: May 2019
Location: cilacap
Posts: 1
Thanks: 0
Thanked 0 Times in 0 Posts
Default

I have a packless 5T coaxial. I can measure for you this weekend if you like, but I'm guessing it's probably 20' if unrolled. My suggestion is go as big as you can....monster size if possible. You can always pump the water through slower if you need to, enjoying the lower pump amp draw.

kiromaru is offline   Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 09:06 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design