07-18-16, 05:52 PM | #1 |
Lex Parsimoniae
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
|
Santa Fe Classic Dehumidifier
This looks like the perfect unit for my basement!
Buy Santa Fe Classic Basement & Whole House Dehumidifier (4029700) | Thermastor 4029700 Capacity @ AHAM: 110 Pints/Day Capacity @ Saturation: 180 Pints/Day Amp Draw: 6.4 Amps CFM: 275 CFM Operating Temp. Range: 56° - 95°F Wow! Listed at $1,671.00 Got it off craigslist for $100 See: http://ecorenovator.org/forum/sale-t...list-used.html It seems to be working Okay. In ideal conditions, it pumped a cup of water in about 35 minutes. After I install some filters, I'll give it a good test run.. It does use about 6.4 Amps at 120vac..
__________________
My hobby is installing & trying to repair mini-splits EPA 608 Type 1 Technician Certification ~ 5 lbs or less.. Last edited by Xringer; 07-18-16 at 06:49 PM.. |
07-18-16, 06:39 PM | #2 |
Super Moderator
Join Date: Jun 2013
Location: SC
Posts: 2,923
Thanks: 172
Thanked 564 Times in 463 Posts
|
Great deal.
__________________
Current project Aquaponics system , Passive Solar Greenhouse build To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts. Solar Install 12.5 Kwh- To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts. Mini Split installs - To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts. EV Chevy Volt - To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts. |
07-19-16, 11:28 PM | #3 |
Supreme EcoRenovator
|
Gut shots? Or did it already get installed somewhere?
|
07-20-16, 12:55 AM | #4 |
Lex Parsimoniae
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
|
I think it's a 6 or 7 years old. Recently replaced. No explanation of why..
But, when I did a short test the day of delivery, it was idea weather for a test. Raining & 80F. in an open garage. Looking at the amount of water that came out. I estimate 1/2 quart per hour. (or less). Spec says under idea conditions, 2 quarts per hour. On some of the reviews I've seen, there were owners saying that refrigerant slowly leaked out. (4 or 5 years) I hope that's all that's wrong with this one.Hope it just needs a shot of R410A.. Planning to test some more when I get some air filters. Noticed the compressor got really hot. Wondering what the normal operating temperature is.?.
__________________
My hobby is installing & trying to repair mini-splits EPA 608 Type 1 Technician Certification ~ 5 lbs or less.. |
07-21-16, 03:05 PM | #5 |
Lex Parsimoniae
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
|
The maintenance port is out on a thin tube..
I can see how it might get broke off when removing the cap..
__________________
My hobby is installing & trying to repair mini-splits EPA 608 Type 1 Technician Certification ~ 5 lbs or less.. |
07-23-16, 06:05 PM | #6 |
Lex Parsimoniae
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
|
Pressure test?
If I put a gauge on the low pressure port while the unit is running, I should see about 240 PSI?
Or, is that the Max pressure? On a mini-split, it seems like 130-140 PSI is common..
__________________
My hobby is installing & trying to repair mini-splits EPA 608 Type 1 Technician Certification ~ 5 lbs or less.. |
07-25-16, 02:12 PM | #7 |
Lex Parsimoniae
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
|
Kinda working..
I'm not so sure.. I found a user that's had a lot of problems with this model..
Sante Fe Classic Quality Issues He's included five links to YouTube videos in his posts.. Mine seems to be working poorly. Only getting about a quart during a 1 hour run.. Temp 70F with RH between 60 & 70 percent. I'm wondering if a Superheat test could tell me anything.. First, I'll have to find out what the 'standard' Superheat temperature is for this model. At 70F & 70%RH.. ~~~~ After a 1/2 hour warm up, I did a little testing of the input air vs the output air. Input air was 62%RH @ 73deg Output was 38%RH @ 82deg A change of 24%RH & 9 deg.
__________________
My hobby is installing & trying to repair mini-splits EPA 608 Type 1 Technician Certification ~ 5 lbs or less.. Last edited by Xringer; 07-25-16 at 07:20 PM.. Reason: add photo |
07-30-16, 02:56 PM | #8 |
Apprentice EcoRenovator
Join Date: Apr 2012
Location: Phillips, WI
Posts: 109
Thanks: 10
Thanked 30 Times in 25 Posts
|
Maybe I'm lucky or something, but we bought a Thermastor Santa Fe Classic dehumidifier in 2003. We put it in the living room to use as a whole house dehumidifier in summer. It's been working perfectly ever since.
The house temperature is typically 75 to 80 deg F, humidity 45 to 50%. The house is well insulated, so we rarely use the AC. Also, the AC does not do a good job of removing moisture. My wife likes it dry, sometimes the humidity gets down to 40%. |
07-30-16, 03:10 PM | #9 |
Lex Parsimoniae
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
|
Wow! That sounds like money well spent.
Is it a R22 or R401a version? I'm also very interested in the temperature of the input air, vs the output air. I think it might be a quick way to determine the correct refrigerant load. If I can get this one working to spec, it would be fantastic for our musky basement..
__________________
My hobby is installing & trying to repair mini-splits EPA 608 Type 1 Technician Certification ~ 5 lbs or less.. |
07-31-16, 09:15 PM | #10 |
Apprentice EcoRenovator
Join Date: Apr 2012
Location: Phillips, WI
Posts: 109
Thanks: 10
Thanked 30 Times in 25 Posts
|
The nameplate says R22. It's running right now. The room temperature is 76 deg F, 53% RH, outlet temperature is 100 deg F. The outlet temperature reading may be a little low, it's a cheap little thermometer laying on the floor.
|
|
|