Default Enphase microinvertors (M215) question

Not sure where to ask this, but here it goes.

How many Enphase microinvertors (M215) can be put on a string. I see 17 are listed, but this is for a 20 A circuit breaker.

I am needing about 40 panels for a 10 kW system with two rows of portrait panels (each row 20 panels).

Can I do a 30 amp breaker, use a larger wire gauge and put 20 invertors on a string?


Thanks,


Steve

__________________
consulting on geothermal heating/cooling & rational energy use since 1990
stevehull is offline   Reply With Quote
Old 12-01-13, 01:55 PM   #2
pinballlooking
Super Moderator
 
pinballlooking's Avatar
 
Join Date: Jun 2013
Location: SC
Posts: 2,923
Thanks: 172
Thanked 564 Times in 463 Posts
Default

Quote:
Originally Posted by stevehull View Post
Not sure where to ask this, but here it goes.

How many Enphase microinvertors (M215) can be put on a string. I see 17 are listed, but this is for a 20 A circuit breaker.

I am needing about 40 panels for a 10 kW system with two rows of portrait panels (each row 20 panels).

Can I do a 30 amp breaker, use a larger wire gauge and put 20 invertors on a string?


Thanks,


Steve
It would be best to start your own post for this question.

Here is the data sheet for them M215
http://enphase.com/global/files/M215_DS_EN_60Hz.pdf

No you cannot put 20 M215 and use a larger breaker.

Each M215 is .9 amps you can have not more than 17 going to a 20 amp breaker.

These docs give you the voltage rise.
http://enphase.com/global/files/Enph...tions_M215.pdf
http://enphase.com/global/files/Enph...Vdrop_M215.pdf
You usually end up breaking up the 17 run in smaller groups (they call this center feeding) then going to a Jbox then take that wire to the 20 amp breaker.

Here are two diagrams one is for 40 modules using four 15 amp breakers.
The other is 50 modules using two 20 amp breakers and two 15 amp breakers.
Attached Thumbnails
Click image for larger version

Name:	dig.JPG
Views:	1589
Size:	117.3 KB
ID:	3730   Click image for larger version

Name:	dig2.JPG
Views:	6836
Size:	121.5 KB
ID:	3731  

Last edited by pinballlooking; 12-02-13 at 12:33 AM..
pinballlooking is offline   Reply With Quote
Old 12-01-13, 08:02 PM   #3
Mikesolar
Master EcoRenovator
 
Mikesolar's Avatar
 
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
Default

Quote:
Originally Posted by pinballlooking View Post
It would be best to start your own post for this question.

Here is the data sheet for them M215
http://enphase.com/global/files/M215_DS_EN_60Hz.pdf

No you cannot put 20 M215 and use a larger breaker.

Each M215 is .9 amps you can have not more than 17 going to a 20 amp breaker.

These docs give you the voltage rise.
http://enphase.com/global/files/Enph...tions_M215.pdf
http://enphase.com/global/files/Enph...Vdrop_M215.pdf
You usually end up breaking up the 17 run in smaller groups (they call this center feeding) then going to a Jbox then take that wire to the 20 amp breaker.
The Canadian and, I think the NEC, calls for the total amperage X 1.25 to give you wire and therefore fuse size so .9 X 17=15.3 x 1.25 (safety factor) = 19.125A. All our wiring must have the 25% safety.
Mikesolar is offline   Reply With Quote
Old 12-02-13, 12:23 AM   #4
pinballlooking
Super Moderator
 
pinballlooking's Avatar
 
Join Date: Jun 2013
Location: SC
Posts: 2,923
Thanks: 172
Thanked 564 Times in 463 Posts
Default

Yes the NEC requires the same here.The Enphase trunk cable is not rated for more than that.That is the limiting factor that keeps you only having 17 microinverters with M215 and you showed the math why you need a 20 amp breaker.
pinballlooking is offline   Reply With Quote
Old 12-02-13, 06:28 AM   #5
stevehull
Steve Hull
 
Join Date: Dec 2012
Location: hilly, tree covered Arcadia, OK USA
Posts: 826
Thanks: 241
Thanked 165 Times in 123 Posts
Default

Got it. The Enphase TRUNK cable is limited, not physical issues other than that.

Given that, what would your recommendations be for the maximum number of inverters per string?

TIA,

Steve
__________________
consulting on geothermal heating/cooling & rational energy use since 1990
stevehull is offline   Reply With Quote
Old 12-02-13, 08:04 AM   #6
gasstingy
Journeyman EcoRenovator
 
Join Date: Feb 2010
Location: Arab, AL
Posts: 491
Thanks: 109
Thanked 49 Times in 43 Posts
Default

You may also want to check and see how many inverters Enphase says the EMU will accommodate. When I bought mine, my EMU manual said it could only handle a string of 14. That was from early 2009.
gasstingy is offline   Reply With Quote
Old 12-02-13, 08:12 AM   #7
pinballlooking
Super Moderator
 
pinballlooking's Avatar
 
Join Date: Jun 2013
Location: SC
Posts: 2,923
Thanks: 172
Thanked 564 Times in 463 Posts
Default

I would max out each run I did not do that and when and if you upgrade it will help if you max each run.
But I would center feed so there is no more than 5 micreinverters before being tied into a Jbox this keeps the voltage rise lower. How far away it your array going to be from your house?
I put in 40 modules thinking I would never put more in but it soon wanted to zero out and added more solar quickly.
The EMU can handle 17 per run with the M215

Last edited by pinballlooking; 12-02-13 at 08:22 AM..
pinballlooking is offline   Reply With Quote
Old 12-08-13, 05:31 PM   #8
where2
DIY Geek
 
Join Date: Apr 2013
Location: Sunny Florida
Posts: 401
Thanks: 74
Thanked 83 Times in 73 Posts
Default

I designed my system with two trunks. Each trunk has 10 inverters. My goal was to fit 20 inverters and panels on my second floor roof, and this was the most efficient method to get to that goal. I considered center feeding since I had a gap between a group of 6 panels and a group of 4 panels in a row (had to avoid a plumbing vent stack). I weighed the pro's and con's and finally decided against center feeding since the best logical location for my weather head and roof penetration was at the upper left corner of the array.

My run from the second floor attic to the combiner panel on the back of the house is all #10AWG UF. Inside a junction box in the attic, I transition from #10 AWG UF to a #12 AWG 4-conductor TCER cable to go up the weather head to a custom Hubbell-Weigman trunk cable termination panel on the roof. At that point, I transition to the #12 AWG Enphase trunk cable.

Looking at my graphs from today, a couple of my inverters saw 252v AC today. No error messages about the voltage, and it didn't correspond with peak panel output.

where2 is offline   Reply With Quote
Reply



Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 08:24 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design