EcoRenovator  

Go Back   EcoRenovator > Improvements > Renovations & New Construction
Advanced Search
 


Blog 60+ Home Energy Saving Tips Recent Posts


 
 
Thread Tools Display Modes
Prev Previous Post   Next Post Next
Old 06-09-20, 02:21 PM   #1
rvCharlie
Lurking Renovator
 
Join Date: Jul 2013
Location: central MS
Posts: 23
Thanks: 2
Thanked 3 Times in 3 Posts
Default Conventional a/c compressor: sump heater question

Hi,

Hoping this is the right subforum to ask this question.

Background: TraneTTX036C100A1 a/c Compressor tripped its mains circuit breaker yesterday.

Troubleshooting: After a a bit of brute force troubleshooting (disconnected all 3 compressor leads from contactor/capacitors, and disconnected one end of the outdoor fan), The unit still tripped the mains CB. Swapped the feed to my other a/c's same-size CB. Took slightly longer to trip, and I could hear a very short 'grunt' from the compressor (on the other side of the house), before the CB tripped. Walked back to the compressor, and some magic smoke had obviously been let out of something... Only thing left was the 'sump htr' circuit, which always has power available when mains supply is hot.

Temporary fix: Disconnected both leads that feed the sump heater circuit, and reconnected everything else. Compressor now runs fine.

Question: Have any of you a/c gurus ever seen a sump heater circuit fail in a dead short mode?

Extra credit: Any danger in operating the unit as-is, until I can obtain a new heater? I'm in MS (USA) and night time temps this time of year won't drop much lower than the thermostat on-point of 73 degrees.

Thanks,

Charlie

rvCharlie is offline   Reply With Quote
 


Tags
compressor, out door unit, sump heater


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 07:42 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design