EcoRenovator  

Go Back   EcoRenovator > Improvements > Solar Power
Advanced Search
 


Blog 60+ Home Energy Saving Tips Recent Posts


Reply
 
Thread Tools Display Modes
Old 02-29-12, 08:45 PM   #1
Slidegate
Lurking Renovator
 
Slidegate's Avatar
 
Join Date: Oct 2011
Location: Mercer, Pa.
Posts: 19
Thanks: 1
Thanked 4 Times in 3 Posts
Default Solar wire sizing

Okay I have a conundrum. If my panels are producing 18 Volts and 6 panels at 3.8 amps each which gives me approx 23 amps to my system. I have a 20foot run from my combiner box to my charge controller. Do I calculate wire sizing useing 12V or 18V in the formula?

Slidegate is offline   Reply With Quote
Old 02-29-12, 11:00 PM   #2
Ryland
Master EcoRenovator
 
Join Date: Mar 2009
Location: Western Wisconsin.
Posts: 913
Thanks: 127
Thanked 82 Times in 71 Posts
Default

Your wire size should be based off the amps, not the voltage, but your voltage under load should drop down to 13 to 14v, depending on your battery bank state of charge.
You can also get a Maximum Power Point Tracker Charge Controller (MPPT) that can handle a higher input voltage and adjust the output voltage to give you the highest wattage possible, often higher then you could otherwise get with a cheaper charge controller, also if you get a MPPT you can wire up your panels to a higher voltage so you can either run a longer run of wire and have your panels in an even more ideal location or you can use a smaller gauge wire.
Ryland is offline   Reply With Quote
The Following User Says Thank You to Ryland For This Useful Post:
Daox (03-01-12)
Old 03-01-12, 04:44 PM   #3
Slidegate
Lurking Renovator
 
Slidegate's Avatar
 
Join Date: Oct 2011
Location: Mercer, Pa.
Posts: 19
Thanks: 1
Thanked 4 Times in 3 Posts
Default

Thanks Ryland. I have an MPPT controller. I was just checking to see if my wire calcs were correct. I have a 20 ft run to my breaker box and with the 6 panels I have at a combined 23 amps so # 4 copper should be fine
Slidegate is offline   Reply With Quote
Old 03-01-12, 07:15 PM   #4
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default

What is the max voltage your MPPT controller will take from PV??

If it's high enough, you can put panels in series, (instead of parallel).
Higher voltage means lower current, and cheaper wire.

My four 18v (125w)panels are connected in series, giving my controller about 72v input.
Use that to keep my 48V battery bank changed up..


Since the current is only about 7 amps, I used about 100 feet of old RF coax
cable to bring the juice indoors to the controller and 48v bank..

Didn't need to break the bank on copper..

The bad thing about using 72 volts, is it could hurt or even kill you.
It's hard to get shocked by 18V.
__________________
My hobby is installing & trying to repair mini-splits
EPA 608 Type 1 Technician Certification ~ 5 lbs or less..
Xringer is offline   Reply With Quote
Old 03-01-12, 11:16 PM   #5
rhino 660
Apprentice EcoRenovator
 
Join Date: Oct 2010
Posts: 105
Thanks: 0
Thanked 10 Times in 8 Posts
Default

when installing systems ive been shocked by 360VDC and it just feals really funny its the amps that kill. higher voltage allows a smaller wire because when you series the volts double and the amps stay the same lotts of amps need a big wire if you parallel volts stay the same and amps add together
rhino 660 is offline   Reply With Quote
Old 03-02-12, 08:02 AM   #6
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default P = (IR)(R) or P = I^2(R)



Using two strings of 3 panels in Series-Parallel, you would be running 8 amps,
which is way better than 23 amps..

Since the line loss, is the current Squared, times the resistance..

8^2 = 64, but 23^2 = 529

So, 0.1 ohms of wire resistance would be 6.4 watts of loss,
but using 23 amps w/ 0.1 ohms is 53 watts of loss..

As you can see, it's not a linear thing.
__________________
My hobby is installing & trying to repair mini-splits
EPA 608 Type 1 Technician Certification ~ 5 lbs or less..

Last edited by Xringer; 03-02-12 at 08:19 AM.. Reason: it's not a linear
Xringer is offline   Reply With Quote
The Following User Says Thank You to Xringer For This Useful Post:
Slidegate (03-03-12)
Old 03-02-12, 08:30 AM   #7
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default

Quote:
Originally Posted by rhino 660 View Post
when installing systems ive been shocked by 360VDC and it just feals really funny its the amps that kill. higher voltage allows a smaller wire because when you series the volts double and the amps stay the same lotts of amps need a big wire if you parallel volts stay the same and amps add together

It feels funny?? At 360 volts, even a tiny bit of current can stop your heart.

I've found that anything over 45 volts across my fingers can stings like crazy,
and I would hate to have that zap going across my chest (left-hand to right hand).
__________________
My hobby is installing & trying to repair mini-splits
EPA 608 Type 1 Technician Certification ~ 5 lbs or less..
Xringer is offline   Reply With Quote
Old 03-02-12, 12:27 PM   #8
MN Renovator
Less usage=Cheaper bills
 
MN Renovator's Avatar
 
Join Date: Nov 2010
Location: Minneapolis, MN
Posts: 939
Thanks: 41
Thanked 116 Times in 90 Posts
Default

It all depends on where the current is passing. I've been zapped by enough power from a small photo capacitor(rated 350v) holding 280 volts that it burned two black marks where the current passed through the tip of my finger and the base of my finger. Source was 2 AA batteries passing through a transformer and then stored in a capacitor the size of a tic-tac.

If the voltage is there and it has any ability to create power and it goes through your heart, you are done. The amperage kills you think doesn't matter so much in the case of very low voltage because 12v won't pass through skin. It takes voltage to push the amperage through the impedance between your skin, your heart, and back through skin again.

A 360v array can kill you if you passes through, say both hands. If it passes through a finger or one part of your right hand through to ground you are lucky. Just hope it doesn't pass through your heart or get you trapped between the conductor and earth through the means of gravity. As always, use only your right hand when handling high voltage unless you are wearing HV resistant gloves and absolutely know it won't touch any other area of your body.
MN Renovator is offline   Reply With Quote
Old 03-03-12, 02:41 PM   #9
Slidegate
Lurking Renovator
 
Slidegate's Avatar
 
Join Date: Oct 2011
Location: Mercer, Pa.
Posts: 19
Thanks: 1
Thanked 4 Times in 3 Posts
Default Wire size

I want to thank you guys for your replies. I have 3 homemade panels on a tracker. Each panel is 18V-65W-3.7A. I am going to expand the framing to add 3 more panels. Thus my question on the wire sizing. I want to thank Xringer because he got me to research a few things. After reading my MPPT manual I found that it will accept up tp 100VDC from the panels to charge my 12V battery system. So if I series 3 panels I get 54V-195W-3.7A. Then if I parralel both 3 panel series I will have 54V-390W-7.4A. So I won't have to run any new wire. Just change some wiring to my combiner box. If anybody see's anything wrong with this please reply
Attached Thumbnails
Click image for larger version

Name:	IMG_0718.JPG
Views:	921
Size:	90.7 KB
ID:	2143  
Slidegate is offline   Reply With Quote
Old 03-04-12, 03:56 PM   #10
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default

Just remember to use heavy wire between the charger and battery..
But if you keep the runs short, #10 wire will be fine.


Another nice thing about running low current and high voltage PV,
is when you want to charge up a 24, 36 or 48 volt battery bank,
you just need to re-config your charge Controller. The PV is ready to go..

__________________
My hobby is installing & trying to repair mini-splits
EPA 608 Type 1 Technician Certification ~ 5 lbs or less..
Xringer is offline   Reply With Quote
Reply



Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 03:40 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design