The important thing to know here is the heat capacity of running water. 1 BTU =1 pound of water changing 1 degF. A gallon of water weighs close to 8 1/3 pounds, so the harvestable heat is 8 1/3 BTU per degF per gallon. This will tell you how much water (at the very least) you need to flow to move your heat.

The heat flow follows Fourier's law of thermal conduction. If you buy copper tubing, the manufacturer publishes tested specs for it. Do a little math and find out if you are in the ballpark as far as surface area and flow rate.
I'm not good with math but I do appreciate how it can save time.

I took some measurements off my radiator well water geoheater in the greenhouse tonight. Its been running about 2 hours.

Single wall polycarbonate 14' x 14' greenhouse
outside air is 26F
inside air is 37F

Heater output is 45F
No sure of CFM
Input air temp measured 38F
Water inlet temperature is 55F
Water outlet temperature is 46F
Flow is 1.2 GPM

So to figure BTU's per hour

60min x 1.2 GPM = 72 gallons per hour
BTU's per Gallon @ deg per gallon extracted = 9 deg x 8.3 per gallon= 74.7
BTU's per Gallon 74.7 x GPH 72 = 5378 BTUs per hour

This is equal to about 1.57 Kwatts per hour of electrical heating. I'm using .2KWH with the blower and well pump running.

So my COP for just using a radiator and fan is 7.85 ???

gadget is offline   Reply With Quote
Old 12-28-19, 01:50 AM   #12
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,287
Thanks: 345
Thanked 576 Times in 482 Posts
Send a message via Yahoo to jeff5may
Default

Sounds like a good ballpark figure to me. Also looks like you are ok with math as well. Trust me on this one: math up your sketch before you build it. Catching a conflict or shortcoming on paper saves a whole lot more than a little time and ink. It usually spells out the difference between something that lasts 5 minutes (or less) and until something unexpected or unplanned happens. With something overbuilt, it may take years for something unexpected to happen.
jeff5may is offline   Reply With Quote
Old 01-16-20, 01:08 PM   #13
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,287
Thanks: 345
Thanked 576 Times in 482 Posts
Send a message via Yahoo to jeff5may
Default

Any progress on the heat pump idea? With the original configuration (water cooler), if you flowed a gallon plus per minute through the original (water cooler) chilling tank, I would bet money it wouldn't freeze solid before your hot water tank got satisfied. We don't know what you're trying to heat, but even with a swimming pool heat sink, and constant source water flow, plus cap tube metering, your water jacket would still lack enough cold to choke the source water flow. Prove me wrong.

jeff5may is offline   Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 01:27 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2020, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design