Default Calculating BTUs from hot air

Can someone help me figure out the calculations for how to get the amount of BTUs you get out of hot air at a specified flow rate? I know that it depends on a lot of different factors like moisture content of the air, but I guess I'm looking for a simplified equation that ball parks things.

For example, lets say I have a solar hot air panel. I know the fan flows 100 CFM and I know that it puts out air that is 20F above ambient. How many BTUs per hour is it going to spit out?

__________________
Current project -
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.



To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
&
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
Daox is offline   Reply With Quote
Old 05-10-16, 02:01 PM   #2
bmxeroh
Helper EcoRenovator
 
Join Date: Sep 2014
Location: Columbus, OH
Posts: 34
Thanks: 1
Thanked 5 Times in 5 Posts
Default

I found this link here that seems to explain what you are looking for. https://www.ruppams.com/Sitedocs/RUP...alculation.pdf

It appears that given the above considerations, about 2160 BTU/hr.
bmxeroh is offline   Reply With Quote
The Following User Says Thank You to bmxeroh For This Useful Post:
Daox (05-10-16)
Old 05-10-16, 04:19 PM   #3
Daox
Administrator
 
Daox's Avatar
 
Join Date: Aug 2008
Location: Germantown, WI
Posts: 5,525
Thanks: 1,162
Thanked 374 Times in 305 Posts
Default

That is perfect. Thanks.
__________________
Current project -
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.



To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
&
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
Daox is offline   Reply With Quote
Old 06-07-16, 03:09 PM   #4
CarbonKevin
Lurking Renovator
 
Join Date: May 2011
Location: Winnipeg, Manisnowba
Posts: 4
Thanks: 0
Thanked 1 Time in 1 Post
Default

Use a psychometric chart and factor in humidity. There is a significant difference in the energy carried by dry air vs humid air, that 1.08 number is a vast oversimplification of the system you're trying to model.
CarbonKevin is offline   Reply With Quote
Old 06-07-16, 08:29 PM   #5
JRMichler
Apprentice EcoRenovator
 
Join Date: Apr 2012
Location: Phillips, WI
Posts: 109
Thanks: 10
Thanked 30 Times in 25 Posts
Default

I use 0.018 BTU/ft^3/deg F, the same as bmxeroh. It's almost certainly more accurate than typical temperature and airflow measurements. A one degree error on inlet and outlet temperatures could cause 10% error on temperature rise, plus another 10% air flow error, results in an easily believable 20% error. Accurate BTU measurements in HVAC systems can be a real challenge.

The largest assumption is that you are not adding or removing moisture. Then you would need a psychrometric chart.
JRMichler is offline   Reply With Quote
The Following User Says Thank You to JRMichler For This Useful Post:
Servicetech (06-12-16)
Old 06-07-16, 08:55 PM   #6
CarbonKevin
Lurking Renovator
 
Join Date: May 2011
Location: Winnipeg, Manisnowba
Posts: 4
Thanks: 0
Thanked 1 Time in 1 Post
Default

Quote:
Originally Posted by JRMichler View Post

The largest assumption is that you are not adding or removing moisture. Then you would need a psychrometric chart.
Correct me if I'm wrong, but I believe moist air requires a greater input of energy to achieve the same delta t as would a comparable volume (or volumetric flow) of dry air.
CarbonKevin is offline   Reply With Quote
The Following User Says Thank You to CarbonKevin For This Useful Post:
Servicetech (06-12-16)
Old 06-08-16, 03:13 AM   #7
ham789
Helper EcoRenovator
 
Join Date: Dec 2011
Location: tigard, oregon
Posts: 42
Thanks: 0
Thanked 4 Times in 4 Posts
Default efficiency?

Quote:
Originally Posted by Daox View Post
Can someone help me figure out the calculations for how to get the amount of BTUs you get out of hot air at a specified flow rate? I know that it depends on a lot of different factors like moisture content of the air, but I guess I'm looking for a simplified equation that ball parks things.

For example, lets say I have a solar hot air panel. I know the fan flows 100 CFM and I know that it puts out air that is 20F above ambient. How many BTUs per hour is it going to spit out?
This question created a bunch of other questions. After thinking about it...
The energy out of the system is equal to the solar energy impinging on it.
The efficiency of the system is the ratio of the energy that's actually
in the form you can use (input - losses)/input.
I argue that a cold collector absorbs more solar energy. Colder air
creates less radiated/conducted loss in the piping outside the heated space.
I think you might want more air and less temperature rise.
BUT
At some point the cost
of moving the air is more than the solar energy recovered.
Somewhere, there ought to be a peak in the net recovered energy curve.
Would be interesting to measure the delta-t at different air flow rates,
plug that into the BTU formula and plot the result. You'll end up with a
family of curves with solar input and outside temperatures as parameters.

Then add some practical limits.
Like, you may want to set a minimum output temperature for comfort reasons.
Or a maximum air flow for noise reasons.

Depending on the shape of the curves, it might be interesting to use a microcontroller to hunt for the peak in real time.
There's some advantage to measuring the thing you actually want to know.
You could even use a thermostat to divert any excess energy into a storage
tank for use when less solar is available.
ham789 is offline   Reply With Quote
Old 06-08-16, 09:38 AM   #8
JRMichler
Apprentice EcoRenovator
 
Join Date: Apr 2012
Location: Phillips, WI
Posts: 109
Thanks: 10
Thanked 30 Times in 25 Posts
Default

CarbonKevin raises a valid point, so I pulled out an ASHRAE #1 pschrometric chart and did a pair of example calculations.

1) 40 deg F in, 60 deg F out, 0 RH, 100 CFM in. From the chart, 12.6 ft^3 per lb in, 9.6 BTU/lb in, and 14.6 BTU/lb out. The calculation: (14.6 - 9.6) X 100 CFM / 12.6 ft^3/lb X 60 min/hr = 2380 BTUH.

2) 85 deg F in, 105 deg F out, 100% RH in, 100 CFM in. From the chart, 14.3 ft^3/lb in, 49.4 BTU/lb in, and 54.1 BTU/lb out. The calculation: (54.1 - 49.4) X 100 CFM / 14.3 ft^3/lb X 60 min/hr = 1970 BTUH.

The simplified approximation is 0.018 BTU/ft^3/deg F X 20 deg F X 100 CFM X 60 min/hr = 2160 BTUH. That's 10% low at the lower temperature, and 10% high at the higher temperature, and very close at normal room temperature. The error from the simplified approximation is less than the typical error from measuring temperature and CFM.

JRMichler is offline   Reply With Quote
The Following User Says Thank You to JRMichler For This Useful Post:
Daox (06-08-16)
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 04:52 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design