Old 03-29-15, 10:28 AM   #11
WyrTwister
Master EcoRenovator
 
Join Date: Jun 2013
Location: USA
Posts: 543
Thanks: 6
Thanked 44 Times in 38 Posts
Default

I am not a pro . However , I have found a common leak is the Schrader valves ( like the valve cores in the valve stems of you car wheels ) . There is a tool to remove & replace them with out discharging the refrigerant . I do this as SOP , as preventive maintenance , when a system has a leak .

Relatively inexpensive ( after you purchase the tool ) and painless . The Schrader valves are cheap at a HVAC supply house .

I have another suggestion for you . Send me a private message if interested .

God bless
Wyr

WyrTwister is offline   Reply With Quote
Old 03-30-15, 08:20 PM   #12
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

Yep, that falls in the service valve category. Both the Schrader valves and the valve body seals can leak, not to mention the flares. This is why they should all have caps tightly installed when not being fooled with.
jeff5may is offline   Reply With Quote
Old 05-08-15, 02:48 AM   #13
BradC
Apprentice EcoRenovator
 
Join Date: Dec 2010
Location: Western Australia
Posts: 148
Thanks: 1
Thanked 48 Times in 34 Posts
Default

Quote:
Originally Posted by steppinthrax View Post
I removed both caps and placed Teflon tape around the threads.
Don't do this _ever_. Those threads are not seals and will not be seals even *with* thread tape. The seal on the service valve is the faceted surface right on the end of the valve, and it seals by smooshing (technical term) against the inside of the valve cap lid. Some valves even go as far as having teflon gaskets, but *none* of them use the threads as seals.

Not targeted at you specifically, but I am sick to death of having to pick oil soaked manky teflon tape off threads because someone thought it might help. It doesn't, _ever_. What it does do is let me know that at some time a "technician" has worked on the system and makes me spend a lot more time checking the basics for other gross hacks.

Thread tape is for "tapered" threads, it has no use on parallel threads.

The bubble solution is a good idea, but there is stuff called "big-blu" bubble liquid specifically for HVAC techs. My experience is it lasts a _lot_ longer and shows up much smaller leaks.

If the leak is particularly sneaky, I still like a sniff of R22 backed with 300 pounds of nitrogen and an electronic leak detector. I have been known to use Propane and a lighter, but then I'm more of a do as I say, not as I do kinda guy.

BradC is offline   Reply With Quote
Reply



Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 07:01 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design