11-06-14, 08:11 PM | #1 |
Apprentice EcoRenovator
Join Date: Oct 2014
Location: SE MI
Posts: 105
Thanks: 3
Thanked 12 Times in 9 Posts
|
Heat pump reversing valve with position sensor
The reversing valve is a key component of a heat pump system. Like any mechanical item that moves, it is subject to failure. I have no idea what is the most common failure (internal leaks ? coil failures ?). If you are designing your own heat pump system with your own controller, a reversing valve with a position sensor could be valuable in resolving problems.
Does this exit ? |
11-06-14, 08:30 PM | #2 |
Supreme EcoRenovator
Join Date: Oct 2008
Location: Austin, TX
Posts: 1,154
Thanks: 14
Thanked 257 Times in 241 Posts
|
Measure the temperatures on each of the 4 lines. That's how they're diagnosed in the field.
__________________
To my surprise, shortly after Naomi Wu gave me a bit of fame for making good use of solar power, Allie Moore got really jealous of her... |
11-07-14, 08:00 AM | #3 |
Supreme EcoRenovator
|
They don't really need a position sensor. 99.9 percent of them are spring loaded. They return to the inactive position when you deenergize the coil. Most heat pumps are rigged so they are in heating mode when not activated.
In addition to temperature and pressure checks, about the only other thing you can check is the coil. When they do fail it is not easy to diagnose. |
11-07-14, 04:17 PM | #4 | |
Apprentice EcoRenovator
Join Date: Oct 2014
Location: SE MI
Posts: 105
Thanks: 3
Thanked 12 Times in 9 Posts
|
Quote:
How common are "pilot operated" valves ? The sensor could go on the pilot valve, but that really won't tell you if the main reversing valve is stuck/in the wrong position. |
|
11-07-14, 07:16 PM | #5 | |
Supreme EcoRenovator
|
Quote:
Service techs usually have two sizes in their trucks: small and large. Small ones go in units rated less than 3 tons, large go in units 3 tons or higher. For really large (commercial) units, they are special order items. The coils are all the same size, so the techs leave the old coils on the new valve after it is changed. (if the coil was not the problem; if it was, the valve is left alone and the coil is changed.) In reality, the valves don't usually have mechanical problems during the life of the unit compared to other components. This is why they are hard for techs to diagnose. In residential units, most techs try to condemn the unit and have it replaced before they troubleshoot things like clogged TXV's or frozen reversing valves. It goes like this: "If I fix this unit, I can only guarantee it for 90 days. For 200 dollars more, I can sell you a whole new outdoor unit that will pay for itself in energy savings. And it has a five year warranty." |
|
11-07-14, 10:15 PM | #6 |
Apprentice EcoRenovator
Join Date: Oct 2014
Location: SE MI
Posts: 105
Thanks: 3
Thanked 12 Times in 9 Posts
|
WOW !! I heard almost those exact words about 3 months ago ! In my case the compressor was smoked !!
|
11-08-14, 06:10 AM | #7 |
Helper EcoRenovator
Join Date: Sep 2014
Location: Oregon
Posts: 30
Thanks: 0
Thanked 1 Time in 1 Post
|
The cheap/free units we get on craigslist gotta come from somewhere.
|
|
|