Old 02-29-12, 08:45 PM   #1
Slidegate
Slidegate's Avatar
Default Solar wire sizing
Okay I have a conundrum. If my panels are producing 18 Volts and 6 panels at 3.8 amps each which gives me approx 23 amps to my system. I have a 20foot run from my combiner box to my charge controller. Do I calculate wire sizing useing 12V or 18V in the formula?
Slidegate is offline   Reply With Quote
Old 02-29-12, 11:00 PM   #2
Your wire size should be based off the amps, not the voltage, but your voltage under load should drop down to 13 to 14v, depending on your battery bank state of charge.
You can also get a Maximum Power Point Tracker Charge Controller (MPPT) that can handle a higher input voltage and adjust the output voltage to give you the highest wattage possible, often higher then you could otherwise get with a cheaper charge controller, also if you get a MPPT you can wire up your panels to a higher voltage so you can either run a longer run of wire and have your panels in an even more ideal location or you can use a smaller gauge wire.
Daox (03-01-12)
Old 03-01-12, 04:44 PM   #3
Slidegate
Slidegate's Avatar
Thanks Ryland. I have an MPPT controller. I was just checking to see if my wire calcs were correct. I have a 20 ft run to my breaker box and with the 6 panels I have at a combined 23 amps so # 4 copper should be fine
Old 03-01-12, 07:15 PM   #4
What is the max voltage your MPPT controller will take from PV??
If it's high enough, you can put panels in series, (instead of parallel).
Higher voltage means lower current, and cheaper wire.
My four 18v (125w)panels are connected in series, giving my controller about 72v input.
Use that to keep my 48V battery bank changed up..
Since the current is only about 7 amps, I used about 100 feet of old RF coax
cable to bring the juice indoors to the controller and 48v bank..
Didn't need to break the bank on copper..
The bad thing about using 72 volts, is it could hurt or even kill you.
It's hard to get shocked by 18V.
Old 03-01-12, 11:16 PM   #5
rhino 660
when installing systems ive been shocked by 360VDC and it just feals really funny its the amps that kill. higher voltage allows a smaller wire because when you series the volts double and the amps stay the same lotts of amps need a big wire if you parallel volts stay the same and amps add together
rhino 660 is offline   Reply With Quote
Old 03-02-12, 08:02 AM   #6
Default P = (IR)(R) or P = I^2(R)
Using two strings of 3 panels in Series-Parallel, you would be running 8 amps,
which is way better than 23 amps..
Since the line loss, is the current Squared, times the resistance..
8^2 = 64, but 23^2 = 529
So, 0.1 ohms of wire resistance would be 6.4 watts of loss,
but using 23 amps w/ 0.1 ohms is 53 watts of loss..
As you can see, it's not a linear thing.
Slidegate (03-03-12)
Old 03-02-12, 08:30 AM   #7
It feels funny?? At 360 volts, even a tiny bit of current can stop your heart.
I've found that anything over 45 volts across my fingers can stings like crazy,
and I would hate to have that zap going across my chest (left-hand to right hand).
Old 03-02-12, 12:27 PM   #8
It all depends on where the current is passing. I've been zapped by enough power from a small photo capacitor(rated 350v) holding 280 volts that it burned two black marks where the current passed through the tip of my finger and the base of my finger. Source was 2 AA batteries passing through a transformer and then stored in a capacitor the size of a tic-tac.
If the voltage is there and it has any ability to create power and it goes through your heart, you are done. The amperage kills you think doesn't matter so much in the case of very low voltage because 12v won't pass through skin. It takes voltage to push the amperage through the impedance between your skin, your heart, and back through skin again.
A 360v array can kill you if you passes through, say both hands. If it passes through a finger or one part of your right hand through to ground you are lucky. Just hope it doesn't pass through your heart or get you trapped between the conductor and earth through the means of gravity. As always, use only your right hand when handling high voltage unless you are wearing HV resistant gloves and absolutely know it won't touch any other area of your body.
Old 03-03-12, 02:41 PM   #9
Slidegate
Slidegate's Avatar
Default Wire size
I want to thank you guys for your replies. I have 3 homemade panels on a tracker. Each panel is 18V-65W-3.7A. I am going to expand the framing to add 3 more panels. Thus my question on the wire sizing. I want to thank Xringer because he got me to research a few things. After reading my MPPT manual I found that it will accept up tp 100VDC from the panels to charge my 12V battery system. So if I series 3 panels I get 54V-195W-3.7A. Then if I parralel both 3 panel series I will have 54V-390W-7.4A. So I won't have to run any new wire. Just change some wiring to my combiner box. If anybody see's anything wrong with this please reply
Old 03-04-12, 03:56 PM   #10
Just remember to use heavy wire between the charger and battery..
But if you keep the runs short, #10 wire will be fine.
Another nice thing about running low current and high voltage PV,
is when you want to charge up a 24, 36 or 48 volt battery bank,
you just need to re-config your charge Controller. The PV is ready to go..