EcoRenovator  

Go Back   EcoRenovator > Improvements > Geothermal & Heat Pumps
Advanced Search
 


Blog 60+ Home Energy Saving Tips Recent Posts Search Today's Posts Mark Forums Read


Reply
 
Thread Tools Display Modes
Old 01-14-14, 01:32 PM   #11
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

Ooh, I don't know, man. That sounds like a waste of a good heat exchanger to me. Once you do something like that, there's no going back. Not to mention any warranty you might have.

If you're considering something of that nature, consider enclosing one side of the outdoor HX with a shell, like an auto radiator. Water conducts lots more heat than air, so you don't need very much surface area to do the job. The bends and u-turns that contain the refrigerant would gain or lose heat (depending on operating mode) to the river water just fine. Since the river water would be under very low pressure, you might get away with sealing the end with silicone and clear plastic or pond liner material.

During cooling season, I know for a fact you can just feed cool water into the drain pan to submerge the bottom inch of HX. This alone will boost the capacity and efficiency of the outdoor HX A LOT. Those half a dozen passes or so of piping at the bottom are enough to lower condensing temperature 20-30 degF. The hotter it gets in the summer, the better that little bit of water will boost your efficiency.

Both of these suggestions make no major material mods to the outdoor unit. To resume original operation, you just quit pumping water and let it drain out. Your warranty stays intact and you can easily remove the mods for a unit swap or factory repairs.

jeff5may is offline   Reply With Quote
Old 01-14-14, 02:22 PM   #12
BeerGrylls
Lurking Renovator
 
Join Date: Dec 2013
Location: Austria
Posts: 25
Thanks: 1
Thanked 1 Time in 1 Post
Default

Jeff, not sure if I was clear enough :-) The hack has to happen so warranty is no issue anymore. I'd love to have this thing kept intact, but there is no way I'll be sailing with that thing on my deck, so needs to go below decks, hence the hack. I did a rough estimation of the current outside HX line length. There are 3 circuits in parallel in the HX totaling about 51m of pipe, pipe seems to be around 7-8mm OD.
An idea would be to make my own HX based on that pipe length, 3 coils of 8mm Cu tube inside black PEX or HDPE pipe in parallel, each coil 17m of pipe length. Could stack them all in a bucket with the compressor and other guts inside the bucket and be done with it. Now, writing about it, seems very doable and easy. It would be damn nice to have a shiny of the shelf shell in tube HX though...
BeerGrylls is offline   Reply With Quote
Old 01-14-14, 08:18 PM   #13
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

Here are some of the coax exchangers you speak of... Turbotec brand:


smaller


larger

In the USA, these coax coils can be found on ebay or at surplus city liquidators. Your mileage may vary in Europe.

Surplus City Liquidators
jeff5may is offline   Reply With Quote
Old 01-16-14, 05:20 AM   #14
BeerGrylls
Lurking Renovator
 
Join Date: Dec 2013
Location: Austria
Posts: 25
Thanks: 1
Thanked 1 Time in 1 Post
Default

Yeah, those would be nice. I contacted them about shipping one of those over here, they only want to ship with UPS which was ridiculous in price. USPS would be 4 times cheaper. Interestingly almost all HX from turbotec are rated 450psi, which is too little for R410a, however, I found that they have updated product codes for some of them and with the updated code they are rated for R410a, I suspect it is the same product, but who knows.

I also learned that a 1ton HX is not a 1 ton HX everywhere and in every application. They are rated for a certain evaporating/condensing temperature and most of them don't mention the temperature they are rated for. Basically if you need to suck heat from -20deg C outside air your HX, even if in 1 ton is huge and probably equivalent to a much higher tonnage for warmer temps. Given this, if I will have a change, I will go much higher than 1 ton.

Last edited by BeerGrylls; 01-16-14 at 05:23 AM..
BeerGrylls is offline   Reply With Quote
Old 01-16-14, 03:37 PM   #15
BeerGrylls
Lurking Renovator
 
Join Date: Dec 2013
Location: Austria
Posts: 25
Thanks: 1
Thanked 1 Time in 1 Post
Default

More poking inside the outdoor unit. Found a little metal encased box at the bottom of the unit. After checking several other manuals from other units, I now presume it is a so called 'reactor'. What exactly is it and what is it doing ? Anyone knows ?
BeerGrylls is offline   Reply With Quote
Old 01-16-14, 04:32 PM   #16
pinballlooking
Super Moderator
 
pinballlooking's Avatar
 
Join Date: Jun 2013
Location: SC
Posts: 2,923
Thanks: 172
Thanked 564 Times in 463 Posts
Default

Quote:
Originally Posted by BeerGrylls View Post
Yeah, those would be nice. I contacted them about shipping one of those over here, they only want to ship with UPS which was ridiculous in price. USPS would be 4 times cheaper. Interestingly almost all HX from turbotec are rated 450psi, which is too little for R410a, however, I found that they have updated product codes for some of them and with the updated code they are rated for R410a, I suspect it is the same product, but who knows.

I also learned that a 1ton HX is not a 1 ton HX everywhere and in every application. They are rated for a certain evaporating/condensing temperature and most of them don't mention the temperature they are rated for. Basically if you need to suck heat from -20deg C outside air your HX, even if in 1 ton is huge and probably equivalent to a much higher tonnage for warmer temps. Given this, if I will have a change, I will go much higher than 1 ton.
If they turn out to be what you need you can have it shipped to me in the states. When I get we can mail it out to you USPS you can just paypal me actual shipping. We ship six days a week we will just add it with the other we stuff we ship.
pinballlooking is offline   Reply With Quote
Old 02-10-14, 10:56 AM   #17
Daox
Administrator
 
Daox's Avatar
 
Join Date: Aug 2008
Location: Germantown, WI
Posts: 5,525
Thanks: 1,162
Thanked 374 Times in 305 Posts
Default

Any updates on this BeerGrylls?
__________________
Current project -
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.



To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
&
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
Daox is offline   Reply With Quote
Old 02-10-14, 02:42 PM   #18
NiHaoMike
Supreme EcoRenovator
 
NiHaoMike's Avatar
 
Join Date: Oct 2008
Location: Austin, TX
Posts: 1,154
Thanks: 14
Thanked 257 Times in 241 Posts
Default

Quote:
Originally Posted by BeerGrylls View Post
More poking inside the outdoor unit. Found a little metal encased box at the bottom of the unit. After checking several other manuals from other units, I now presume it is a so called 'reactor'. What exactly is it and what is it doing ? Anyone knows ?
That's the boost inductor for the active PFC.
__________________
To my surprise, shortly after Naomi Wu gave me a bit of fame for making good use of solar power, Allie Moore got really jealous of her...
NiHaoMike is offline   Reply With Quote
Old 02-21-14, 04:06 PM   #19
BeerGrylls
Lurking Renovator
 
Join Date: Dec 2013
Location: Austria
Posts: 25
Thanks: 1
Thanked 1 Time in 1 Post
Default spring is coming

Hi All,
Firstly, many thanks pinballooking for the offer. Unfortunately I haven't found a suitable HX yet. If I do find one in the states I would definitely appreciate some help with shipping. Secondly, there is no progress except doing lots of reading and searching for HXs. This is a high pressure unit and there aren't any HX I can afford around this corner of the world, or other places. I am also studying the design of this pump and others as well, to see why and how they are built they way they are.
Thirdly, what is a boost inductor for the active pfc in laymen terms ?
Last night I pulled the entire indoor unit apart due to noise and vibration, was trying to rip itself off the bulkhead. I found out: the centrifugal blower end support it is really bad design, and those little Chinese children assembling the unit forgot to add grease in this rubber end sleeve suporting the blower on one end. Now it is packed with grease and running smoothly, at least for some time...
Since there is no HX in sight, I have been thinking of stripping all the alu fins off the outdoor hx, unfold it flat ( it us L shaped now) and put it in a black box with a perspex or acrylic glass screen and mount it on the boat transom. When real warm weather comes I will first evacuate the unit and start chopping it up. I am really afraiud of how much a company will quote me for the gas recovery, been thinking better find a recovery machine on ebay, do my work with it and sell it again...
Anyway, this is as much info I have for the moment. Been really happy with the unit so far. About 7.8kw/day average. We had about 2 weeks of -10 degrees, ice around the boat, but not touching the hull. Boat was warming the water around it.
Another hx alternative I have been thinking about - buy a used cheap big indoor unit, strip the hx as it is compact and put it in some sort of casing.
Cheers from the warm boat.
F
BeerGrylls is offline   Reply With Quote
Old 02-21-14, 04:22 PM   #20
BeerGrylls
Lurking Renovator
 
Join Date: Dec 2013
Location: Austria
Posts: 25
Thanks: 1
Thanked 1 Time in 1 Post
Default

Btw I have looked at the size of the current hx for referrence, if anyone interested.
Outdoor about 51 lenghts of 76cm pipes, 3 circuits, pipe is 7.6? mm weird diameter, probably not metric.
Indoor 36 lenghts of 70cm pipes , same od, 4 circuits.

So indoor hx is roughly 2/3 of outdoor hx.
Cheers
F

BeerGrylls is offline   Reply With Quote
Reply


Tags
ashp, heat pump, inverter, minisplit, wshp

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 07:09 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design