AC,
If the control board made this unit try to work by pressing the test button, and didn't flash the red light, it probably works. This is good for you because you can interface with the brawny parts (relays, contactors, thermistors, etc) directly pretty easily. Interfacing with an arduino would be simple to do. Just throw an addressable switch (DS 2406, DS 2408) in the unit and impose control thru the 1-wire interface. IMHO, this approach would be much easier and cheaper than re-inventing a control board or decoding comms and faking an indoor unit.

jeff5may is offline   Reply With Quote
Old 01-18-13, 03:59 AM   #12
launboy
Apprentice EcoRenovator
 
Join Date: Mar 2011
Location: SE Wisconin
Posts: 107
Thanks: 3
Thanked 11 Times in 9 Posts
Default

Im curious is there any advantage to a non-inverter mini-split without its control? What makes the mini-split any more efficient than say a window unit? Larger coil obviously helps, but what advantage does the multi-speed fan have if the compressor doesn't ramp up and down with it?

In Heat-pump mode it seems to me you would basically want the outdoor fan to run full speed always(beside defrost) to obtain the max amount of heat from the air, and vary the indoor pump speed to maintain adequate head pressure and floor temperature. Actually if that's the case, building your own controls shouldn't be to hard if you can figure out a decent demand defrost algorithm.

Best of luck,
Adam
launboy is offline   Reply With Quote
Old 01-18-13, 09:19 AM   #13
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default This From Acuario...

This from Acuario in response to questions about controller electronics:

Quote:
Hi AC,

The fan sounds like it is single speed. You will probably find one wire goes to a common connection somewhere, the other 2 go to a capacitor and then one of the wires from the capacitor connects to the main feed. The capacitor is there to give an offset phase to run the motor.

On my units (at the moment) as I only use them for heating I run the fan continuously so just connected to the live feed.

The compressor is controlled via a connected to a mechanical thermostat. This switches the compressor (and fan) on/off when there is a call for heat.

I did build a defrost circuit (plans etc. on the forum) that controls the compressor and changeover valve. It seems to work well. It hasn’t been that cold here this winter so it’s only operated a couple of times.

I just acquired a machine that actually has got a sump heater – never come across one before! Interestingly I found the manual for the controller that manages it plus the defrost etc. and gives all the timings etc.

You can get the manual here.

Regards,

Nigel
NOTE: Acuario live in Spain where compressor sump heaters are not needed, thus his surprise.

Best,

-AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
Old 01-21-13, 04:22 PM   #14
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default Digging Deeper...

I removed the front panel to allow a closer look at the components...


Here's a look at the whole unit from the front, showing the fan and the compressor. I see that the fan shows a little discoloration, but really, very little.


Here is the compressor compartment with all the compressor-related components...


This is a closeup of the compressor identification label.


The crankcase heating assembly.



This is the reversing valve.


The transformer for the control board power supply (or maybe it's for the fan?)



The starting cap for the compressor that provides a slightly off-phase kick to get the compressor motor going.


And lastly, reaching the camera through a small space behind the compressor and pressing the shutter with the bloody knuckle of my thumb, is the cap tube.


Best,

-AC
Attached Thumbnails
Click image for larger version

Name:	Dsc09807s.jpg
Views:	613
Size:	45.2 KB
ID:	2889   Click image for larger version

Name:	Dsc09808s.jpg
Views:	592
Size:	81.0 KB
ID:	2890   Click image for larger version

Name:	Dsc09809s.jpg
Views:	2227
Size:	26.7 KB
ID:	2891   Click image for larger version

Name:	Dsc09811s.jpg
Views:	2276
Size:	36.8 KB
ID:	2893   Click image for larger version

Name:	Dsc09815s.jpg
Views:	2389
Size:	47.4 KB
ID:	2894  

Click image for larger version

Name:	Dsc09818s.jpg
Views:	2447
Size:	57.1 KB
ID:	2895   Click image for larger version

Name:	Dsc09810s.jpg
Views:	2548
Size:	36.7 KB
ID:	2896   Click image for larger version

Name:	Dsc09819s.jpg
Views:	2172
Size:	54.8 KB
ID:	2898  
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...

Last edited by AC_Hacker; 01-23-13 at 09:59 PM..
AC_Hacker is offline   Reply With Quote
Old 01-21-13, 09:14 PM   #15
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default

That heater coil/spring looks the same as on my Sanyos. It might be controlled by the controller board.
My heaters were traceable back to a relay on the main controller board. When it's warm out, the heater stays off..

I would keep the controller if possible, since it might have a good defrost setup.


When you hook up AC power (to 5&6), two of the other terminals should go hot, to power the indoor unit.
You could find them with a voltmeter.

~~~
If you have found the 2 power lines, you should find out if one of the low voltage lines is ground.
For safety, one one of the lines going inside the house might be ground.
If it is ground, that only leaves 1 line left for control.

Single line controllers sometimes use a DC bias voltage and the control input is a set of resistive loads.
Maybe like this:
A. Zero ohms (short) = standby
B. 2.3V+ = Cool (medium resistance)
C. 5.0V+ = Heat (high resistance)
D. No load = Maintenance mode, use test button.

If were to find one of the lines had low voltage DC on it,
you could try connecting a Pot or variable resistor and turn it's resistances up and down to see if it changed the operating mode..?.
The other side of the pot would be connected to ground.
But, before I did this, I would do a lot of searching for a schematic diagram.

~~~
If there is no ground, and you have two control lines, one might be compressor ON and the other one would be mode, cool or heat..
Hopefully both these lines would have a low DC voltage on them..

__________________
My hobby is installing & trying to repair mini-splits
EPA 608 Type 1 Technician Certification ~ 5 lbs or less..
Xringer is offline   Reply With Quote
Old 01-21-13, 10:45 PM   #16
Geo NR Gee
Journeyman EcoRenovator
 
Join Date: Jan 2011
Location: Seattle
Posts: 326
Thanks: 109
Thanked 23 Times in 18 Posts
Default

That unit looks clean! Did you notice any dirt in the coils?
Geo NR Gee is offline   Reply With Quote
Old 01-22-13, 01:44 AM   #17
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

Hey AC,
I believe I found your schematic/service manual. From the parts seen in the pics, it looks like your unit is in fact an LG model HMH012KD under the skin.
The schematic and service manual is here (rebranded as ICP Commercial):
http://icpindexing.toddsit.com/docum...litservice.pdf
Happy hunting!
Jeff
jeff5may is offline   Reply With Quote
Old 01-22-13, 02:07 AM   #18
BradC
Apprentice EcoRenovator
 
Join Date: Dec 2010
Location: Western Australia
Posts: 148
Thanks: 1
Thanked 48 Times in 34 Posts
Default

Well, that schematic corresponds pretty closely with the configuration on that outdoor board.

So I'll eat my words. It uses a one wire serial protocol on terminal 1 of the unit-to-unit link.

Having said that, you can quite easily remove the CPU chip and drive all your solenoids from the inputs of IC8 using logic levels, so you don't need to interface to any high voltages. In addition, you have a thermistor connected to the main cpu also which you could connect directly to an arduino or equivalent.

Last edited by BradC; 01-22-13 at 02:26 AM.. Reason: Only one thermistor. The other pins are option resistors
BradC is offline   Reply With Quote
Old 01-22-13, 08:24 AM   #19
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default

Yeah, fooled me. I would not have expected an older non-inverter unit to have serial.
I guess the newer stuff is just a copy of the old stuff..

Pin #1 is a bi-directional control line. So, you not only send commands outdoors, you read back status data too.


Seems like it would be simpler to wire your control pair across the test button.. Brute Force Control.

Outdoor
• Once push : Ignore Communication error.
• Twice push : Comp. ON, / Outdoor Fan ON / Reversing Valve Coil ON(only Heating Model) / Crank Case heater Coil ON(only Heating Model)
• 3 Times push : Comp. ON, Outdoor Fan ON / Reversing Valve Coil OFF(only Heating Model) / Crank Case Heater Coil OFF(only Heating Model)
• 4 Times push : Same
• 5 Times push : Error LED(Red) ON
• 6 Times push : Comp OFF, Outdoor FAN OFF
• 7 Times push : Reset

That might get you the basic operations you need. If it will stay running in the test mode.. (No time-out).
And, you will likely have all protection/defrost functions too..
__________________
My hobby is installing & trying to repair mini-splits
EPA 608 Type 1 Technician Certification ~ 5 lbs or less..
Xringer is offline   Reply With Quote
Old 01-22-13, 04:00 PM   #20
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Mega Thankyou's to Xringer, BradC & jeff5may!

You've provided some interesting info & approaches. The manual looks awfully close to the unit I have. The differences appear to be very small.

Geo NR Gee: Nope, the coils are sparkling clean... much cleaner than the fan blades.

At this point, I don't have any intention to run the unit in cooling mode, but for the time being, I'll leave the reversing valve where it is. It might be useful to be able to send some of the summer heat into the ground.

Anyway, from your info, I'll do some testing & let you know what I'm finding out.

BTW, I saw a time-line chart the other day about R22, and it looks like the final phaseout (no more sales of R22) will be a few years from now. So you can expect to see a considerable amount of good HVAC hardware for a song or even free, pretty soon. I was seeing new R22 mini-splits for sale as recently as 3 years ago... in a few years, they'll be unserviceable unless you know a few secrets.

Keep your eyes peeled!

Best,

-AC

__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 06:27 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design