EcoRenovator  

Go Back   EcoRenovator > Improvements > Solar Power
Advanced Search
 


Blog 60+ Home Energy Saving Tips Recent Posts Search Today's Posts Mark Forums Read


Reply
 
Thread Tools Display Modes
Old 11-29-19, 08:55 AM   #1
Robaroni
Journeyman EcoRenovator
 
Robaroni's Avatar
 
Join Date: Jun 2013
Location: Delhi, NY
Posts: 332
Thanks: 20
Thanked 53 Times in 40 Posts
Default A 10Kw LiFeP04 battery bank

About 2 years ago, before LIFEP04 batteries became the backup standard, I scored 640 new Tenergy 32700 LiFeP04 batteries for about $900 USD including shipping. These were purchased to replace my 13 year old L/A bank.

A little background:
I have two systems here, in 2006 I installed my first PV array with backup. I went to backup, as opposed to off-grid, because I have ready access to grid power and running batteries everyday is an expensive battery solution. I knew as I built my system I would install an intertie down the line and selling my excess to the grid was a better option. This way the grid keeps my batteries charged for when I need them and I still sell my excess after all my needs are met.
In 2011 I installed my intertie system which just sells back to the grid. So I have two systems, the intertie sells back to the grid and the intertie/off grid sells back after my needs are met.

First and foremost was safety - I wanted the bank to be bullet proof safe
and I wanted at least 2 to 2-1/2 days of power in complete darkness - which should never occur.

______________________________________

The build:

Because these batteries are stationary I built them in 4 groups of 4S36P (4 series and 36 parallel).
The batteries are rated at 3.2V, 5.5A, this meant that 16S (4x4S) would give me 51.2V for my 48V system.

I used one piece of finished plywood (~$25 at Home Depot) cut into 4 equal pieces (see pictures)
I machined jigs to cut and form each battery holder in the system. I wanted access to each battery and I wanted to be able to remove each battery. I also wanted each battery fused - just in case one went south. I did test a battery with a dead short to see how it would react. No fire no flames, just got warm and died. LiFeP04's are ideal for backup.

For fusing I used bare 24AWG wire on each battery and for the bus bars I used 1/2" copper pipe (the heavier pipe, L?) I connected the four 12V modules using AWG 2/0 battery cable.

The clips were made from surplus 316 SS 3/4" x .020" 100 foot rolls of banding and the battery wooden rails from hard maple. Because you can't solder directly to 316SS I spot welded nickel tabs to the SS when running fuse wires.

________________________

As it stands now I have a little over 10Kw of PV. My energy supplier owes me several hundred dollars and I have driven my EV for the last 2-1/2 years at a total cost of less than $75 for maintenance, inspections and charging. If the grid fails I expect to run easily for several weeks, even at my 42 latitude in the winter, without issues. I tested the system this winter accidentally leaving a space heater on during the test. It ran about 24 hours and the system recharged the next day which was partially overcast.

Attached Thumbnails
Click image for larger version

Name:	DSCN3437.jpg
Views:	601
Size:	397.0 KB
ID:	8762   Click image for larger version

Name:	DSCN3409.jpg
Views:	609
Size:	201.3 KB
ID:	8763   Click image for larger version

Name:	DSCN3414 1.jpg
Views:	616
Size:	323.5 KB
ID:	8764   Click image for larger version

Name:	DSCN3405.jpg
Views:	602
Size:	376.6 KB
ID:	8765   Click image for larger version

Name:	DSCN3419.jpg
Views:	635
Size:	395.0 KB
ID:	8766  

Robaroni is offline   Reply With Quote
The Following 6 Users Say Thank You to Robaroni For This Useful Post:
arnesr (12-09-19), Daox (11-30-19), gasstingy (12-26-19), philb (11-30-19), pinballlooking (11-29-19), wlbryce (12-20-19)
Old 11-30-19, 03:25 PM   #2
Daox
Administrator
 
Daox's Avatar
 
Join Date: Aug 2008
Location: Germantown, WI
Posts: 5,525
Thanks: 1,162
Thanked 374 Times in 305 Posts
Default

Wow, that setup looks great!

What kind of inverter are you running?
__________________
Current project -
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.



To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
&
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
Daox is offline   Reply With Quote
Old 11-30-19, 04:41 PM   #3
Robaroni
Journeyman EcoRenovator
 
Robaroni's Avatar
 
Join Date: Jun 2013
Location: Delhi, NY
Posts: 332
Thanks: 20
Thanked 53 Times in 40 Posts
Default

Thanks Daox!
I haven't posted in awhile, been busy with projects but I thought you guys would like to see what I've been up too.

I'm using two Outback GFX3648 inverters for a total of 7.2Kw with a Flex80 and a Flex60 charge controller.

The project took about 2 mos. to complete but I saved thousands of dollars so I think it was worth it.
Next I hope (finally!) to get to wind and microhydro but I needed to put them aside as I had no backup during power failures, my L/A batteries were shot.
Rob
Robaroni is offline   Reply With Quote
Old 11-30-19, 05:23 PM   #4
philb
Apprentice EcoRenovator
 
Join Date: Nov 2010
Location: Oklahoma City
Posts: 155
Thanks: 58
Thanked 17 Times in 14 Posts
Default

Really impressive! Nice setup.

Your only using Flex 60's and 80's. No expensive BMS?

I have 24 GC2 6volt batteries on one system that die when the sun goes down. Most of them are 8 years old. $3800 for a traction demo battery. Maybe you could point me to a LIFEP04 retailer?

This post came at just the right time!
Thanks Rob!
philb is offline   Reply With Quote
Old 11-30-19, 05:52 PM   #5
Robaroni
Journeyman EcoRenovator
 
Robaroni's Avatar
 
Join Date: Jun 2013
Location: Delhi, NY
Posts: 332
Thanks: 20
Thanked 53 Times in 40 Posts
Default

Quote:
Originally Posted by philb View Post
Really impressive! Nice setup.

Your only using Flex 60's and 80's. No expensive BMS?

I have 24 GC2 6volt batteries on one system that die when the sun goes down. Most of them are 8 years old. $3800 for a traction demo battery. Maybe you could point me to a LIFEP04 retailer?

This post came at just the right time!
Thanks Rob!
I initially set up the system with a BMS system but after exhaustive testing
I found the best solution was to charge the bank to 3.4V (each cell 54.4V for the bank) max which, according to the data sheets on my batteries brings them up to almost 100% charge. I also spoke to the engineers at Tenergy who corroborated this.
I did carefully bring all the batteries into balance and I carefully checked all 576 batteries to make sure they were within 50mV of each other before putting them into the system.

Cheap Chinese BMS boards can't control batteries above a few hundred mV so it's best not to use them at all. The wires they use are too thin and the voltage drop across the wires makes it hard to regulate batteries well.

There's a YT guy named Will Prowse who's doing a lot of battery testing. My problem is that I simply don't have access to all the batteries so I can't give you hands on information.
From what I've seen the best LiFeP04's around is the Battleborn. I think it may have an internal BMS. Several people are using them with good results. If I had to go with a commercial battery this would be it.

https://battlebornbatteries.com/?gcl...SAAEgKTHfD_BwE
Robaroni is offline   Reply With Quote
Old 11-30-19, 08:31 PM   #6
Daox
Administrator
 
Daox's Avatar
 
Join Date: Aug 2008
Location: Germantown, WI
Posts: 5,525
Thanks: 1,162
Thanked 374 Times in 305 Posts
Default

I would suggest Battery Hookup. I ordered some 18650 cells from them not too long ago. Great prices!
__________________
Current project -
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.



To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
&
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
Daox is offline   Reply With Quote
The Following User Says Thank You to Daox For This Useful Post:
philb (12-01-19)
Old 12-01-19, 12:13 PM   #7
randen
Uber EcoRenovator
 
Join Date: Apr 2011
Location: Strathroy Ontario Canada
Posts: 657
Thanks: 9
Thanked 191 Times in 129 Posts
Default

Robaroni

Nice looking system and the price also excellent. 10 kWh for $900.00 unheard-of !! To have an autonomous system is very nice in-deed. 2 days reserve power amazing !!

Could you give a idea to what you power in your home. I think that impresses the value of a system. You had mentioned about charging your car and driving on sunshine now thats something. Do you remember buying gasoline to get to work??

randen
randen is offline   Reply With Quote
Old 12-01-19, 08:41 PM   #8
where2
DIY Geek
 
Join Date: Apr 2013
Location: Sunny Florida
Posts: 401
Thanks: 74
Thanked 83 Times in 73 Posts
Default

Having a 4.4kW solar array, and having a neighbor who regularly asks me when I'm going to come up with a "backup plan" for when the grid is down, Rob wins the prize for having created his own solution to this common question. Now I just need to incorporate this concept into my upcoming 5.6kW PV array. Having a grid tied array is easy, having a backup plan to recharge my e-Golf is a better plan...
where2 is offline   Reply With Quote
Old 12-09-19, 01:22 PM   #9
arnesr
Lurking Renovator
 
Join Date: Feb 2017
Location: Greenville WI
Posts: 13
Thanks: 1
Thanked 7 Times in 2 Posts
Default

Fantastic work, thanks for sharing! I am truly envious, that seems like a great DIY backup system.
arnesr is offline   Reply With Quote
Old 12-20-19, 02:47 PM   #10
wlbryce
Lurking Renovator
 
Join Date: Dec 2009
Posts: 5
Thanks: 2
Thanked 0 Times in 0 Posts
Default

Great Job, But, you still should use a BMS. The BMS is not just for balancing, it is the safety for the battery bank. Inverters and especially charge controllers are not foolproof in regards to the charging and DOD control.

The BMS, will insure that you do not overcharge or over discharge the battery.
It not just good practice but its adds a level of safety for the battery bank.
Overcharging LA battery just ruins the battery but over charging Lithium even LiFE chemistry might end with a diffrent result.

Logan
instagram. com/wlbryce

wlbryce is offline   Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 11:14 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design