Memphis - this "oil return" line is getting complicated and fraught with potential problems. The number of connections (each with potential leaks) also increases the gas loss issue. I am very good at copper pipe soldering and am surprised when I have a pin hole leak - but it happens.

I am thinking a water exchange poly pipe coil in the pond, with a heat exchanger, will be a simpler, lower cost, time tested and more reliable solution.

There is beauty in simplicity. DX may appear to be that on the surface, but multiple coils, oil return lines, etc look problematic to me.

But I do NOT want to be any wet towel here! You have done impressive work and it is ALWAYS better to think out a system before building it physically.

Steve

__________________
consulting on geothermal heating/cooling & rational energy use since 1990
stevehull is offline   Reply With Quote
Old 07-24-15, 09:12 AM   #52
MEMPHIS91
Journeyman EcoRenovator
 
MEMPHIS91's Avatar
 
Join Date: Apr 2015
Location: Oxford, MS USA
Posts: 496
Thanks: 69
Thanked 87 Times in 61 Posts
Default

Wise advice. Yes the water based closed loop systems do seem to be the easiest install and less maintenance. On top of cheaper and might just be more efficient. There are flat plate exchangers and tons of info on how to make them run well. I will be giving that option some thought.
DX is just so rare. And the techs that put them in are not as willing to talk specs as most HVAC guys are. I would love to blue the doors wide open for more DIY guys to be able to use this type set up. I have unlimited options. They may not.
Oil oil oil is the problem. Sure a set of lines can be way to big for the compressor to handle but oil return looks to be the number one issue with DX. AC says a document exist that has hard facts and numbers on the oil return. If I can find that and design a system that will nitre than likely work then I will continue with DX. If not, closed loop of pump and dump seems wisest. Thanks for your input.
MEMPHIS91 is offline   Reply With Quote
Old 07-24-15, 10:59 AM   #53
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

This magic device is called an oil separator.

Inside the shell:

Last edited by jeff5may; 07-25-15 at 04:02 PM..
jeff5may is offline   Reply With Quote
Old 07-24-15, 11:58 AM   #54
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by ;46092
...
Oil oil oil is the problem. Sure a set of lines can be way to big for the compressor to handle but oil return looks to be the number one issue with DX. AC says a document exist that has hard facts and numbers on the oil return. If I can find that and design a system that will nitre than likely work then I will continue with DX. If not, closed loop of pump and dump seems wisest. Thanks for your input.
MEMPHIS91,

I was looking over your sketch, and I am curious why you want the compressor near the house? If your project idea is to use condensing DX inside the house, then I get it. But if your idea is to go through an HX at the compressor, and use heated water as your heat transfer medium, or something, you might consider a different approach.

If you re-located your compressor to be nearer your pond, you would be able to shorten the overall length of your copper. You would also keep the possibility of any R290 leaks, removed a safe distance from your house, AND the problems would be down hill, which is very important.

Don't know if you read my account in the 'Manifesto':
Quote:
Early one October morning (high humidity & cold), I was mucking about in the back yard with propane, trying to fill some small green bottles from a large tank. My cellar steps leading down to the basement were not far away. There was a leak in the process, and an amount of propane escaped before I could get to the valve on the tank. Because the escaping propane chilled the air, the condensing water vapor made the propane visible. I watched the propane cloud flow across the ground and down into the cellar stair well, where it filled it stair well up about half way, and it seethed and settled there. The top of this propane cloud moved and rippled like waves across water.

I dashed into the house, and got a large box fan, and made sure it was on and running before I opened the cellar door, and let it quickly blow the propane away.

That image has never left me, neither has my caution and respect regarding R290.
Before you get too far on this project, why don't you whip out a smaller test unit, maybe a quarter Ton or half Ton compressor, and do a test of your idea in your pond... one loop. You could have your evaporator be a goodly coil of copper in the bottom of a 55 gal barrel, and you could measure the temp at the start and end, and calculate the overall heat output, and COP. This would tell you what your heat output per loop would be, and how many loops you would need to hit your target heat goal.

If there were problems, they would probably begin to show up there. If there were problems associated with size, length or diameter, etc., you could tweak and remedy the issue. Then with that confidence, you could replicate your configuration, and test out your manifold concept, and grow piece by piece. This way, your test loop would become one of several 'know good' loops if your final project.

If you do this, and relocate your compressor near your pond, be sure to never lose sight of a healthy fear of electricity and water. I would suggest very strongly to have a GFI at the source of your power cord. Ask me how I know...

-AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...

Last edited by AC_Hacker; 07-24-15 at 12:34 PM..
AC_Hacker is offline   Reply With Quote
The Following User Says Thank You to AC_Hacker For This Useful Post:
stevehull (07-24-15)
Old 07-24-15, 12:12 PM   #55
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

The magic device you seek is known as an oil separator. It resembles a muffler with a cap tube at the low point. Some are filled with copper or steel wool, or other , ,more exquisite material. The thing is plumbed in between the compressor discharge and the reversing valve. The cap tube taps into the suction line. No more oil return problem.
jeff5may is offline   Reply With Quote
The Following User Says Thank You to jeff5may For This Useful Post:
stevehull (07-24-15)
Old 07-24-15, 09:41 PM   #56
MEMPHIS91
Journeyman EcoRenovator
 
MEMPHIS91's Avatar
 
Join Date: Apr 2015
Location: Oxford, MS USA
Posts: 496
Thanks: 69
Thanked 87 Times in 61 Posts
Default

AC, the main reason the compressor is at the house is because that is where the air source unit is now. It makes it SO much easier and I saw no problems if I were doing it DX.
A small prototype is a good idea, I have a few compressors that might work well for it.
Propane is scary stuff, I am a state certified firefighter, I've seen it do crazy things. Not as eerie as your story though, but I do vaguely remember reading as I power read through the entire thread.

Jeff, YOU ARE AWESOME! I knew something like this had I exist.
Q E HVAC R Refrigeration Oil Separator 7 8" ODS New | eBay

I will continue reading up on it but it seems as though I can push the size of the pond loop now. I'm thinking 100 feet of 5/8 going out to the manifold, with 5 150 feet long 5/16 loops coming back through 100 feet of 1/2 to the compressor. Other than friction loss is there a problem with the loops being to big now that the oil is not an issue? That is less than $900 worth of copper.

Btw I will super test the entire line set/manifold/loops on the ground for leaks before and after installation.

Last edited by MEMPHIS91; 07-24-15 at 10:09 PM.. Reason: http://www.achrnews.com/articles/91004-selecting-installing-oil-separators
MEMPHIS91 is offline   Reply With Quote
Old 07-25-15, 04:52 AM   #57
stevehull
Steve Hull
 
Join Date: Dec 2012
Location: hilly, tree covered Arcadia, OK USA
Posts: 826
Thanks: 241
Thanked 165 Times in 123 Posts
Default

Whew - $900 for copper to make the DX work? Ouch!

Steve
__________________
consulting on geothermal heating/cooling & rational energy use since 1990
stevehull is offline   Reply With Quote
Old 07-25-15, 05:29 AM   #58
MEMPHIS91
Journeyman EcoRenovator
 
MEMPHIS91's Avatar
 
Join Date: Apr 2015
Location: Oxford, MS USA
Posts: 496
Thanks: 69
Thanked 87 Times in 61 Posts
Default

Quote:
Originally Posted by stevehull View Post
Whew - $900 for copper to make the DX work? Ouch!

Steve
That's for a oversized system. More like 5 tons. The closed loop hdpe pipe would be about $800-$1,000 for the same size unit. Not including needed an extra pump and controls and anti freeze. I think the copper is the cheaper route.
MEMPHIS91 is offline   Reply With Quote
Old 07-25-15, 08:16 AM   #59
randen
Uber EcoRenovator
 
Join Date: Apr 2011
Location: Strathroy Ontario Canada
Posts: 657
Thanks: 9
Thanked 191 Times in 129 Posts
Default DX build

Memphis

I'm siding with AC_Hacker Obtain a small window shaker put it in the window of your home and take the condenser out and put a nice 3/8 or 5/15 copper loop down to your pond and back.

Test the theory If after a few weeks you break open the loop and find a huge quantity of oil, there maybe trouble.

On the other hand if there is very little you have the green light.

I'm thinking the propane refrigerant being a petroleum distillant may keep the oil in a suspension returning it to the compressor.

$900 for a 4 ton loop INEXPENSIVE!! like you have found no circ. pumps, no heat exchangers, no propylene glycol $$, heat pump nirvana!! Pure efficiency!!

Randen
randen is offline   Reply With Quote
Old 07-25-15, 01:07 PM   #60
MEMPHIS91
Journeyman EcoRenovator
 
MEMPHIS91's Avatar
 
Join Date: Apr 2015
Location: Oxford, MS USA
Posts: 496
Thanks: 69
Thanked 87 Times in 61 Posts
Default

Randen, thanks. In fact I already have a perfect window unit just waiting for this project. Though after Jeff told me about the oil separator , I am convinced oil will not be the problem. It will give me more Peace of mind if no oil is in the coil without a separator. I really need to know sizing of the pond loops. And this test should help with that.

I am thinking now that 2 oil separators back to back will make sure I get no oil in the pond loops. Been reading articles that are saying the oil is bad in a DX system anyway because it coats the inside of the tubing and blocks heat loss.
What are the thoughts on using an oil that is not soluble in propane. If the refrigerant doesn't pick up as much oil from the compressor because it doesn't mix with it, I would think that's a good thing right? And I would think that the oil separator would work better. There are a bunch of "I thinks" in the last paragraph. I've got allot more studying to do.
Thanks for all the feedback guys.

MEMPHIS91 is offline   Reply With Quote
Reply



Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 01:33 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design