Quote:
Originally Posted by gtojohn View Post
yes combustion air from outside the conditioned space is definitely the way to go. Each Cubic foot of gas requires 10 cubic feet of air, so 100kbtu would exchange all the air in your house several times over. Thats why outside combustion air is part of the energy code. Mine are located in the unconditioned open air attic crawl space so there's no loss there. What I suggest is preheating the combustion air which presumably you are bring in from outside, which is colder because you are running the heater. You already have a flue and need combustion air why not preheat it? Testing a double wall flue last week, 3' from the furnace still very hot, couldn't keep my hand on it. about 4' from it it was warm to touch, maybe 100-105f. If I wanted to get max heat out of it I'd use single wall vent. Unfortunately winter's over here, my hvac has been off for almost a month, so might not happen for me until fall. Maybe someone in a colder climate might want to try it before then.
Would it? 100kBTU is 1ccf or 100 cubic feet, so based on your numbers, that would be 1000 cubic feet of combustion air. That would be an air exchange for 125 square feet. 24 hours of continous runtime for a 100kBTUhr unit would be 24,000 cubic feet which would be a single air change for 3000 square feet. Figuring that this system is probably oversized and I figure it wouldn't even run 1/3 the time of a day, that would an air exchange for a 1000 square foot building. That doesn't seem like many times over.

Granted, it is still an unwanted air exchange and I'd prefer it be sourced from the outside too, but it isn't as much air as you are implying.
MN Renovator is offline   Reply With Quote
The Following User Says Thank You to MN Renovator For This Useful Post:
Servicetech (03-15-16)
 


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 05:55 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design