Default $2000.00 gshp

Johnnypeste

Unless the current radiators are fan-forced there is not enough heat available to make your living space comfortable. The heat pump produces a water temp. around 40 Deg. C. And this may not be enough for a convection type of radiator. However a fan forced radiator may be enough but it would run longer on a low speed setting which may do the job and keep you comfortable.

I had installed a fan center (fan behind radiator)with DIY GSHP in my shop and its working extremely well saving a ton of money. I used to burn dinosaurs as well. Diesel $2800 for heat. Heat-pump less than $1000.00 for a year

Ground source heat pumps coupled with in-floor heating is the holy grail IMHO and is very economical. However the house must be well insulated and sealed against fresh air blowing through it. $2000.00 for a complete system even DIYed might be a little optimistic if you include the ground loop.

I'm not sure of your climate in Portugal but the Mini-split heat-pumps look very interesting.

As you are starting to understand we are entering an interesting time. Solar panels coupled to heat-pump keeping the family home warm.!!! Although its a little simplified in that statement but its now being done.

Randen

randen is offline   Reply With Quote
Old 10-17-15, 10:07 AM   #1762
johnnypeste
Lurking Renovator
 
Join Date: Oct 2015
Location: portugal
Posts: 6
Thanks: 0
Thanked 0 Times in 0 Posts
Default

So for what i understood you are saying i should forget the radiators and gshp and go for n mini split heat pumps in each n division of the house? The climate outside is -10 C in the worst winter day. Its a pitty not being able to save the radiators...
johnnypeste is offline   Reply With Quote
Old 10-17-15, 06:39 PM   #1763
johnnypeste
Lurking Renovator
 
Join Date: Oct 2015
Location: portugal
Posts: 6
Thanks: 0
Thanked 0 Times in 0 Posts
Default

Do you recommend any mini split brand in particular?
johnnypeste is offline   Reply With Quote
Old 10-17-15, 06:51 PM   #1764
Mikesolar
Master EcoRenovator
 
Mikesolar's Avatar
 
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
Default

Don't get rid of the rads. Keep them as a second stage for really cold days. Turn the boiler max temp down to 50C and see if it will still provide the heat you need.. Oil usually needs a higher water temp but it all depends on how much m3 of radiator you have.

Use a Fujitsu or Mitsubishi ductless where you can, in the bigger rooms, You may need 2 of them for 200m2 house. These are be best performing units (highest efficiency) and the 3.5-4kw ones are the best. Really, you should have a heat loss done on the house to determine what size to use.
Mikesolar is offline   Reply With Quote
Old 10-18-15, 01:34 AM   #1765
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by johnnypeste View Post
So for what i understood you are saying i should forget the radiators and gshp and go for n mini split heat pumps in each n division of the house? The climate outside is -10 C in the worst winter day. Its a pitty not being able to save the radiators...
Most people make the mistake of initially focusing on getting a heating source, rather than preventing heat loss. Retaining heat is less expensive and less damaging to the environment than creating heat.

The place to start is to quantify your heat loss. There are many ways to do this, but here is a pretty good way to do it for free:

Home Heat Loss Calculator

...the units are US, but conversion shouldn't be too bad.

Your biggest loss is usually air infiltration, then the next is insulation.

As I understand, your energy costs are twice what they are in North America. This make a big difference in your heating project. You should carefully consider the advice you get from this side of the pond, and calculate for yourself what makes best value for the money given your local economy.

From what I understand, higher-cost, but higher-efficiency heating systems pay for themselves faster where you live, than they do in North America.

The whole idea behind the Heat Pump Manifest thread, is that you can greatly reduce the cost of a ground source heat pump system if you do the work yourself. That is the reason that the thread you are now posting to was created, to encourage people to build their own systems.

'Randen' who is one of the people who responded to your question, is probably the best example of someone who has actually followed through and built his own working ground source heat pump systems. His system costs him about 25% per year to run, compared to what he payed before when he heated with oil. It was a lot of work for randen to do what he did, and he nearly gave up more than once. But he persisted, and now he has both the satisfaction of saving a lot of money each year, but also the pride in designing and building his own, unique system.

'Mikesolar' has years of experience in, and is very knowledgeable about the home heating industry in which he works, but to my knowledge, he has not built his own ground source heat pump system.

They both have great expertise in their past, that is highly relevant to your questions.

If you think you may be interested in building your own Ground Source Heat Pump system, this thread is for you, and you are welcome to be here, as this thread is for people who have made up their minds that they want to build a homemade heat pump system, and need help and advice to do it.

If you are considering a more conventional approach, that does not involve a homemade heat pump, I invite you to create a new thread where your concerns and ideas can be discussed by the entire EcoRenovator community.

I try to keep this thread, that I call the 'Manifesto' thread, focused on homemade ground source heat pump systems.

As far as I know, there is no other place on the entire Internet where Homemade Heat Pump systems are openly discussed.

I hope that you understand and respect the thread you are now posting to.


Sincerely,

-AC_Hacker
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
Old 10-18-15, 04:06 AM   #1766
johnnypeste
Lurking Renovator
 
Join Date: Oct 2015
Location: portugal
Posts: 6
Thanks: 0
Thanked 0 Times in 0 Posts
Default

I understood this is a special project. I have made a direct question. If it was possible to use the same radiators i already have. It seems its not. Sorry for disturbing. Best regards
johnnypeste is offline   Reply With Quote
Old 10-19-15, 08:23 AM   #1767
Pegasus
Lurking Renovator
 
Join Date: Feb 2012
Location: Greece
Posts: 13
Thanks: 3
Thanked 3 Times in 2 Posts
Default GSHP Project back to life !!!

Hello to all,

After many setbacks I finally made it to built my "proof of concept" GSHP.
My main concern was the output of the GS HX Loop (~ 500m of pipe, divided in 6 circuits and buried at ~ 2m depth under the house foundation). The main consept was to test the Ground Loop with the least amount of money, while getting in to the nuts and bolts of a GSHP.

The contraption is consisted by :
- Compressor : R22 2,9KW - 0.85 Ton from an old A/C (COP 3.5)
- Condenser : The A/C condenser coil submerged into a barrel where the Ground Loop water circulates (I can get a proper plate HX costs about 300 Euros)
- Metering Device : R22 Danfos adjustable TXV that can handle the compressor cooling capacity.
- Evaporator : 2 x plate HX ( I used both because they are small. Wrong e-bay order)
- Refrigerant : Initially R-22 then R-290
- Extras : LP+HP Safety switch, Refrigerant HX, Filter - Dryer (for R-407)

All welded together with awful craftsmanship (unlike randen) and put to the test.

During my GSHP study period I have found a very helpful book for beginners in the HVAC world like me (attached in the post). It is written for fridge truckers in plain English. It also has a very easy troubleshooting guide that the most experienced of you could quantify for R-290 GSHPs, check it out.

I am writing this because my main problem is that I can't lower SH below 6 deg C so that to use all of the Evaporator capacity. From the above troubleshooter my case is (most likely) the liquid line restriction and my best guess is the small orifice that I chose since I didn't took under consideration the increased COP.

As far as the Ground Loop, I believe it can handle a bigger compressor since the return temp is only 2 deg above the no load temp (25 --> 27) so it is a go for a proper set-up.

Any comments would be helpful.

P.S. There is a very nice "Refrigerant Slider" free app from Danfos that includes R-290!
Attached Thumbnails
Click image for larger version

Name:	IMG_20151018_154715.jpg
Views:	682
Size:	468.1 KB
ID:	6112   Click image for larger version

Name:	IMG_20151018_154657.jpg
Views:	663
Size:	374.6 KB
ID:	6113   Click image for larger version

Name:	IMG_20151018_154731.jpg
Views:	634
Size:	371.7 KB
ID:	6114   Click image for larger version

Name:	IMG_20151018_154801.jpg
Views:	609
Size:	377.9 KB
ID:	6115   Click image for larger version

Name:	IMG_20151018_155956.jpg
Views:	601
Size:	429.8 KB
ID:	6116  

Click image for larger version

Name:	IMG_20151018_155944.jpg
Views:	552
Size:	441.5 KB
ID:	6117   Click image for larger version

Name:	IMG_20151018_160053.jpg
Views:	571
Size:	358.0 KB
ID:	6118   Click image for larger version

Name:	IMG_20151018_191712.jpg
Views:	584
Size:	348.0 KB
ID:	6119  
Attached Files
File Type: pdf Refrigeration-Mannual.pdf (1.86 MB, 585 views)
Pegasus is offline   Reply With Quote
The Following 2 Users Say Thank You to Pegasus For This Useful Post:
jeff5may (10-20-15), pinballlooking (10-19-15)
Old 10-19-15, 08:32 AM   #1768
paramax55
Lurking Renovator
 
Join Date: Sep 2015
Location: Florida
Posts: 3
Thanks: 0
Thanked 0 Times in 0 Posts
Default

I have seen more and more posts with the idea of using mini splits. They are probably not the best choice for a DIY ground source heat pump. They are incredibly efficient and the off-brand ones are a fraction of the brand-name units. Yet they are not found all over the place and I figured there had to be a reason why. I asked a commercial AC guy (big company - high dollar) and my suspicions were confirmed. He said that they are noisy (I already knew that). While they can be reliable and last a long time, they can be troublesome when you first install them. When they break, there is also a shortage of people who can troubleshoot them and fix them. They are computer controlled and usually you have to find the bad board and replace the whole thing.

As far as hacking goes, it's all three phase motors. What you would need to do is rip out all of the electronics and install your own three phase motor controllers - similar to the idea of hopping up a modern sports car with twin turbos or something and controlling your engine with a "stand alone" engine management system.

The computer has algorythms to figure out how hard it needs to work to maintain a temperature in a room and then only runs at that level. It can balance the compressor for cooling (or heat) level, then balance the condenser fan for subcooling and evaporator fan for superheat. You would need to control these three variables for the level of heat transfer that you want.

This could be done if someone wanted to do it - anything is possible - but it's probably not good to jump in to that on the first try. There is so much more to a GSHP project that it probably makes sense to learn to crawl before learning to run. A hacked-up AC can be done so easily and cheaply that you wouldn't loose anything if you later switched to a mini-split and threw your initial project away after a year. But you would never do that.

The GSHP will be so much more efficient than other forms of heat transfer, you'll probably see no reason to go through the trouble of hacking a mini-split.
paramax55 is offline   Reply With Quote
Old 10-19-15, 10:41 AM   #1769
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by Pegasus View Post
After many setbacks I finally made it to built my "proof of concept" GSHP. My main concern was the output of the GS HX Loop (~ 500m of pipe, divided in 6 circuits and buried at ~ 2m depth under the house foundation). The main consept was to test the Ground Loop with the least amount of money, while getting in to the nuts and bolts of a GSHP.
Pegasus,

Congratulations on moving on to the testing stage!

There are many others on EcoRenovtor who are much more experienced than I am about fine adjustment of a compressor system.


Your photos are great. I can see in the background of the photos, some of the details of your ground loop setup. Very interesting to see that you have built in valves for each segment of your ground loop. Very useful for purging and also it allows you to isolate each segment, should you need to test through your loop array, to locate some problem.

Quote:
Originally Posted by Pegasus View Post
...The A/C condenser coil submerged into a barrel where the Ground Loop water circulates (I can get a proper plate HX costs about 300 Euros)
Plate HXs are great. The price you are quoting seems to me to be a bit high. EBAY is a wonderful source for low price plate HXs. If you check for a proper plate HX often, you should be able to find what you want. EBAY is a waiting game. A R290 system will have lower pressure, so that opens more possible choices when looking for the perfect HX.

Quote:
Originally Posted by Pegasus View Post
During my GSHP study period I have found a very helpful book for beginners in the HVAC world like me (attached in the post).
You are right! Very clearly written. Perfect for beginners. I have added it to my personal library.


Quote:
Originally Posted by Pegasus View Post
As far as the Ground Loop, I believe it can handle a bigger compressor since the return temp is only 2 deg above the no load temp (25 --> 27) so it is a go for a proper set-up.
You may well be right about a bigger compressor being able to extract more heat.

There is a factor to keep in mind, which is the possibility of your ground source gradually cooling (over a period of years). Your ground source ultimately receives its heat from the sun. In your case, the surrounding earth will be warmed by the sun and will conduct their heat gradually into the earth that is your loop field.

The factors that determine long-term decline are complex. The best thing is to monitor and record the yearly loop temperature as the season progresses, and keep an eye on any long-term temperature decline.

If you are using your system for cooling, the same is true, in reverse.

Quote:
Originally Posted by Pegasus View Post
P.S. There is a very nice "Refrigerant Slider" free app from Danfos that includes R-290!
I want to see this one!

Best,

-AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
Old 10-19-15, 11:12 AM   #1770
pinballlooking
Super Moderator
 
pinballlooking's Avatar
 
Join Date: Jun 2013
Location: SC
Posts: 2,923
Thanks: 172
Thanked 564 Times in 463 Posts
Default

Thanks for posting the document. I will be reading through it in detail. I hope to be doing a Heat Pump water heater for my fish tank later this winter.

pinballlooking is offline   Reply With Quote
Reply


Tags
air conditioner, diy, gshp, heat pump, homemade

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 03:59 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design