Originally Posted by Blauhung View Post
Ok, for drilling starting to think about the possibility of finding a used treadmill. Motors in those are ~2HP and with the whole thing i've got a DC power supply and PWM speed controler in the package.
Damn! Clever!

Will it cut stone?

S-F is offline   Reply With Quote
Old 05-02-11, 08:00 PM   #722
randen
Uber EcoRenovator
 
Join Date: Apr 2011
Location: Strathroy Ontario Canada
Posts: 657
Thanks: 9
Thanked 191 Times in 129 Posts
Default

Is anyone up for a discusion on the pros-cons flat plate HX vs copper Aqua Systems efficient Liquid to Refrigerant Heat Exchangers HX both are about the same money but maybe the copper wins over the stainless??
One other detail I had seen was the reverse valve in a GSHP caused a parallel flow condition through the HX reducing the efficiency as opposed to the counter-flow.

Thanks Randen
randen is offline   Reply With Quote
Old 05-02-11, 10:04 PM   #723
Blauhung
Lurking Renovator
 
Join Date: Feb 2010
Location: Portland, OR
Posts: 27
Thanks: 0
Thanked 0 Times in 0 Posts
Default

Quote:
Originally Posted by S-F View Post
Damn! Clever!

Will it cut stone?
may not cut stone, but if all you need to do is push them out of the way it may work. My thought is to gear the motor way down so you favor high torque as opposed to high RPM. Running at 30 RPM might be slow, but a 1 horse motor at 30 RPM is 175ft-lbs of torque. would need a beefy frame to hold it.
Blauhung is offline   Reply With Quote
Old 05-03-11, 10:07 AM   #724
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by randen View Post
Is anyone up for a discusion on the pros-cons flat plate HX vs copper Aqua Systems efficient Liquid to Refrigerant Heat Exchangers HX both are about the same money but maybe the copper wins over the stainless??
If you are using a HX in an open source configuration (pump & dump, hot water loop also being used for DHW, etc) then accumulation of minerals or particles (AKA: scaling) would be a deal-breaker for Brazed Plate.

I don't think that the copper vs. stainless would be such an issue since the stainless layers are so thin, but if you did a BTU/$ calculation, that should tell you what you need to know.


Quote:
Originally Posted by randen View Post
One other detail I had seen was the reverse valve in a GSHP caused a parallel flow condition through the HX reducing the efficiency as opposed to the counter-flow.
Do you know how large a difference the parallel flow issue makes? It may be too small to make much difference.

But you should make sure that you have counter flow in the mode that you will be using most. I would suspect that AC mode would be secondary for you.

-AC_Hacker

Thanks Randen[/QUOTE]
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
Old 05-03-11, 10:19 AM   #725
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by Blauhung View Post
Ok, for drilling starting to think about the possibility of finding a used treadmill. Motors in those are ~2HP and with the whole thing i've got a DC power supply and PWM speed controler in the package.
Great idea!

Now you just have to come up with a good, strong speed reducer.

I really think 30 rpm is too slow... I get the torque idea, but somewhere around 60 to 120 rpm would be good.

And don't under estimate the part that the mud pump plays. It's not just for lubrication, it lifts the cuttings, clears the drill bit, and even erosion plays a part in the process. So you want a continuous, copious supply of mud.

The mud pump is a really important part of the tool.

-AC_Hacker
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
Old 05-03-11, 10:02 PM   #726
tweeker
Green Energy Pioneer
 
Join Date: Apr 2011
Location: Pennsylvania
Posts: 16
Thanks: 1
Thanked 1 Time in 1 Post
Default

I just got home from testing the Fedders 5K unit Compressor for it's BTU waste heat output.

I encapsulated/submerged the Fedders A/C Unit compressor, up to just a 1/2" below the electrical contact access caps on the top, in a container filled with water, in an 8 inch diameter PVC pipe cap and an additional 6 inches of aluminum flashing to top it off.

Just the compressor, @ 400 Watts was producing approx 900 BTU's an Hour.

So, if I were to insulate the top 6" of aluminum flashing, I think I could get 1200 BTU's an Hour @ 400 Watts just from the compressor, meaning the 5,000+ BTU's of heat generated by the condenser, could mean that this 5,000 BTU's from the Condenser would be the pay off ?

Captured the BTU's from the electricity used for the compressor, and 5,000 FREE BTU's in BONUS POINTS from the Condenser ?

Hmmmmm ? ? ? Need to do more tests ! Very Interesting :-)
tweeker is offline   Reply With Quote
Old 05-03-11, 10:37 PM   #727
tweeker
Green Energy Pioneer
 
Join Date: Apr 2011
Location: Pennsylvania
Posts: 16
Thanks: 1
Thanked 1 Time in 1 Post
Default

Hi Randen,

my limited experience with HX's, is that all parts are not equal according to the brochures, BUT having 10 times the area to dissapate the Heat/Cold in order to dissapate the fabricated energy hydronically into a air filled living area is my rile of thumb.

If I have a 1.5 Square Foot (S.F.) Condensor with TWO 1 S.F. heat exchangers (2 S.F.) in the same container, and transfering the working fluid in the container by a thermally low conductive pipe (CPVC) to a hydronic HX (heat exchanger) made of Copper, I would consider using approx 15 S.F. of HX area, or an equivalent mass cross section area, assisted by a low RPM, low Watt fan.
Just my opinion.

Tweeker
tweeker is offline   Reply With Quote
The Following User Says Thank You to tweeker For This Useful Post:
pinokio (05-16-11)
Old 05-04-11, 02:17 AM   #728
randen
Uber EcoRenovator
 
Join Date: Apr 2011
Location: Strathroy Ontario Canada
Posts: 657
Thanks: 9
Thanked 191 Times in 129 Posts
Default

Hello Tweeker

Thankyou for your input. The two HX I'm considering is the stainless plate HX vs the copper co-axil wound Aqua System used to exchange heat energy from the refrigerant to the water/glycol of the ground loop. The two seem so closely matched for there performance maybe AC Hacker has hit the nail on the head with BTU/$ calculation. But thats a close match as well. The cost for a 3T HX is about $160.00 for each.

Thanks Randen
randen is offline   Reply With Quote
Old 05-04-11, 04:42 PM   #729
tweeker
Green Energy Pioneer
 
Join Date: Apr 2011
Location: Pennsylvania
Posts: 16
Thanks: 1
Thanked 1 Time in 1 Post
Default

Wow, only $160 for a 3T HX. Which model are you referring to.

I have an old Copper Solar Flat panel HX that is 7' 9" X 34", Basically 23 S.F. I use it for hydronic heating and cooling in the living area. If I had to buy the 3/8" copper tubing to make a similar panel, then add the copper sheeting between the tubes, I think my estimate was something like $500 for just the copper materials, I got 3 of them from a recycling center for $200 EACH a couple years ago, when copper was lower in price, they weigh about 50-60 Lbs a piece. I think they were OLIN Flat Panels, I don't have any parts from the rest of the panels, it was all aluminum and I scrapped it this year.
tweeker is offline   Reply With Quote
Old 05-05-11, 04:18 PM   #730
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default AC_Hacker post for tweeker...

AC_Hacker posting pics for tweeker...

>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>> >>
Tests revealed that the Fredders Compressor was running HOT. So I thought it would be a good IDEA to see just how much HEAT I might beable to recover from the Fredders Compressor. So I took a roll of 3/16" copper coil I had squirreled away and made a coil that would screw on and wrap around the Fredders compressor.


Stages of the Compressor heat recovery Coil installation Part 2


Stages of the Compressor Coil installation Part 1


>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>> >>

End of post.

tweeker,

If you want more pictures posted, you're going to have to do it yourself, or find someone else to do it for you...

Somehow I thought you lived here in Portland Oregon. I'm not inclined to go to Pennsylvania to show you how to post pics.

-AC_Hacker

Attached Thumbnails
Click image for larger version

Name:	tweeker-1.jpg
Views:	4619
Size:	97.0 KB
ID:	1456   Click image for larger version

Name:	tweeker-2.jpg
Views:	3560
Size:	91.6 KB
ID:	1457   Click image for larger version

Name:	tweeker-3.jpg
Views:	3014
Size:	92.4 KB
ID:	1458  
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
Reply


Tags
air conditioner, diy, gshp, heat pump, homemade

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 06:27 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design