Old 05-08-14, 02:45 PM   #111
buffalobillpatrick
Master EcoRenovator
 
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
Default

ODR is not perfect, it does not take into account several things:

Wind & thus infiltration, and clear cold night radiation into space.

I have designed & tested an Outdoor sensor that takes both factors into account.

It consists of a small slightly heated steel box, like a very very small house.

It reacts to wind & night radiation in that both cause cooling below air temperature.

It's normal temperature is 10* F above ambient, so this must be adjusted for when setting up ODR parameters.


Last edited by buffalobillpatrick; 05-08-14 at 02:58 PM..
buffalobillpatrick is offline   Reply With Quote
Old 05-08-14, 02:55 PM   #112
buffalobillpatrick
Master EcoRenovator
 
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
Default

NiHaoMike,

"Even better is to only raise the tank temperature using the heat pump if it's not keeping up with demand. "

A heat source not keeping up with demand, is an issue that I haven't worked out yet.

Kind of like, when to down shift going up a hill.

I could do a time delay & check status to determine if gaining or loosing ground.

Sources of info such as:

http://www.geoexchange.org/forum

Recommend 2 tanks with desuperheater.

I believe that buffering is necessary between heat source & sink.

My 2 ton HP will, in all cases, output more heat than any 1 or 2 hydronic zones require.

Some buffering will take place in slab floors, but unlike some French systems I've read about, I don't want to overshoot room thermostat for a bit of eff.

I have some nice PID Tekmar thermostats that have a air sensor & a slab sensor to help prevent over & under shoot.

Last edited by buffalobillpatrick; 05-08-14 at 03:20 PM..
buffalobillpatrick is offline   Reply With Quote
Old 05-08-14, 03:57 PM   #113
NiHaoMike
Supreme EcoRenovator
 
NiHaoMike's Avatar
 
Join Date: Oct 2008
Location: Austin, TX
Posts: 1,154
Thanks: 14
Thanked 257 Times in 241 Posts
Default

You could measure the derivative of the space temperature and see if it's going up or down. It would probably be necessary to do some filtering to prevent noise from causing false triggering.
__________________
To my surprise, shortly after Naomi Wu gave me a bit of fame for making good use of solar power, Allie Moore got really jealous of her...
NiHaoMike is offline   Reply With Quote
The Following User Says Thank You to NiHaoMike For This Useful Post:
buffalobillpatrick (05-08-14)
Old 05-08-14, 06:02 PM   #114
buffalobillpatrick
Master EcoRenovator
 
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
Default

Trying to chase room(s) air stats with buffer tank temp. Would cause big over/undershoot.
buffalobillpatrick is offline   Reply With Quote
Old 05-08-14, 06:48 PM   #115
NiHaoMike
Supreme EcoRenovator
 
NiHaoMike's Avatar
 
Join Date: Oct 2008
Location: Austin, TX
Posts: 1,154
Thanks: 14
Thanked 257 Times in 241 Posts
Default

As I've designed it, as soon as the heat pump starts up, the heat output is immediately used for the floor heating (with the remainder going into the tank) so the response is almost instant. The floors are going to have a lot of thermal mass (much higher than the room air in a more common air type heat pump) and the system would have a lot of time to respond.

If you're trying to get very precise temperature regulation, you'll likely need to use a VFD. But I'm pretty certain it would work more than good enough without one.

__________________
To my surprise, shortly after Naomi Wu gave me a bit of fame for making good use of solar power, Allie Moore got really jealous of her...
NiHaoMike is offline   Reply With Quote
The Following User Says Thank You to NiHaoMike For This Useful Post:
buffalobillpatrick (05-12-14)
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 12:11 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design