Old 07-17-13, 04:09 PM   #31
ELGo
Helper EcoRenovator
 
Join Date: Apr 2013
Location: Albuquerque
Posts: 66
Thanks: 4
Thanked 3 Times in 3 Posts
Default

Quote:
Originally Posted by AC_Hacker View Post
But the relationship is not linear, because area increases at roughly a square function, and volume increases at roughly a cubic function... and heat loss is proportional to area.
You are right with large numbers to focus on the exponents, but consider e.g. a rectangle that is elongated in height by 50%:

The surface area increases from
2xy + 2xh + 2yh to
2xy + 3xh + 3yh

While the volume increases from xyh to 1.5xyh.

Not that far off from linear in this range.

By the way, what is the temperature gradient in your fridge from bottom to top ? I'm wondering if extra external insulation on the top of the fridge would have much of an effect.

ELGo is offline   Reply With Quote
Old 07-17-13, 05:34 PM   #32
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by ELGo View Post
You are right with large numbers to focus on the exponents, but consider e.g. a rectangle that is elongated in height by 50%:

The surface area increases from
2xy + 2xh + 2yh to
2xy + 3xh + 3yh

While the volume increases from xyh to 1.5xyh.

Not that far off from linear in this range.
If the size of the refrigerators was determined by a chainsaw, this would be correct, but smaller refrigerators tend to become narrower, and sometimes shallower, too.

Quote:
Originally Posted by ELGo View Post
...By the way, what is the temperature gradient in your fridge from bottom to top ? I'm wondering if extra external insulation on the top of the fridge would have much of an effect.
Yes, it would have a very significant effect.

My Freezerator, as most of the currently produced units, have the integral coils, and the outside surfaces become the heat radiating surface... the top, the two sides, and the back, all have integral coils. So to insulate would have a negative impact on efficiency.

Personally, I think that the integral coils feature costs the planet a huge amount of CO2. Only reason for it that I can imagine is that the coils are much less likely to be damaged during shipping. After shipping, it's down hill.

-AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...

Last edited by AC_Hacker; 07-17-13 at 05:39 PM..
AC_Hacker is offline   Reply With Quote
Old 07-19-13, 03:41 AM   #33
oil pan 4
Land owner
 
Join Date: Nov 2012
Location: NM
Posts: 1,026
Thanks: 12
Thanked 127 Times in 107 Posts
Default

The current refrigerator we are using is consuming upwards of 5 kwh a day.
I think something is very wrong.
oil pan 4 is offline   Reply With Quote
Old 07-19-13, 05:19 PM   #34
stevehull
Steve Hull
 
Join Date: Dec 2012
Location: hilly, tree covered Arcadia, OK USA
Posts: 826
Thanks: 241
Thanked 165 Times in 123 Posts
Default

Just thinking here - and provoking AC to give us some thoughts (others too).

Clearly a square box is the simplest way to maximize volume with the smallest surface area (OK, I don't need smart *** comments on this really being a sphere!).

But if we were to built, from scratch, a 'fridge, how would we do it?

I bet we would build a modified rectangle, trying to be close to a cube, but wary of the deep recesses in back where "food goes to die" (quoting AC).

I bet we would choose an external "radiator" with stand offs and not one inside the metal cabinet - likely on the back (assuming an air to air compressor system).

I bet we would insulate with at least two inches of high performance foam (R10 per inch) and I bet we would forgo a freezer to maximize compressor performance with an interior temp of about 40 F.

Since the volume is small, how much water flow would it take to make this a water source compressor type fridge? I bet less than a fraction of a gallon per minute. (I know that as I use a rule of thumb of about 1-2 gallons/minute of water flow per 12,000 BTU of cooling.

Assume a 30 degree delta T with a house temp of 70 F (inside fridge temp of 40F).

Assume an outside 'fridge dimension of 4 feet tall, 3 feet wide and 2.5 feet deep (total surface area of 39 sq feet)

Given the above, what would it take to build this? I don't have my calculator available or I would calculate the net amount of BTUs needed to keep it at this design temp.

I bet a tiny compressor would be needed and a quart of water per minute (assuming an open loop system with a ten F delta T from water well temp to outflow temp.

Now, where could I get a fractional compressor real cheap . . . . (a compressor from a window AC unit would be far too big, same with auto and dehumidifier . . . .).

We all need a 'fridge and I bet this would not be a hard nut to crack!

Just thinking . . . .

Steve
__________________
consulting on geothermal heating/cooling & rational energy use since 1990
stevehull is offline   Reply With Quote
Old 07-19-13, 08:05 PM   #35
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by stevehull View Post
Just thinking here - and provoking AC to give us some thoughts (others too).

Just thinking . . . .

Steve
Good thinking here.

I've done some serious looking into available compressors (probably no surprise there), and small refrigerator compressors are available in the 100 to 200 watt size. Trouble with them is that they use a very strange coaxial cap tube arrangement that seem to me to be difficult to hack, or duplicate. I wouldn't want to discourage anyone from trying, but I was not able to visualize an easy solution. If this cap tube thing could be overcome, the size of the compressor just might be perfect.

On the other hand, very small compressor-type dehumidifiers (as opposed to peltier-junction) can be found. The smallest that I have seen in the wild is a 25 pint per day... which was the guts for my first heat pump. I know that Sears sells a 20 pint per day, with a really small compressor... smallest I know of. The dehumidifier will have a conventional cap tube that will be easy to salvage and re-use.

So, if you're going to do this right, the compressor & condenser should sit on top of the unit, for best efficiency... just like the very first home refrigerators.



Sunfrost uses this kind of arrangement... and their efficiency is legendary... but they haven't brought a water-source unit to market.

I think a good place to start would be to find some kind of pre-made plastic container that would be the right size for the inside of the refrigerator, and build upon that.

Best,

-AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
Old 07-20-13, 02:20 AM   #36
oil pan 4
Land owner
 
Join Date: Nov 2012
Location: NM
Posts: 1,026
Thanks: 12
Thanked 127 Times in 107 Posts
Default

I agree, stuffing the compressor and condenser up under the fridge is stupid.
Over sized passive coils along the back or top coils are best, it almost seems if their engineers forgot about convection.
oil pan 4 is offline   Reply With Quote
Old 07-20-13, 06:45 AM   #37
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

Most of the newer (plastic) dehumidifiers are run by either a 4000 or 6000 btu compressor and use R22. The older (metal) dehumidifiers use R12 (ancient) or R134a (old) and have the size compressors in them you are looking for. I have seen a few with mini-fridge style compresssors in them that only draw 150 watts (including the fan). They run much more silently than the newer units. Check freecycle or craigslist in your area.
jeff5may is offline   Reply With Quote
Old 07-20-13, 12:23 PM   #38
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by jeff5may View Post
...Most of the newer (plastic) dehumidifiers are run by either a 4000 or 6000 btu compressor and use R22...
By "newer", you must be referring to newer used equipment.

R22 equipment is no longer allowed to be sold as new.

But the R22 used stuff is a very good fit for R290, and that makes it very attractive.

-AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
Old 07-24-13, 07:05 PM   #39
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default Freezerator Update...

I was looking about for a spare Kill-a-Watt, when I realized that I had left one attached to the Freezerator since March (1705 hours to be exact).

So I ran the numbers from the stored data (28.08 kw-h), and I am pleased to say that the average power use calculates to:

395.26 watt-hr/day

(about 1/12th of what oil_pan_4 is pulling from his refrigerator)

It did rise a bit (see photo below) because of the higher ambient temp, but I think that it is really quite respectable.

-AC

__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...

Last edited by AC_Hacker; 07-24-13 at 07:11 PM..
AC_Hacker is offline   Reply With Quote
The Following User Says Thank You to AC_Hacker For This Useful Post:
Daox (07-25-13)
Old 07-25-13, 07:52 AM   #40
Daox
Administrator
 
Daox's Avatar
 
Join Date: Aug 2008
Location: Germantown, WI
Posts: 5,525
Thanks: 1,162
Thanked 374 Times in 305 Posts
Default

Very nice. That is about 1/3rd what my fridge uses.

__________________
Current project -
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.



To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
&
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
Daox is offline   Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 03:44 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design