EcoRenovator  

Go Back   EcoRenovator > Improvements > Conservation
Advanced Search
 


Blog 60+ Home Energy Saving Tips Recent Posts Search Today's Posts Mark Forums Read


Reply
 
Thread Tools Display Modes
Old 08-12-14, 05:51 PM   #1
BillS111
Lurking Renovator
 
Join Date: Aug 2014
Location: Boston
Posts: 7
Thanks: 6
Thanked 0 Times in 0 Posts
Default Seeking window mounted (or DIY) ERV or HRV solution

Hello - I live in a rental, so i am not allowed to do duct work or wall work.

Does anyone know of an HRV or ERV system that can be window mounted, like an a/c? Or is there a 'workaround' DIY solution where i could take one of the 'duct-work required' units and just sit it on a table, running ducts through a window?

My goal is to keep the Co2 ppm in the low 400s in a 300 sq ft apt, does anyone know the CFM rating that would be needed for this?

Thanks!

BillS111 is offline   Reply With Quote
Old 08-12-14, 06:32 PM   #2
Daox
Administrator
 
Daox's Avatar
 
Join Date: Aug 2008
Location: Germantown, WI
Posts: 5,525
Thanks: 1,162
Thanked 374 Times in 305 Posts
Default

Welcome to the site Bill.

Have you measured your CO2 levels and see them exceeding them? If so I'd say you're pretty lucky to rent a place that is that efficiently built!
__________________
Current project -
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.



To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
&
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
Daox is offline   Reply With Quote
The Following User Says Thank You to Daox For This Useful Post:
BillS111 (08-12-14)
Old 08-12-14, 06:42 PM   #3
BillS111
Lurking Renovator
 
Join Date: Aug 2014
Location: Boston
Posts: 7
Thanks: 6
Thanked 0 Times in 0 Posts
Default

Quote:
Originally Posted by Daox View Post
Welcome to the site Bill.

Have you measured your CO2 levels and see them exceeding them? If so I'd say you're pretty lucky to rent a place that is that efficiently built!
Daox - thank you! Glad to be here!

Yes, the Co2 ppm gets as high as 600 (there are other people in the house in other rooms). I can keep the ppm at about 425 with the windows open all summer, but obviously that's going to be a problem come fall and winter.
BillS111 is offline   Reply With Quote
Old 08-12-14, 07:12 PM   #4
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 724 Times in 534 Posts
Default

Quote:
Originally Posted by BillS111 View Post

My goal is to keep the Co2 ppm in the low 400s in a 300 sq ft apt, does anyone know the CFM rating that would be needed for this?

Thanks!
Do you actually have a CO2 measuring device?

I built a CO2 detecting HRV controller, and I know what CO2 levels actually look like in an urban environment.

Your target level is pretty optimistic, but it is doable. Your air exchange rates will be pretty high.

There is a DIY HRV thread that features lots of brave and creative HRVs that could be window adapted.

Wishing you success with your project, and take loads of photos!

Best Luck,

-AC_Hacker
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
The Following User Says Thank You to AC_Hacker For This Useful Post:
BillS111 (08-12-14)
Old 08-12-14, 07:20 PM   #5
BillS111
Lurking Renovator
 
Join Date: Aug 2014
Location: Boston
Posts: 7
Thanks: 6
Thanked 0 Times in 0 Posts
Default

Quote:
Originally Posted by AC_Hacker View Post
Do you actually have a CO2 measuring device?

I built a CO2 detecting HRV controller, and I know what CO2 levels actually look like in an urban environment.

Your target level is pretty optimistic, but it is doable. Your air exchange rates will be pretty high.

There is a thread that features lots of brave and creative HRVs that could be window adapted.

Wishing you success with your project, and take loads of photos!

Best Luck,

-AC_Hacker
Thank you so much! I will check out those threads.

The ambient Co2 where i am is at 400ppm during the day. So i would love to mimic that as close as possible.

I used the ASHRAE formula for Co2 ppm. Here: b3mn dot org/guidelines/archive/version2_1/downloads_v2_1/5IEQ_App-I-2_V2-1.pdf

According to this, if i want 420 ppm, i will need about 550 CFM. Does that sound about right?

Thanks!

ps - yes, i have a Co2 meter
BillS111 is offline   Reply With Quote
Old 08-12-14, 08:05 PM   #6
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 724 Times in 534 Posts
Default

Quote:
Originally Posted by BillS111 View Post
Thank you so much! I will check out those threads.

According to this, if i want 420 ppm, i will need about 550 CFM. Does that sound about right?

ps - yes, i have a Co2 meter
My CO2 controller is built and working, but the HRV is still parts at this point.

I looked at your paper, and to be honest, the cfm doesn't mean too much to me at this point, since I am counting on my HRV controller to supply air at what ever rate rate is required give me my target CO2 range.

I have noticed that if your winter air is fairly still, CO2 'bubbles' will form where you may be sitting, or working.

Gas cooking is a CO2 crime scene, and I have gone to induction cooking when possible (almost always).

My gas dryer is also bad as is my gas water heater, and they're all hooked up OK.

Last time I looked closely at ASHRE CO2 acceptable levels, I thought they were way too high. So I'm not sure if you paper will get you what you want or not.

I also found some great research from Germany, citing better school performance when CO2 levels were below 800 ppm. Makes sense to me.

Here is a link to an Irish Passive House HRV, that was my inspitation for building my CO2 controller, and I plan to closely model my HRV on their product, which they will not sell into the US.

[QUOTE]
The system will always run itself to maintain the highest level of efficiency while ensuring CO2 and humidity levels are regulated using sensors for each. When CO2 reaches 650ppm or humidity reaches 45%, the unit automatically slows down to trickle speed until levels become higher again.
[/QIOTE]

By the way, how is your indoor plant situation? (no joke)


Best,

-AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...

Last edited by AC_Hacker; 08-12-14 at 08:31 PM..
AC_Hacker is offline   Reply With Quote
The Following User Says Thank You to AC_Hacker For This Useful Post:
BillS111 (08-12-14)
Old 08-12-14, 08:24 PM   #7
BillS111
Lurking Renovator
 
Join Date: Aug 2014
Location: Boston
Posts: 7
Thanks: 6
Thanked 0 Times in 0 Posts
Default

Thanks, but i looked into plants, and they dont really lower Co2 any meaningful amount. See page 2 here: sweets.construction dot com/swts_content_files/152845/713268.pdf

I agree that the ASHRAE levels are way too high. I was more using that paper to figure out what CFM i need in an HRV/ERV unit, for a given Co2 ppm target.

Just curious - why wont they sell that HRV into the US? (not that i could use it anyway as it is an 'in-wall' unit)

Thanks

Last edited by BillS111; 08-12-14 at 08:30 PM..
BillS111 is offline   Reply With Quote
Old 08-12-14, 08:36 PM   #8
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 724 Times in 534 Posts
Default

Quote:
Originally Posted by BillS111 View Post
Just curious - why wont they sell that HRV into the US? (not that i could use it anyway as it is an 'in-wall' unit)
They claim that the 120v/60 Hz is not compatible with their controller. Hard for me to imagine, I mean China can do it, maybe they can, too.

You should contact them, maybe they changed their mind(s).

-AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
The Following User Says Thank You to AC_Hacker For This Useful Post:
BillS111 (08-12-14)
Old 08-12-14, 08:41 PM   #9
BillS111
Lurking Renovator
 
Join Date: Aug 2014
Location: Boston
Posts: 7
Thanks: 6
Thanked 0 Times in 0 Posts
Default

Quote:
Originally Posted by AC_Hacker View Post
They claim that the 120v/60 Hz is not compatible with their controller. Hard for me to imagine, I mean China can do it, maybe they can, too.

You should contact them, maybe they changed their mind(s).
-AC
Thanks, i will contact them. But that is a thru-wall unit, no? My Landlord wont allow me to make those types of changes.

Interesting on the controller, i would think an adapter would work.
BillS111 is offline   Reply With Quote
Old 08-12-14, 08:58 PM   #10
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 724 Times in 534 Posts
Default

Quote:
Originally Posted by BillS111 View Post
Thanks, i will contact them. But that is a thru-wall unit, no? My Landlord wont allow me to make those types of changes.
You were talking about even setting the thing on the floor & making some kind of window-adapter... their HRV will run in any position, but there is an condensation issue with any HRV and theirs relies on gravity, so it does need to be upright.

BTW, there are other window mounted units, but they don't have anything close to the same efficiency.

Study the drawing really closely, you're not so far away from your goal.

-AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
The Following User Says Thank You to AC_Hacker For This Useful Post:
BillS111 (08-12-14)
Reply


Tags
carbon dioxide, co2, erv, hrv

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 07:25 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design