02-12-13, 11:38 AM | #11 |
Uber EcoRenovator
Join Date: Apr 2011
Location: Strathroy Ontario Canada
Posts: 657
Thanks: 9
Thanked 191 Times in 129 Posts
|
AC_Hacker I will approach this with some caution. The ground loop now is a mixture of propylene glycol and water protecting from freezing down to -15 Deg C. But if my loop approaches 2 Deg C I'm going to stop the system I don't what to freeze the ground around the loop tubes. I've heard some stories about making permafrost. And airconditioning in the summmer is not the cure.
Randen |
02-12-13, 07:35 PM | #12 |
Master EcoRenovator
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
|
Randon, I would not be too concerned about the 2C mark. Since the glycol is good to -15C, you will not harm the system going down farther than 2C. Also, you will have a VFD so you can run it at 80% if you like just to keep it closer to the original design. Keep the pumps running regardless.
|
02-13-13, 05:48 AM | #13 |
Master EcoRenovator
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
|
Randon, how did you filter the propane? I was thinking that there might be non condensables that are keeping your performance down.
|
02-13-13, 07:46 AM | #14 |
Apprentice EcoRenovator
Join Date: Dec 2010
Location: Western Australia
Posts: 148
Thanks: 1
Thanked 48 Times in 34 Posts
|
|
02-13-13, 08:33 AM | #15 |
Master EcoRenovator
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
|
Yes, but you can get water with your liquid propane and there is varying amounts depending on supplier. Am I missing something here?
|
02-13-13, 05:33 PM | #16 |
Uber EcoRenovator
Join Date: Apr 2011
Location: Strathroy Ontario Canada
Posts: 657
Thanks: 9
Thanked 191 Times in 129 Posts
|
Well we have another GSHP running. The Varible Frequency Drive (VFD) is sooo smooth with the way the motor ramps on start-up. Of coarse you can control the presure with the speed. The scroll compressor is soo quiet. It is just running on the bench with no heat exchanging fluids so temps and pressures went crazy after 1 min.
I had programmed in a ramp to 3450 RPM in 5 sec and a ramp down to 0 RPM in 10 sec. If the motor becomes overloaded it will shut down. As the motor is starting you can watch the LED read-out with the current voltage RPM as they change. You can set a fault to wait on re-start. There are so many great capibilities with the VFD. It has low voltage input for the thermostat control. I may have to wait till the weekend to install the GSHP with the loop connections. Randen |
02-13-13, 06:13 PM | #17 | |
Apprentice EcoRenovator
Join Date: Dec 2010
Location: Western Australia
Posts: 148
Thanks: 1
Thanked 48 Times in 34 Posts
|
Quote:
Having said that, pulling liquid and then feeding it through a couple of filter/driers would take care of that. The molecular sieves used in those will grab the water pronto. |
|
02-13-13, 06:18 PM | #18 | |
Master EcoRenovator
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
|
Quote:
|
|
02-13-13, 06:34 PM | #19 | |
Master EcoRenovator
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
|
Quote:
|
|
02-14-13, 08:49 AM | #20 | |
Supreme EcoRenovator
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 724 Times in 534 Posts
|
Quote:
Is there some kind of computer control interface to the VFD? -AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker... |
|
Thread Tools | |
Display Modes | |
|
|