I assure you that ever post you have made gave me a AHA! moment. And I then scratch my head for several hours/days to figure out what I didn't understand. So again I say thank you.
Yes I know a larger compressor will change everything. But I do not believe this system is capable of doing what I really need it to with the 7,500btu. I have my eyes on a 9,900btu 3/4hp 115V 60Hertz 51LRA beauty. Most my real tuning should probably wait til then. I was just getting a good fill of things and a decent charge because temps have been colder lately. Low of 23F tonight. I fill that one day I will be digging around the water tank in order to insulate it because heating the water is much easier and more important than air temp. I know that the evap can handle the larger compressor. And I can always add another coil in both the water or air condenser if needed. I have come this far I don't know why I would settle for less. Since this system is heating only, meaning no running at all during the summer, is finding the critical charge that important? I am guessing it will run almost 3/4 to all night tonight to keep up. I guess I don't understand why the critical point is needed other than for safety. I have a 345psi shut off ready to braze on when I get the larger compressor. I do understand that I should tune everything to the air side though. Because the water loop will always run less head pressure. Thanks again man
__________________
שְׁמַע יִשְׂרָאֵל ה' אֱלֹהֵינוּ ה' אֶחָד |
01-02-16, 09:32 PM | #152 |
Supreme EcoRenovator
|
Some generalized info:
Safety and quality run together. A high-quality job is safe by nature. A safety interlock is nice, but a design that doesn't need one is better. Your 7500 btu compressor could quite possibly put out 9900 btu into a better condenser. A 9900 btu compressor might not move 9900 btu through your existing condenser. It will definitely gobble up more power. A 9900 btu compressor might move 12000 btu into a much better condenser. Whatever happens, the darn thing already works way better than a 1500 watt aquarium heater. |
01-03-16, 09:22 AM | #153 |
Journeyman EcoRenovator
Join Date: Apr 2015
Location: Oxford, MS USA
Posts: 496
Thanks: 69
Thanked 87 Times in 61 Posts
|
Yeah that is what I was thinking, until I max out my evap, the condenser is the only thing limiting compressor size. Not that I want something too big and it cycle on and off a bunch but with 400 gallons of water I don't see that happening.
__________________
שְׁמַע יִשְׂרָאֵל ה' אֱלֹהֵינוּ ה' אֶחָד |
01-03-16, 12:09 PM | #154 |
Journeyman EcoRenovator
Join Date: Apr 2015
Location: Oxford, MS USA
Posts: 496
Thanks: 69
Thanked 87 Times in 61 Posts
|
The test data from 4" from the bottom of the pond is in! Note we have had 3 nights in a row of less than 30F nights.
PHP Code:
__________________
שְׁמַע יִשְׂרָאֵל ה' אֱלֹהֵינוּ ה' אֶחָד |
01-15-16, 07:58 PM | #155 |
Journeyman EcoRenovator
Join Date: Apr 2015
Location: Oxford, MS USA
Posts: 496
Thanks: 69
Thanked 87 Times in 61 Posts
|
So I got the 53 LRA R22 10,000 BTU compress on.
Went ahead a made a larger condenser for the fish tank. I added another 20 feet of 1/4" painted black nontoxic copper tubing. And I filled it with straight R290 Here are the numbers, first is the temp of the incoming and outgoing lines in the fish tank. Next is the pressures and the suction temp (low number) and the line temp right before the txv. So as you can see pretty low superheat and higher subcooling. Which means I'm slightly over charged, but I'm only pulling 775 watts. I only used .6 kwh last night compared 2.5-3.5 kwh with the same temps. My pond temp is about 45F. Here is the data from the pond, some days got down to 15F. PHP Code:
__________________
שְׁמַע יִשְׂרָאֵל ה' אֱלֹהֵינוּ ה' אֶחָד |
01-15-16, 09:51 PM | #156 |
Supreme EcoRenovator
|
Sweet! Those numbers look and sound a lot better. The extra pipe in the water made a world of difference.
|
01-15-16, 11:41 PM | #157 |
Journeyman EcoRenovator
Join Date: Jan 2011
Location: Seattle
Posts: 326
Thanks: 109
Thanked 23 Times in 18 Posts
|
I always remember that the warmth is near the surface and the farther down you get it gets cooler. At least from my days of swimming in the lakes as a kid.
Can you run a temp probe into the lake and check the different depths? |
01-16-16, 12:48 PM | #158 |
Journeyman EcoRenovator
Join Date: Apr 2015
Location: Oxford, MS USA
Posts: 496
Thanks: 69
Thanked 87 Times in 61 Posts
|
Jeff, yes it sure did help.
Geo NR Gee, Yes that is what I thought too, but the uppermost layer is going to be affected by the cold more I believe, seeing as it freezes first. I have data loggers in a couple different places right now. I will need cold water in the summer, so seeing as I have more cooling days than heating days, I might be best staying close to the bottom. I found this link, Heat in Lakes
__________________
שְׁמַע יִשְׂרָאֵל ה' אֱלֹהֵינוּ ה' אֶחָד |
01-16-16, 09:25 PM | #159 |
Journeyman EcoRenovator
Join Date: Apr 2015
Location: Oxford, MS USA
Posts: 496
Thanks: 69
Thanked 87 Times in 61 Posts
|
Another link http://fishandboat.com/anglerboater/...y02finding.pdf
that says that the water right under the ice is normally 39.2F. That to me is great news, my water temp should never be lower than that. This pond is 17 feet deep. I have never seen more than 2 inches of ice on it and that only lasted for a few days. There is a lot of heat in 39.3F water.
__________________
שְׁמַע יִשְׂרָאֵל ה' אֱלֹהֵינוּ ה' אֶחָד |
|
|