I also noticed that you haven't installed an outlet duct in the bathroom, I guess it's for the constructing difficulties but extracting the stale air from there will definitely help further more.
At this point in time the bathroom and toilet (kitchen inlet is blocked) are connected to the old whole house exhaust fan in the attic. That one will be decommisioned.
I'll connect the HRV to the existing ductwork so that toilet- and bathroom air will pass through the HRV. For this I made it so that when it's colder outside more air will be extracted in total than is inserted into the livingroom. (When it is not colder then several windows will be open, enough ventilation)

Our livingspace is the warm area, upstairs can be colder. The warm area is well sealed, floor insulation is so-so, which will be my next project. The goal for the warm living area is balanced ventilation with HRV. Upstairs will have some negative pressure, colder fresh air will trickle in, especially via the attic which is actually a useable room (In the Netherlands an attic is livingspace or a storageroom, we insulate the roof instead of covering the floor with a foot of cellulose)

So the HRV will take over from the whole house extraction fan. That single fan (anno 1984) uses more electricity than the 2 in the HRV together, 20,- gain per year on that.

So far I didn't mention the bathroom, it's upstairs and the sketch a few posts above only covers the groundfloor. I did include it in my plans though, it is a place that needs ventilation after all, need to remove the moist from taking a shower, and can recover heat from that.

Fornax is offline   Reply With Quote
Old 01-14-13, 02:41 AM   #332
kostas
Helper EcoRenovator
 
Join Date: Dec 2012
Location: Venice, Italy
Posts: 89
Thanks: 15
Thanked 41 Times in 19 Posts
Default

Here's what I'm planning to do for the ducting.
I live in a two-floor house (total area 90 sqm), ground floor is another property, on the first floor I have the entrance, an open space with the kitchen and a slightly separate living room, a bathroom and the stairs that lead to the attic. There I have a small corridor, another bathroom, a studio and two bedrooms.
Behind all this there is a small place (25 sqm) used as a closet. I will install the HRV there as I can easily reach every room using short distance ducts (max is 5 mt long). I will plug the main inlet and outlet to the outside via the roof right above the machine (the drawing is quite schematic, in and out ducts will be much more distant from each other).
On the first floor I will have fresh air in at the living room while taken the stale air from the kitchen area and the bathroom.
On the attic I'll plug the fresh air in the bedrooms and take it back from the bathroom and the stairs arrival (in that way I'll get some of the kitchen odors that inevitably go upstairs + max hot inside air).
I think it's quite balanced like that. The only problem is that I'll have to make three 120mm diameter holes to the attic towards the first floor, that's 45 cm thick!
Attached Thumbnails
Click image for larger version

Name:	impiantopp.jpg
Views:	1157
Size:	87.2 KB
ID:	2847   Click image for larger version

Name:	impiantops2copia.jpg
Views:	1188
Size:	101.6 KB
ID:	2848   Click image for larger version

Name:	xrayxq.jpg
Views:	5195
Size:	213.1 KB
ID:	2849  
kostas is offline   Reply With Quote
Old 01-14-13, 09:55 AM   #333
Piwoslaw
Super Moderator
 
Piwoslaw's Avatar
 
Join Date: May 2009
Location: Warsaw, Poland
Posts: 961
Thanks: 188
Thanked 110 Times in 86 Posts
Default

Quote:
Originally Posted by kostas View Post
Notice two pairs of ducts: (bathroom & livingroom) and (bedroom1 & kitchen). In both pairs one intake and one exhaust duct run next to each other for 2-4 meters. Can you turn each pair of ducts into a long countercurrent heat exchanger? Use rectangular ducts instead of round ones and have them touching along the larger sides, then wrap the pair in insulation.
Putting smaller HXs ahead of the main recuperator will increase the efficiency of the whole setup, like having a larger recup.

Quote:
Originally Posted by kostas View Post
and the stairs arrival (in that way I'll get some of the kitchen odors that inevitably go upstairs + max hot inside air)
Great placement!
__________________
Ecorenovation - the bottomless piggy bank that tries to tame the energy hog.
Piwoslaw is offline   Reply With Quote
Old 01-14-13, 11:18 AM   #334
kostas
Helper EcoRenovator
 
Join Date: Dec 2012
Location: Venice, Italy
Posts: 89
Thanks: 15
Thanked 41 Times in 19 Posts
Default

Quote:
Originally Posted by Piwoslaw View Post
Notice two pairs of ducts: (bathroom & livingroom) and (bedroom1 & kitchen). In both pairs one intake and one exhaust duct run next to each other for 2-4 meters. Can you turn each pair of ducts into a long countercurrent heat exchanger? Use rectangular ducts instead of round ones and have them touching along the larger sides, then wrap the pair in insulation.
Putting smaller HXs ahead of the main recuperator will increase the efficiency of the whole setup, like having a larger recup.


Great placement!
Yes, that could be a good idea but I have some concerns:
First some dew may occur to the exhausting duct, so I'll have to put another condensation pipe.
Second the heat exchanged by those ducts will only affect the destination rooms and not the whole system.
Sincerely I have serious doubts about the effectiveness of this solution.
But I am speaking as a non-expert, so maybe I'm wrong.

Speaking about the aforementioned ductwork I was thinking of another improvement:
In the first floor I have the internal AC unit (Daikin dual split 18000Btu Inverter) placed between the stairs and the bathroom (AC1 in the drawing).
In the summertime I could deviate the fresh air supply right above the unit so that the incoming air gets immediately chilled and distributed with major speed by the fans.

While above the kitchen I could add some more recessed intake points in order to catch all that precious heat generated by cooking in winter time ...



What do you guys think about it?
Attached Thumbnails
Click image for larger version

Name:	PP01 DUCTWORK.jpg
Views:	4861
Size:	67.1 KB
ID:	2851  

Last edited by kostas; 01-17-13 at 03:30 AM.. Reason: image placement
kostas is offline   Reply With Quote
Old 01-15-13, 04:42 AM   #335
kostas
Helper EcoRenovator
 
Join Date: Dec 2012
Location: Venice, Italy
Posts: 89
Thanks: 15
Thanked 41 Times in 19 Posts
Default

Having a second thought of it, conveying the FAI duct to the AC in the summer seems to be quite mandatory...

Quote:
This means that in the Summer, the very humid air can be tempered, but will increase the indoor RH and cause an increase in load on your air-conditioner.
Excess Air: New England: HRV or ERV?

BTW, the guy's blog has an interesting and useful duct construction guide here:

Excess Air: Rules of Duct Design, Why?
kostas is offline   Reply With Quote
Old 01-15-13, 09:20 AM   #336
Piwoslaw
Super Moderator
 
Piwoslaw's Avatar
 
Join Date: May 2009
Location: Warsaw, Poland
Posts: 961
Thanks: 188
Thanked 110 Times in 86 Posts
Default

Quote:
Originally Posted by kostas View Post
Yes, that could be a good idea but I have some concerns:
First some dew may occur to the exhausting duct, so I'll have to put another condensation pipe.
There shouldn't be much condensation since the temperature difference across the HX will be no more than a few degrees. In some cases there might be some, but it will be in the duct already going to the main recuperator unit, so slightly tilting the duct down towards the recup should let it drain into the main unit, which will already be handling condensate.
Quote:
Originally Posted by kostas View Post
Second the heat exchanged by those ducts will only affect the destination rooms and not the whole system.
I did a few quick and dirty calculations (assuming outdoor temp 0°C, room temp 20°C and all HXs 80% efficient) and the effects are:
  1. The fresh air which goes though those extra heat exchangers is warmer when it arrives at its destination room (18-19°C instead of 16°C).
  2. The fresh air which does not go through a second HX is slightly cooler than if the whole system had only the main recup unit (14-15°C instead of 16°C).
  3. The stale air exhaust is slightly cooler (3.5-3.7°C instead of 4°), which means that the efficiency of the whole system is higher (~82% vs 80%).
So, there are gains to be had, though during most of the year probably not worth the extra work. I could do a more detailed calculation with better input data.
__________________
Ecorenovation - the bottomless piggy bank that tries to tame the energy hog.
Piwoslaw is offline   Reply With Quote
Old 01-15-13, 10:13 AM   #337
kostas
Helper EcoRenovator
 
Join Date: Dec 2012
Location: Venice, Italy
Posts: 89
Thanks: 15
Thanked 41 Times in 19 Posts
Default

Yes, you could be right about it.
But my guess is that you'll need something more that just two adjacent ducts to exchange some serious amount of heat.
Theoretically speaking you could put a number of some CPU heat coolers on both channels (side to side) to enable heat transfer. Something like this without the peltier chip:

But then, you could always built a more efficient HX by adding some more PP sheets!..
kostas is offline   Reply With Quote
Old 01-15-13, 12:17 PM   #338
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by Piwoslaw View Post
... I could do a more detailed calculation with better input data...
Please do more calculations, with more details and please post the entire calculation process here in the forum.

I would like to see how you are going about it.

-AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
Old 01-15-13, 04:19 PM   #339
Piwoslaw
Super Moderator
 
Piwoslaw's Avatar
 
Join Date: May 2009
Location: Warsaw, Poland
Posts: 961
Thanks: 188
Thanked 110 Times in 86 Posts
Default

Quote:
Originally Posted by AC_Hacker View Post
Please do more calculations, with more details and please post the entire calculation process here in the forum.

I would like to see how you are going about it.
How about this: I'll share my rough calculations with comments and tell what and where can be modified. Then anyone can plug in their own parameters to get a better approximation of their own system.

Since there are many different temperatures to keep track of, I'll use a drawing to explain which is where:

So there are two heat exchangers: All of the air goes through HX1, but only part goes through HX2.
Fin: Fresh air in,
Out1: Fresh air leaving HX1,
RF1: Fresh air entering Room1, temperature equal to Out1,
In2: Fresh air entering HX2 temperature equal to Out1,
RF2: Fresh air exiting HX2 into Room2,
RS2: Stale air entering HX2 from Room2,
Out2: Stale air exiting HX2,
RS1: Stale air from Room1,
In1: Stale air entering HX1, temperature is a weighted average of Out2 and RS1
Sout: Stale air exiting HX1 to outdoors.

My assumptions:
  • Fin=0°C,
  • RS1=RS2=20°C,
  • both heat exchangers are 80% efficient,
  • exactly half of the fresh air goes to Room1 and the other half goes through HX2.
In order to get a first estimate of Out1 I assumed for a moment that In1=20°C. Since HX1 recovers 80% of the heat, and In1-Fin=20°C, then Out1=Fin+0.8*20°C=16°C, while Sout=In1+Out1-Fin=4°C.
So, since Out1=16°C, then this is the temp of the fresh air going to Room1 (RF1) and going into HX2 (In2).
HX2 recovers 80% of the heat, and the temp difference of its two inputs RS2 and In2 is 20-16=4°C, then RF2=In2+0.8*4°C=19.2°C, and Out2=16.8°C.
In1 is the average of Out2 and RS1, since equal amounts of HX1's air go through HX2 and go to Room1. So In1=(16.8+20)/2=18.4°C.

OK, now we are back at the first step (where we temporarily assumed that In1=20°C). Now we do everything over again starting with In1=18.4°C. This will change most of the numbers and after a few steps we get yet another value for In1. With each iteration the changes become smaller, so 3-4 steps are enough.

I did this again assuming that the Room1 and HX2 split HX1's air not equally, but 1:2 (ie HX2 gets twice as much air as Room1). The only real variation is that In1=(RS1+2*Out2)/3 instead of a regular average.

As I mentioned earlier, these calculations were meant to be quick and dirty. There may be a better way to do it, but I am not John von Neumann to sum up infinite series Just an estimation was enough in this case.

Anyone who wants to do this in more detail should plug in his own numbers: each HX may have a different efficiency, each room may have a different temperature, etc. Moisture in the air will also skew the results. Have fun!
Attached Thumbnails
Click image for larger version

Name:	2HX.jpg
Views:	4984
Size:	16.4 KB
ID:	2855  
__________________
Ecorenovation - the bottomless piggy bank that tries to tame the energy hog.
Piwoslaw is offline   Reply With Quote
The Following 2 Users Say Thank You to Piwoslaw For This Useful Post:
AC_Hacker (01-16-13), kostas (01-17-13)
Old 01-19-13, 05:10 PM   #340
ham789
Helper EcoRenovator
 
Join Date: Dec 2011
Location: tigard, oregon
Posts: 42
Thanks: 0
Thanked 4 Times in 4 Posts
Default heat sinks

I tried the computer heat sink method.
Problem is that the thing is designed to get rid of about
100W with a temperature differential > 60C.
The heat pipe temperature differential was relatively small,
but, at low temperature differentials, it boils down to coupling
to the air with tiny delta-T. I didn't save the test data
because it wasn't even close to feasible in my context.

I don't think there's anything wrong with the concept
if you can make it BIG enough.

In order to get more than 50% efficiency, you need
a temperature gradient over the transfer path.
That's gonna require multiple heatsinks and heatpipes
in series.

I tried to solve that problem with a bunch of butane cylinders
poked thru two adjacent ducts. Same problem. Heat pipes
work fine, just need a way to get the heat out of 'em
into the air.
I had some emotional issues with my HRV being a bomb.
Would work great for water to water heat transfer.

I thought about spot welding some fins, but decided a live
butane tank wasn't the best choice for welding.

Attached Thumbnails
Click image for larger version

Name:	hrv2c.jpg
Views:	1241
Size:	21.5 KB
ID:	2870   Click image for larger version

Name:	butane.jpg
Views:	1246
Size:	21.2 KB
ID:	2871  
ham789 is offline   Reply With Quote
Reply


Tags
erv, heat recovery, hrv


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 12:50 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design