Old 03-01-12, 02:38 AM   #1151
BradC
Apprentice EcoRenovator
 
Join Date: Dec 2010
Location: Western Australia
Posts: 148
Thanks: 1
Thanked 48 Times in 34 Posts
Default

Quote:
Originally Posted by Vlad View Post
If we cool bottle down to -5-10 Degree Celsius and start pulling propane as a vapor (bottle valve up) with recovery unit then propane will start evaporating (and it will help to keep bottle cold) but butane will stay as a liquid. Also this will keep water in original bottle as well.

We will get some non condensables but it is easy to get rid of them by purging and charging as a liquid.
Your theory is sound, but you will want to start quite a bit lower than -10C as you are likely to have some iso-butane in there also.

Hydrocarbon gasses that you want to keep are very much more dense than any non-condensible you are likely to find in the bottle. Leaving the bottle overnight and then very slowly cracking the valve to purge out the top part of the bottle will likely rid you of 99.9% of them before you even start decanting. The trick is to make sure you don't disturb the bottle so the layers can stratify.

You will need to limit the rate you pull the propane from the bottle, but certainly the theory is sound. What you are doing is effectively fractional distillation. The R290 for heatpumps thread has quite a bit of information on water and propane. It's not quite as easy to separate as you might think, particularly if you live in a country like mine where negative temperatures only happen in deep freeze units.

BradC is offline   Reply With Quote
The Following User Says Thank You to BradC For This Useful Post:
buffalobillpatrick (05-18-14)
Old 03-01-12, 03:04 AM   #1152
Vlad
Apprentice EcoRenovator
 
Join Date: Aug 2010
Location: Windsor ON Canada
Posts: 229
Thanks: 4
Thanked 30 Times in 22 Posts
Default

Quote:
Originally Posted by BradC View Post
You will need to limit the rate you pull the propane from the bottle, but certainly the theory is sound. What you are doing is effectively fractional distillation. The R290 for heatpumps thread has quite a bit of information on water and propane. It's not quite as easy to separate as you might think, particularly if you live in a country like mine where negative temperatures only happen in deep freeze units.
I have just checked boiling point for Isobutane it is -11.7 Celsius. You can easily find -15-18 in your chest freezer (you will need to move some kenguru out of there ). Also at this temperature propane will be very "lazy" to evaporate. After you start pulling propane it will keep itself cold so you can put kenguru back into freezer .

It is almost impossible to get pure R290 at home, but we will get close enough.
Vlad is offline   Reply With Quote
The Following User Says Thank You to Vlad For This Useful Post:
buffalobillpatrick (05-18-14)
Old 03-01-12, 04:37 AM   #1153
BradC
Apprentice EcoRenovator
 
Join Date: Dec 2010
Location: Western Australia
Posts: 148
Thanks: 1
Thanked 48 Times in 34 Posts
Default

Quote:
Originally Posted by Vlad View Post
After you start pulling propane it will keep itself cold so you can put kenguru back into freezer
I decanted 8KG of Propane by drawing vapor from a bottle. It was a 30C day, but the time I'd finished the source bottle had a very nice thick fur of frost. Wish I'd taken a photo.

We don't keep 'roo in the freezer. It gets quite gamey the longer you keep it, so shoot it and eat it fresh.
BradC is offline   Reply With Quote
The Following User Says Thank You to BradC For This Useful Post:
buffalobillpatrick (05-18-14)
Old 03-01-12, 06:20 AM   #1154
Pegasus
Lurking Renovator
 
Join Date: Feb 2012
Location: Greece
Posts: 13
Thanks: 3
Thanked 3 Times in 2 Posts
Default Firts step

I finally got hold of the compressor for the heat pump project :

Compressor (Model - Type) : YZG-39RCT1 - Rotary
Power rating (W) : 1300
Cooling capacity (W - BTU/h) : 3900 - 13310
Displacement (Cm3/rev) : 23.4
EER (w/w) : 3.10
Refrigerant (Type - Kg) : R22 - 1.03

It has two cap tubes in parallel and a 220v operated reversing (4 Way) valve

(Sorry but cannot post photos till my sixth post! Available though to my photo album)

@ Vlad,
Since I'm going to use it both for heating and cooling, I would need to install 2 TXV' s, if it is to replace the cap tubes, correct? (This would increase the cost and complexity of it)

My HVAC friend also insists on a LP + HP differential safety switch which I am going to install, having in mint the water HX pressure limit to prevent any rupture.

My intention was also, to test the heat pump with R22 and then replace it with propane, but you said that finally you will go directly to propane, why is that?

@AC_Hacker
I don't want to spoil your "inner warmth" but here it is still cold - raining - snowing - blowing etc, one of the worst winters (in many aspects) for Greece, we hope for a better spring and summer.

I have in mind two possible configurations about the expansion / fill tank + circ. pump set-up for the ground loop (mine consists of 6 circuits in parallel of about 75m each) :

- Open tank (barrel) with submersible pump (ease of construction but hight consumption)
- Sealed Exp. tank with a 50w / 5m head central heating pump (More difficult to construct but with low consumption)

What would you suggest ?
Pegasus is offline   Reply With Quote
Old 03-01-12, 07:07 AM   #1155
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default

Quote:
Originally Posted by Ko_deZ View Post
Regarding SSR and electro-mechanical. The SSR does have a voltage drop across it. Ususally SSRs have something like 1.5V drop. Pulling 1A will give you 1*1.5=1.5W heat loss. Not a whole lot, but with more current you will get more wattage lost, and potentially a need for cooling. .


I've been using SSRs on my Sanyo ASHPs and they don't seem to heat up
their heat sinks much at all. Slightly warm to the touch maybe..

SSR:


Maybe it's just too cool in my basement for the heat sink to store much heat.?.
The back side of the sink has some short cooling fins.
Even in summer, I don't think a fan will ever be needed in this application.

When it's really cold, the typical current increases to 4 or 5 amps.
But, the heat sink never really gets much warmer than it is this morning..


Sanyo #2 uses a single SSR mounted to it's sheet metal chassis.
http://i46.photobucket.com/albums/f1...CL/afterBH.jpg
Heat Scan during the late summer showed no noticeable heat increase.
I guess the chassis is too large and has too much air flow to warm up.


EMR: (Before hack)
http://i46.photobucket.com/albums/f1...L/BeforeBH.jpg

We do get current surges up to 10 amps. Anything above 10A triggers
the sensor and shuts down the system for about 60 seconds.


Anyone thinking of using R290 should consider using SSRs, instead of relays.
Unless the relays are considered safe to use in a propane-air environment.


I'm not an expert, but it just seems like common sense to avoid sparks with some gases.
__________________
My hobby is installing & trying to repair mini-splits
EPA 608 Type 1 Technician Certification ~ 5 lbs or less..

Last edited by Xringer; 03-01-12 at 07:16 AM.. Reason: R290
Xringer is offline   Reply With Quote
Old 03-02-12, 02:08 AM   #1156
Vlad
Apprentice EcoRenovator
 
Join Date: Aug 2010
Location: Windsor ON Canada
Posts: 229
Thanks: 4
Thanked 30 Times in 22 Posts
Default

Quote:
Originally Posted by Pegasus View Post
I finally got hold of the compressor for the heat

It has two cap tubes in parallel and a 220v operated reversing (4 Way) valve
Are you sure about 220v reversing valve?
Quote:
Originally Posted by Pegasus View Post
@ Vlad,
Since I'm going to use it both for heating and cooling, I would need to install 2 TXV' s, if it is to replace the cap tubes, correct? (This would increase the cost and complexity of it)
Yes you need 2 txvs and if they are non HP you need 2 check valves. Start with caps and later you can change it if you want.
Quote:
Originally Posted by Pegasus View Post
My HVAC friend also insists on a LP + HP differential safety switch which I am going to install, having in mint the water HX pressure limit to prevent any rupture.
Usually you can find differential pressure switches on walk-in cooler/freezers. You don't need thermostat in this case. Thermostat in this type of environment is always a pain especially when condensing unit is located 100 feet away. They are not cheap.

" LP + HP differential safety switch" sounds new. Can you provide more details?
Quote:
Originally Posted by Pegasus View Post
My intention was also, to test the heat pump with R22 and then replace it with propane, but you said that finally you will go directly to propane, why is that?
Just to keep my motivation up .

Last edited by Vlad; 03-02-12 at 02:13 AM..
Vlad is offline   Reply With Quote
Old 03-07-12, 04:01 PM   #1157
Pegasus
Lurking Renovator
 
Join Date: Feb 2012
Location: Greece
Posts: 13
Thanks: 3
Thanked 3 Times in 2 Posts
Default

Quote:
Originally Posted by Vlad View Post
Are you sure about 220v reversing valve?
Yes checked it twice. It seems to be the standard for the low range split type A/C here. Very easy to integrate it to my existing controls.


Quote:
Originally Posted by Vlad View Post
" LP + HP differential safety switch" sounds new. Can you provide more details?
I meant something like what BradC is suggesting for both the High and Low Side. Sorry for my incomplete HVAC jargon!
Pegasus is offline   Reply With Quote
Old 03-07-12, 04:39 PM   #1158
randen
Uber EcoRenovator
 
Join Date: Apr 2011
Location: Strathroy Ontario Canada
Posts: 657
Thanks: 9
Thanked 191 Times in 129 Posts
Default 2 Ton Shop GSHP Replaced with 3.5 Ton

The homemade shop 2T GSHP was swaped out for the larger 3.5T. As some may remember I had built a small 2T GSHP that didn't produce enough heat for my liking in the shop but I had another 3.5 ton compressor, nearly new and constructed but another one around that. Now its a little premature but I'm thinking its not much better GRR!!. Drawing more current but dosen't seem to be liberating much heat. The ground loop is 6 Deg C and its sucking back 9.5 Amps @ 214V. The 2 T would maintain an average temp 17 Deg. C in the shop drawing 6 Amp. outside -8 Deg C. A little tuning maybe. And we will have to wait for a bit of a cold snap. A 4 hr test run raised the shop from 13 to 17 degree C. with an outside temp of 4 Deg. C.

Randen
randen is offline   Reply With Quote
Old 03-07-12, 05:37 PM   #1159
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default

Quote:
Originally Posted by Pegasus View Post
Originally Posted by Vlad View Post Are you sure about 220v reversing valve?

Yes checked it twice. It seems to be the standard for the low range split type A/C here. Very easy to integrate it to my existing controls.
I know my 220vac Sanyo 24KHS72 units use 220vac reversing valves,
and that seems logical for units that are also sold in countries where
only 220vac is available.

In the USA, it's common for a 240vac laundry drier to use half the circuit
to power it's 120vac motor, while the heating elements use 240v.

I don't think that type of setup would work in some 220v countries,
where the ground is just that, a ground and not the 'N' side for two 120v lines.

Please correct me, if I'm wrong about this.
I've never used 220 appliances while overseas.
__________________
My hobby is installing & trying to repair mini-splits
EPA 608 Type 1 Technician Certification ~ 5 lbs or less..
Xringer is offline   Reply With Quote
Old 03-07-12, 08:09 PM   #1160
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by randen View Post
...but I'm thinking its not much better GRR!!. Drawing more current but dosen't seem to be liberating much heat...
You are demanding almost 2x the heat from your system...
Perhaps it's your heat exchanger?
Did you scale up your heat exchanger by 2x?
Did you increase your loop flow rate by 2x?

...just saying...

-AC_Hacker

__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
Reply


Tags
air conditioner, diy, gshp, heat pump, homemade


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On