Commercial codes are more stringent, and it's easy to see why with ventilation standards. Commercial settings will see many more people in a given area, and the rate may be increased to reduce the incidence of airborne infections spreading.

I believe most of the US residential code now falls under IRC (International Residential Code) and the most recent version requires 0.35ACH or 15CFM per occupant. It also requires 100CFM intermittent or 25CFM continuous from kitchens and 50CFM intermittent/20CFM continuous from bathrooms.

ASHRAE 62.2 is residential ventilation industry standard, and I believe the latest version stipulates 7.5CFM/occupant + 1CFM/100sqft (Environmental Energy Technologies Division News)

mrd is offline   Reply With Quote
Old 06-28-10, 06:05 PM   #52
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default 1 Cubic Foot Polypropylene DIY HRV Core...

(NOTE: My original post said 'polyethylene', my error. I should have said 'polypropylene' and have corrected this post.)

Today, I picked up my black plastic sign-board material.


I explained to them that I was going to stack the 12" square pieces and that I wanted to end up with with a 1 foot cubed stack. Since the material is 4mm thick, it turned out that I required about 72 pieces, which worked out to about two and a third 4' x 8' pieces to make one heat exchanger.

I was a bit off on the prices in my previous post, but the Corex charge for black was $15.25 per 4 x 8 sheet, and the cutting charge was $15, so the overall cost to me was $45.50. They had a bit of scrap laying about, so they didn't charge for it.

Since I'm trying to build a $700 Energy Recovery Ventilator for far less, $45.50 cost for the core seems reasonable, but I do think it could be done for less.

When I was stacking the 12" square sheets (alternating the orientation of each layer) , I noticed that most of the sheets had a slight 'cup' to each sheet, so I pit them all 'cup-side' down. My resulting pile had less 'spring' than my original, randomly oriented pile, so that should mean that the sheets are in closer contact.


I have done some searching for polypropylene cement, and it doesn't seem to exist. So, it looks like some kind of pressure arrangement will be the way to go. If anyone has any other ideas, I'm all ears. I suspect that even with fiters, periodic cleaning of the core will be required.


Best Regards,

-AC_Hacker

* * *
Attached Thumbnails
Click image for larger version

Name:	core-pile.jpg
Views:	24261
Size:	36.9 KB
ID:	818   Click image for larger version

Name:	core-corner.jpg
Views:	14974
Size:	46.2 KB
ID:	819  

Last edited by AC_Hacker; 06-28-10 at 07:16 PM..
AC_Hacker is offline   Reply With Quote
Old 06-28-10, 08:22 PM   #53
mrd
Apprentice EcoRenovator
 
Join Date: Feb 2010
Location: Milford, DE
Posts: 106
Thanks: 5
Thanked 9 Times in 9 Posts
Default

Hopefully pressure alone will be enough to maintain isolation of the two air streams. If not, 3M spray adhesive #72 says it bonds polypropylene. Not sure if it would be safe for household air, once adhered. The MSDS shows hazards, but I don't know if that's only while in aerosol form, or what.
mrd is offline   Reply With Quote
Old 06-29-10, 06:20 AM   #54
Daox
Administrator
 
Daox's Avatar
 
Join Date: Aug 2008
Location: Germantown, WI
Posts: 5,525
Thanks: 1,162
Thanked 374 Times in 305 Posts
Default

I guess I'd try to use some material that has a decent heat transfer rating.
__________________
Current project -
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.



To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
&
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
Daox is offline   Reply With Quote
Old 06-29-10, 07:43 AM   #55
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default

As I said above, "I would try a very small shot of spray glue between sheet layers.
Just a mist of Duro All-Purpose Spray Adhesive."
@Local hardware stores.
In the directions, they say to spray 'one surface', so you can re-posistion.
If you spray Both surfaces, it's an Instant bond. Faster than super glue!


Anyways, the idea being, use very-very little adhesive. One molecule thick if possible..
That should give you the best possible coro-to-coro contact.

I've put off cutting my coroplas, since I've been so dang busy with car-recall, medical, dental, basement repairs, & FiOs problems..

Now, I just might wait to see how your DIY OFC (One Foot Cube) works out,
before I start hacking my little 8" Cube..
Xringer is offline   Reply With Quote
Old 06-29-10, 12:15 PM   #56
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default 8 inch cube

Quote:
Originally Posted by Xringer View Post
Now, I just might wait to see how your DIY OFC (One Foot Cube) works out, before I start hacking my little 8" Cube..
I've been pouring over more literature, looking at cross-flow Heat Recovery Ventilators and their reported efficiencies. Here are some HRV's that use almost identical design concepts and are almost identical in size.


NOTE:
The Panasonic is different because it is a design meant for one modest room, and is designed to fit between ceiling joist spaces. This is of special interest to me because I have limited the amount of my house that I heat and cool.
(info here)
I think the brand-to-brand efficiencies should be cautiously compared because there are so many ways to 'enhance' test results, with the lower numbers shown probably being closer to reality.

But the variations within a brand are probably a reliable indicator. In that light I find it interesting that the lower the CFM, the higher the efficiency.

My house is pretty small to begin with, and I'm not heating/cooling the whole thing, so my heating/cooling bills have been laughably small. But, eco-minded tightwad such as I am, I'm constantly trying to beat it down even smaller.

So most of the HRV's on the chart above are meant to be used with a house of 1600 feet and above (up to 3500 sq ft) , which is how the American market usually lives. But my conditioned space is only about 600 sq ft, so with the exception of the Panasonic, even on the lowest setting, the HRV's are changing out air at twice the optimum rate for my house-space... I wouldn't even be able turn it down... only off.

I looked at the scale drawing of the Panasonic, in particular the core, and did a graphic divide across the length dimension and came up with the size of the core being 5.5 inches square. Pretty darn small. But the efficiency is pretty darn average...

Using the criteria supplied by mrd in a previous post,

Quote:
ASHRAE 62.2 is residential ventilation industry standard, and I believe the latest version stipulates 7.5CFM/occupant + 1CFM/100sqft
My house is small (600 sq ft) and single occupancy, so:

7.5CFM + 6CFM = 13.5CFM = minimum ventilation.

So I'm thinking that the core I am copying is really appropriate for a much bigger house (4x to 10x bigger), but if I am very careful in the selection of my fans and achieve a CFM of 15CFM minimum, my efficiency should be pretty favorable.

So Xringer depending on your conditioned house volume, your little 8 inch cube may not be so little after all...

-AC_Hacker
Attached Thumbnails
Click image for larger version

Name:	HRV efficiencies compared.gif
Views:	10509
Size:	5.5 KB
ID:	820  

Last edited by AC_Hacker; 06-29-10 at 02:20 PM..
AC_Hacker is offline   Reply With Quote
Old 06-29-10, 01:42 PM   #57
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default What??

Am I reading that right? The Airiva cores are the best? Better than Aluminum?
How the heck can plastic be better than aluminum??

My off-hand guess on for the Panasonic cube was 4.5"x4.5"xn"..

So, maybe I should see if I find enough coro to make a box too..
Xringer is offline   Reply With Quote
Old 06-29-10, 01:59 PM   #58
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by Xringer View Post
Am I reading that right? The Airiva cores are the best?
Ariva cores might be the best, then again their test results might be the most 'enhanced'. You really can't compare unless one lab did all the testing under identical conditions and also did the reporting, treating all data by the same criteria.

Don't be fooled by numbers.

-AC_Hacker
AC_Hacker is offline   Reply With Quote
Old 06-29-10, 06:21 PM   #59
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default

Did that chart come from the Airiva website?

Yeah, maybe I better wait until you have done some testing..
Xringer is offline   Reply With Quote
Old 06-29-10, 07:41 PM   #60
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default HVR Links of Interest...

HVR links of interest:

Here's one from UK that is a cointer-flow and claims 80% efficiency. 80 percent seems to be a suspiciously round number to me. Not much detail pictured, but I'd guess it to be a cross-flow that has been flattened out like a squashed "X" and called a cross-flow.
http://www.fahrenergy.co.uk/FAHR_Installation.pdf

Here's a paper that is done by the University of South Dakota. Note the efficiency numbers there. They aren't trying to sell anything.
http://www.ag.ndsu.edu/pubs/ageng/structu/ae1393.pdf

Here's a FAQ done by the University of Minnesota.
Common Questions about Heat and Energy Recovery Ventilators

Here's a Guy named Marsen who installed one (Airiva) in his workshop in Maine. Well documented. Curiously, he never comments on the quality of the air after the installation.
Guy Marsden - Installing a heat recovery ventilation system in my workshop

Here's a paper that focuses on using the ERV in primarily hot humid climates.
http://www.advancedenergy.org/buildi...lation/erv.pdf

-AC_Hacker


Last edited by AC_Hacker; 06-30-10 at 01:47 AM..
AC_Hacker is offline   Reply With Quote
The Following User Says Thank You to AC_Hacker For This Useful Post:
jeff5may (02-09-21)
Reply


Tags
erv, heat recovery, hrv

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 07:35 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design