Old 03-26-20, 10:28 PM   #11
menaus2
Apprentice EcoRenovator
 
Join Date: Feb 2011
Location: Driftless Region, North America, Earth, Solar System, Orion Arm, Milky Way Galaxy,Virgo Supercluster
Posts: 116
Thanks: 13
Thanked 34 Times in 25 Posts
Default

The world slows down, but construction continues! Framing has been completed. The shed wall isn't exactly plumb, but it's level. Good enough! I siliconed (black silicone) the wood to keep moisture out on back side. Next is the 1" polyiso board (staggered). Then pine 3/4"x 1.5"s to finish the glazing support. Glazing support is set back 1/2" to allow the polycarbonate to be siliconed on the outside. I put 2" strips of polyiso on the inside edge of the frame to finish up the insulation. Currently working on putting up the 1/2" OSB panels over the polyiso. All the piping/ collector fins will be eventually stapled to the OSB.

The underground insulated pex I got is the reflexive bubble wrap inside of drain tile style. Some online sources point out they can lose a ton of heat if water gets into the pipe. Does anyone have experience with wood boiler pipe like this? I was thinking I might install sock drain tile pipe beneath it just incase the pipe ever got punctured to keep it dry enough. Possibly a drain hole at the low point of the underground boiler pipe just to give the water an escape route in case water ever did get in?




















Attached Thumbnails
Click image for larger version

Name:	20200326_125451.jpg
Views:	934
Size:	588.0 KB
ID:	8899   Click image for larger version

Name:	20200326_125508.jpg
Views:	904
Size:	539.3 KB
ID:	8900   Click image for larger version

Name:	20200326_125521.jpg
Views:	925
Size:	545.2 KB
ID:	8901   Click image for larger version

Name:	20200326_125713.jpg
Views:	943
Size:	550.7 KB
ID:	8902   Click image for larger version

Name:	20200326_131050.jpg
Views:	917
Size:	582.3 KB
ID:	8903  

Click image for larger version

Name:	20200326_133346.jpg
Views:	923
Size:	580.5 KB
ID:	8904   Click image for larger version

Name:	20200326_164552.jpg
Views:	908
Size:	561.7 KB
ID:	8905   Click image for larger version

Name:	20200326_175251.jpg
Views:	945
Size:	543.0 KB
ID:	8906   Click image for larger version

Name:	20200326_175301.jpg
Views:	914
Size:	592.0 KB
ID:	8907   Click image for larger version

Name:	20200326_180824.jpg
Views:	908
Size:	584.9 KB
ID:	8908  


Last edited by Daox; 04-05-20 at 10:34 AM..
menaus2 is offline   Reply With Quote
The Following 2 Users Say Thank You to menaus2 For This Useful Post:
Daox (04-05-20), jeff5may (04-05-20)
Old 03-28-20, 09:42 AM   #12
menaus2
Apprentice EcoRenovator
 
Join Date: Feb 2011
Location: Driftless Region, North America, Earth, Solar System, Orion Arm, Milky Way Galaxy,Virgo Supercluster
Posts: 116
Thanks: 13
Thanked 34 Times in 25 Posts
Default

Had nice weather yesterday before rain moved in, so prioritized making sure the OSB was protected enough since it shouldn't get wet & I don't have plastic laying around. Sealed up all the seams with silicone & painted over with flat black spray paint.

For additional protection, I used aluminum facia trim for a roof. Scrap block pieces from the glazing support gave it a little pitch. Screwed it down with roofing screws that were laying around. When things dry up, installing the pex-al-pex pipe & absorber fins will be next.

Also, looking at the actual dimensions & depending how I do the glazing the collector area is looking more like 118-125 square feet.









Attached Thumbnails
Click image for larger version

Name:	20200327_135821.jpg
Views:	775
Size:	595.8 KB
ID:	8910   Click image for larger version

Name:	20200327_163215.jpg
Views:	772
Size:	571.3 KB
ID:	8911   Click image for larger version

Name:	20200327_165121.jpg
Views:	736
Size:	585.7 KB
ID:	8912   Click image for larger version

Name:	20200327_165125.jpg
Views:	743
Size:	569.6 KB
ID:	8913   Click image for larger version

Name:	20200327_180028.jpg
Views:	775
Size:	601.7 KB
ID:	8914  


Last edited by Daox; 04-05-20 at 10:35 AM..
menaus2 is offline   Reply With Quote
The Following User Says Thank You to menaus2 For This Useful Post:
jeff5may (04-05-20)
Old 04-04-20, 10:19 AM   #13
menaus2
Apprentice EcoRenovator
 
Join Date: Feb 2011
Location: Driftless Region, North America, Earth, Solar System, Orion Arm, Milky Way Galaxy,Virgo Supercluster
Posts: 116
Thanks: 13
Thanked 34 Times in 25 Posts
Default

Construction continues into the slow tedious phase of collector pipe and aluminum absorbers. For the back of the absorber I stapled up 3" wide strips of aluminum coilstock. Not sure on the thickness, but good enough I suppose. 8 strips by about 56 feet so about 112 sqft of material.

I'm currently in the middle of stamping out the absorber find & installing them. Helps break up the monotony of either task . The front absorber plates are cut with power shears into 6" x 24" blanks. Then my sophisticated stamping process consisting of a wooden form, 5/8" steel rod, junk boards, mallet and a post pounder. With ever 200 to make total, needless to say it will take a while.

But when the weather is nice, I can install the absorbers. The pex-al-pex doesn't need a perfect level, just a few beads of silicone for good contact & some narrow crown staples does the trick. Just a matter of time, since this is probably the single most time consuming step of construction.



















Attached Thumbnails
Click image for larger version

Name:	20200330_123728.jpg
Views:	750
Size:	584.2 KB
ID:	8923   Click image for larger version

Name:	20200330_143125.jpg
Views:	746
Size:	596.1 KB
ID:	8924   Click image for larger version

Name:	20200330_193856.jpg
Views:	733
Size:	597.3 KB
ID:	8925   Click image for larger version

Name:	20200330_195856.jpg
Views:	767
Size:	450.0 KB
ID:	8926   Click image for larger version

Name:	20200330_200143.jpg
Views:	746
Size:	457.4 KB
ID:	8927  

Click image for larger version

Name:	20200330_200750.jpg
Views:	737
Size:	478.9 KB
ID:	8928   Click image for larger version

Name:	20200331_133238.jpg
Views:	724
Size:	594.7 KB
ID:	8929   Click image for larger version

Name:	20200331_165459.jpg
Views:	719
Size:	525.7 KB
ID:	8930   Click image for larger version

Name:	20200331_170410.jpg
Views:	726
Size:	572.8 KB
ID:	8931   Click image for larger version

Name:	20200403_111626.jpg
Views:	742
Size:	593.7 KB
ID:	8932  


Last edited by Daox; 04-05-20 at 10:37 AM..
menaus2 is offline   Reply With Quote
The Following User Says Thank You to menaus2 For This Useful Post:
jeff5may (04-05-20)
Old 04-05-20, 10:43 AM   #14
Daox
Administrator
 
Daox's Avatar
 
Join Date: Aug 2008
Location: Germantown, WI
Posts: 5,525
Thanks: 1,162
Thanked 374 Times in 305 Posts
Default

Its coming along great!

How much work is it to stamp out those heat spreaders?
__________________
Current project -
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.



To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
&
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
Daox is offline   Reply With Quote
Old 04-05-20, 12:45 PM   #15
pinballlooking
Super Moderator
 
pinballlooking's Avatar
 
Join Date: Jun 2013
Location: SC
Posts: 2,923
Thanks: 172
Thanked 564 Times in 463 Posts
Default

Great progress.
__________________
Current project Aquaponics system , Passive Solar Greenhouse build

To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.

Solar Install 12.5 Kwh-
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.

Mini Split installs -
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.

EV Chevy Volt -
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
pinballlooking is offline   Reply With Quote
Old 04-07-20, 06:26 PM   #16
menaus2
Apprentice EcoRenovator
 
Join Date: Feb 2011
Location: Driftless Region, North America, Earth, Solar System, Orion Arm, Milky Way Galaxy,Virgo Supercluster
Posts: 116
Thanks: 13
Thanked 34 Times in 25 Posts
Default

Quote:
Originally Posted by Daox View Post
Its coming along great!

How much work is it to stamp out those heat spreaders?
Thank you for the kind words. Yes, it's a good amount of work with over 200 to stamp out. After a while you figure out the "technique" and easier when you get the post pounder to bounce a bit.
menaus2 is offline   Reply With Quote
Old 04-11-20, 10:42 AM   #17
menaus2
Apprentice EcoRenovator
 
Join Date: Feb 2011
Location: Driftless Region, North America, Earth, Solar System, Orion Arm, Milky Way Galaxy,Virgo Supercluster
Posts: 116
Thanks: 13
Thanked 34 Times in 25 Posts
Default

Absorber fin installation continues! A little over halfway done. I've spray painted completed sections to get an idea what it'll look like finished (as well as a motivation boost!) Straightening out the pex-al-pex takes time and patience. I'm doing my best to keep them equal lengths so the flow is balanced between the 4 separate runs. It sure takes a lot of silicone!





Attached Thumbnails
Click image for larger version

Name:	20200404_161801.jpg
Views:	698
Size:	597.8 KB
ID:	8935   Click image for larger version

Name:	20200406_180042.jpg
Views:	680
Size:	601.8 KB
ID:	8936   Click image for larger version

Name:	20200410_170936.jpg
Views:	679
Size:	596.8 KB
ID:	8937  

Last edited by Daox; 04-12-20 at 10:58 AM..
menaus2 is offline   Reply With Quote
The Following 2 Users Say Thank You to menaus2 For This Useful Post:
Daox (04-12-20), jeff5may (04-18-20)
Old 04-18-20, 09:51 AM   #18
menaus2
Apprentice EcoRenovator
 
Join Date: Feb 2011
Location: Driftless Region, North America, Earth, Solar System, Orion Arm, Milky Way Galaxy,Virgo Supercluster
Posts: 116
Thanks: 13
Thanked 34 Times in 25 Posts
Default

Absorber fins and painting are done! I did my best to make everything an equal length, but I'm sure each run will be off a bit.

Does anyone have an idea how much difference in flow there might be between the 4 loops or how much this could impact performance? Say if there were 6-9" differences in loop lengths? Extra valves & gauges to balance things perfectly could add up. Maybe adding ball valves & use an IR camera with glazing off to see imbalances? I'm guessing higher flow in one loop would show up cooler than the others?

Anyways, the next step is digging a trench for the piping. I will be laying draintile underneath the wrap style insulated pipe to protect it from getting water inside of it. It will have the added benefit of keeping the yard & basement a little dryer!





Attached Thumbnails
Click image for larger version

Name:	20200411_175633.jpg
Views:	659
Size:	580.6 KB
ID:	8938   Click image for larger version

Name:	20200416_181542.jpg
Views:	682
Size:	595.4 KB
ID:	8939   Click image for larger version

Name:	20200416_195959.jpg
Views:	649
Size:	575.1 KB
ID:	8940  

Last edited by Daox; 04-18-20 at 10:55 AM..
menaus2 is offline   Reply With Quote
The Following User Says Thank You to menaus2 For This Useful Post:
jeff5may (04-18-20)
Old 04-18-20, 10:57 AM   #19
Daox
Administrator
 
Daox's Avatar
 
Join Date: Aug 2008
Location: Germantown, WI
Posts: 5,525
Thanks: 1,162
Thanked 374 Times in 305 Posts
Default

It looks like your setup is roughly 62 feet (750 inches) long? So, plus or minus 9 inches isn't going to matter much at all. 9/750 = .012, so 1% flow difference. Not worth any worry.


It look awesome by the way!
__________________
Current project -
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.



To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
&
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
Daox is offline   Reply With Quote
Old 04-30-20, 10:45 PM   #20
menaus2
Apprentice EcoRenovator
 
Join Date: Feb 2011
Location: Driftless Region, North America, Earth, Solar System, Orion Arm, Milky Way Galaxy,Virgo Supercluster
Posts: 116
Thanks: 13
Thanked 34 Times in 25 Posts
Default

Quote:
Originally Posted by Daox View Post
It looks like your setup is roughly 62 feet (750 inches) long? So, plus or minus 9 inches isn't going to matter much at all. 9/750 = .012, so 1% flow difference. Not worth any worry.


It look awesome by the way!
Whew! Thanks for the info!

Since my last post, I've gotten the underground pipe in (mostly). It was easily a week of digging and probably the hardest part of the whole project so far since it was mostly done with just a shovel. Rocks are not fun!

Basically I dug down 28"-30" made sure everything had a slight slope with a level. I then laid landscape fabric along the bottom of the trench. Over the fabric I laid about 1" layer of washed river rock. Over that base layer of rock I laid a 4" socked perforated corrugated pipe. Then filled the pipe up to its top with more river rock. The extra landscape fabric in the trench folded over the top over the rock & pipe like a big ol' burrito.

Theeeeen, my corrugated underground boiler pipe laid over the drain pipe and I buried by a few inches with some of the nicer soil. I put some strips of 250 psi XPS polyiso over that. I figured it would add some insulation & strength to protect the boiler pipe. The rest of the trench I could backfill with rockier and rougher soil.

At the lowest part of the boiler pipe before it pokes up near the house, I put a bunch of holes in the outside of it in a 1-2 foot section. That style of boiler pipe is basically useless if it fills with water. By keeping the surround soil dry with the drainage below it, then sloping it to a drained low point, it should allow any water that eventually works it's way in to be naturally drained through those holes. Boy I really hope it does, because it was a lot of work to dig it up again! In retrospect, I would've gone with thermopex.

What remains:
1. Hooking up pipes & run sensor wires
2. Run pump & check for leaks
3. Wiring controls
4. Attach glazing
5. The separate pump & controls for the furnace heat exchanger (less important as we're coming out of the heating season).
6. Make things pretty, maybe cut down a few trees if they block the panel too much.

menaus2 is offline   Reply With Quote
The Following User Says Thank You to menaus2 For This Useful Post:
Daox (05-05-20)
Reply


Tags
heating, pex, solar, thermal, water

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 05:31 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design