Old 12-18-14, 06:41 PM   #31
Mikesolar
Master EcoRenovator
 
Mikesolar's Avatar
 
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
Default

OK., assuming Randon has 3/4" tubing, he has a heat exchange surface area of 706 ft2. He will have to say what the spacing and ground cover area is being used.

Yours is 1256 ft2 of surface area but there is not a direct correlation between the surface area of two different tube sizes and their heat transfer. The majority of the fluid just flows through the centre and it takes a lot longer to exchange the heat. On top of this is the problem of low turbulence in a big pipe, further reducing heat transfer.

My rough guess is that you have perhaps the same heat transfer as Randen does, all other things being equal so i expect 6 tons is difficult to achieve. This is just a rough thought tho...

Mikesolar is offline   Reply With Quote
Old 12-19-14, 12:17 AM   #32
SDMCF
Apprentice EcoRenovator
 
Join Date: Jul 2014
Location: Finland
Posts: 125
Thanks: 5
Thanked 35 Times in 34 Posts
Default

It doesn't seem particularly low to me. I see similar temperatures from our ground loop, and ours also goes below 0 at times. In our climate we have similar low temperatures to you so maybe it is a valid comparison.

I think you would have been better to have dug longer trenches but not so deep. I have read claims that putting the ground loop too deep reduces performance year-on-year because the ground at that depth doesn't get re-heated so much during summer. I can't say if that is correct or not but it seems sort of logical. Still, I wouldn't be too concerned at the temperatures you report. I would look more to the house or the heat pump rather than the ground loop.
SDMCF is offline   Reply With Quote
Old 12-19-14, 04:51 AM   #33
stevehull
Steve Hull
 
Join Date: Dec 2012
Location: hilly, tree covered Arcadia, OK USA
Posts: 826
Thanks: 241
Thanked 165 Times in 123 Posts
Default

Mechanic,

I agree with AC. Check air infiltration with blower door test and replace bathroom vents with small ERVs.

Something is not right.


Steve
__________________
consulting on geothermal heating/cooling & rational energy use since 1990

Last edited by stevehull; 12-19-14 at 05:02 AM..
stevehull is offline   Reply With Quote
Old 12-20-14, 06:16 AM   #34
Mikesolar
Master EcoRenovator
 
Mikesolar's Avatar
 
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
Default

It is almost never good to oversize a HP unless you are able to store the extra heat in a big buffer tank. First, the compressor should be limited to 4-5 starts per hour for longevity and 6 tons is a lot for a house like yours. That is one reason why I think it would be useful to limit it to stage one if possible and see what transpires. It may be a better balance for the loop size.

With an ICF basement (and I assume at least 2" of foam underslab) there should be minimal heat loss there. I'm not too familiar with RTM construction but a typical 2x6 wall with glass insulation and without 2" of foam on the outside may barely meet code. I would get that blower door test done. There was a report recently that showed OSB to be quite porous to moisture so should not be considered as a moisture barrier by itself.

What is the exterior finish of the house and do you think 2-3" of EPS foam could go on there? It would do wonders for the heat load.
Mikesolar is offline   Reply With Quote
Old 12-20-14, 09:01 AM   #35
mechanic
Apprentice EcoRenovator
 
Join Date: Aug 2014
Location: Saskatchewan, Canada
Posts: 117
Thanks: 10
Thanked 16 Times in 12 Posts
Default

It's 2x6 with typar wrap on the outside then vinyl siding. I ordered one of those flir iPhone cameras for our business, at that price it should be a pretty useful tool. I'll maybe price out that blower test, were 65km out of the city so mileage is a killer... I blocked out stage 2 for now. Hp manual says that limits it to 67%.
mechanic is offline   Reply With Quote
Old 12-20-14, 09:03 AM   #36
mechanic
Apprentice EcoRenovator
 
Join Date: Aug 2014
Location: Saskatchewan, Canada
Posts: 117
Thanks: 10
Thanked 16 Times in 12 Posts
Default

Quote:
Originally Posted by SDMCF View Post
It doesn't seem particularly low to me. I see similar temperatures from our ground loop, and ours also goes below 0 at times. In our climate we have similar low temperatures to you so maybe it is a valid comparison.

I think you would have been better to have dug longer trenches but not so deep. I have read claims that putting the ground loop too deep reduces performance year-on-year because the ground at that depth doesn't get re-heated so much during summer. I can't say if that is correct or not but it seems sort of logical. Still, I wouldn't be too concerned at the temperatures you report. I would look more to the house or the heat pump rather than the ground loop.
Our frost line is at least 6', can they be run that much closer?
mechanic is offline   Reply With Quote
Old 12-20-14, 09:06 AM   #37
mechanic
Apprentice EcoRenovator
 
Join Date: Aug 2014
Location: Saskatchewan, Canada
Posts: 117
Thanks: 10
Thanked 16 Times in 12 Posts
Default

As far as the extra insulation I guess a guy could pull all the siding down and add it in, would be a fairly big job though...
mechanic is offline   Reply With Quote
Old 12-20-14, 10:01 AM   #38
randen
Uber EcoRenovator
 
Join Date: Apr 2011
Location: Strathroy Ontario Canada
Posts: 657
Thanks: 9
Thanked 191 Times in 129 Posts
Default

Mechanic

Man now your talking. Putting a big overcoat on your home. HUGE. You would eliminate the bridging with the 2 x 6.

I have an acquaintance he install two layers of foam on the exterior. I believe first a shiplap blue SM with taped joints and then he followed with another layer of foam for the stucco. In the end I think he was using recessed plastic plugs with 3 1/2" screws. a good 3" of foam on a 2 x 6 wall.

Randen
randen is offline   Reply With Quote
Old 12-20-14, 02:11 PM   #39
SDMCF
Apprentice EcoRenovator
 
Join Date: Jul 2014
Location: Finland
Posts: 125
Thanks: 5
Thanked 35 Times in 34 Posts
Default

Quote:
Originally Posted by mechanic View Post
Our frost line is at least 6', can they be run that much closer?
I really don't know, and the claims I have seen about problems running the loop too near the surface are not something I have seen proven anyway. Perhaps someone else has better knowledge, but even if true I don't think that is your real/main problem.
SDMCF is offline   Reply With Quote
Old 12-20-14, 05:50 PM   #40
Mikesolar
Master EcoRenovator
 
Mikesolar's Avatar
 
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
Default

There are a few important things here. First, the heat load is LARGE for todays houses. Is there foam under the basement floor? If not, take up the wood and put some down, minimum of 3" for your area. The walls need to have the foam. It doesn't need to be SM, it can be higher density EPS like the stucco guys use....and a minimum of 3" thick. Then Typar, then vertical slats about 8" apart made of 1/2" plywood (not OSB). This allows a rainscreen so that any moisture that does get behind the siding (and it will do so) can run down to the foundation and out, without being held against the typar (which is what you have now). This will keep the Typar dry and extend it's life. I have seen wet Typar after 4-5 years and it is not good. Then put the siding onto the slats.


Last edited by Mikesolar; 12-20-14 at 05:52 PM..
Mikesolar is offline   Reply With Quote
Reply



Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 08:28 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design