01-25-14, 10:44 PM | #31 |
Supreme EcoRenovator
Join Date: Oct 2008
Location: Austin, TX
Posts: 1,154
Thanks: 14
Thanked 257 Times in 241 Posts
|
Private IPs will not work over the Internet...
__________________
To my surprise, shortly after Naomi Wu gave me a bit of fame for making good use of solar power, Allie Moore got really jealous of her... |
01-27-14, 11:41 AM | #32 |
Lex Parsimoniae
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
|
Yes, but they work fine for me. Since the CIA board is plugged into my router.
~~~~~~ Current copy of program: START DELAY 400 MUL CH 60 RAM8 ADD RAM8 CM VAR8 SET VAR1 T1 SET VAR2 T2 SET VAR3 T3 SET VAR5 T4 SET VAR4 H1 TSTEQ VAR4 0 SET VAR4 707 SET RAM7 0 SET VAR7 0 ADD VAR1 48 VAR6 CALLSUB CALLER END CALLER: TSTLE VAR8 480 RET TSTGT VAR8 1140 RET TSTLE VAR5 VAR6 CALLSUB FAN_OFF TSTLE VAR5 VAR6 RET TSTGT VAR4 80 CALLSUB FAN_OFF TSTLE VAR4 80 CALLSUB FAN_ON RET FAN_ON: X10 2 7 1 DELAY 1000 X10 2 7 1 SET OP1 1 SET OP2 0 SET RAM7 900 CALLSUB TIME10 SET RAM7 0 RET FAN_OFF: DELAY 1000 X10 2 7 0 DELAY 1000 X10 2 7 0 SET OP1 0 SET OP2 1 SET RAM7 900 CALLSUB TIME10 SET RAM7 0 RET TIME10: SET VAR7 0 MIDEE: DELAY 1000 TSTEQ VAR7 RAM7 RET INC VAR7 GOTO MIDEE As of 1/27/14
__________________
My hobby is installing & trying to repair mini-splits EPA 608 Type 1 Technician Certification ~ 5 lbs or less.. |
01-28-14, 05:03 PM | #33 |
Lex Parsimoniae
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
|
Note:
Due to NSA snooping on Yahoo, Yahoo promises encryption as NSA’s email and IM contact list collection is exposed — Tech News and Analysis Their email now require SSL/TLS security, which webcontrol WC8 CAI does not support. Unless you buy the new larger memory WC32 board. Yahoo is out. ~~~Edit~~~ Got the email notify to work with @gmx.com
__________________
My hobby is installing & trying to repair mini-splits EPA 608 Type 1 Technician Certification ~ 5 lbs or less.. Last edited by Xringer; 02-07-14 at 03:47 PM.. Reason: @gmx.com |
02-07-14, 04:55 PM | #34 |
Lex Parsimoniae
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
|
More extra cold nights ahead..
Our Sanyo ASHP heaters started resetting this morning, when it got too cold for them.
They have been hacked to draw a max of 10A (2.5kW) before the power shuts off. That Accuweather forecast predicted it would stay above 10.0 °F all night. My wife heard at least one reset 6:28am. It was 6.0°F at 7:13am. I know these things don't work very well below 10.0°F, and use a LOT of power at those temps. Hence the 10A shut-down. At midnight, I checked and the temperature seemed to be going up. Slept late and never noticed any shutdowns or chilliness. So, temperatures in the single digits seem to be more common now.. My fix, is a software temperature alarm set for 12°F. When the outdoor temperature is less than 12°F, the CAI will send a signal to the X-10 in the living-room. The X10 will supply 12VDC to a back-up-alarm. The alert is a nice Asian lady, saying "Attention please, this car is backing up"..
__________________
My hobby is installing & trying to repair mini-splits EPA 608 Type 1 Technician Certification ~ 5 lbs or less.. |
02-07-14, 05:43 PM | #35 |
Supreme EcoRenovator
Join Date: Oct 2008
Location: Austin, TX
Posts: 1,154
Thanks: 14
Thanked 257 Times in 241 Posts
|
Connect the 12V to some resistors (small heaters) set underneath the remotes. Now it will automatically scale them back.
__________________
To my surprise, shortly after Naomi Wu gave me a bit of fame for making good use of solar power, Allie Moore got really jealous of her... |
02-07-14, 07:47 PM | #36 |
Lex Parsimoniae
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
|
I've considered that idea before. The 'install' job has too many strikes against it.
If I could snake wire to where it was needed, it would be a good way to go. Plus, there isn't an idea location for the Tstat in the den. Like a TV remote, it's always being moved around. Especially on sunny days. If it sits in the sun, the heat goes right off. I want to be awakened, so I can decide which back-up heat to use, and how I want it set up (depending on the hour). If the sun is coming up in 30 minutes, I'll just use space heaters and leave the oil in it's tank. I've ordered a cheap voice record/playback board. It's on it's way from China. ISD1820 Voice Recording Recorder Module with Mic Sound Audio Loudspeaker New | eBay If it's loud enough to wake me, I'll use it, instead of the car-back-up alert. (That will be installed on my car.. Someday). The nice part about using this method.. If the forecast is wrong, and it stays above 12F all night, I don't have to worry about the Sanyos, because I'll be sleeping like an old dog.. Three times this year, the forecast has been wrong, and I've wasted oil, by programming the (oil burner) timer, based on the hourly forecast.
__________________
My hobby is installing & trying to repair mini-splits EPA 608 Type 1 Technician Certification ~ 5 lbs or less.. |
02-08-14, 10:32 AM | #37 |
Lex Parsimoniae
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
|
PLC program 2-8-14
This is today's version with the warning to turn on oil heat etc..
The new section is Caller2, and it's the first call made out of the Main. Caller2 checks the outdoor temp. (Later I will add in other checks). If outdoors is colder than 12F, then heat_on: is called. heat_on: runs the X10 connected to the alarm horn for 45 seconds, shuts it off and returns to caller2: then to Main. This cycle will repeat endlessly, until intervention, or warmer weather. My plan is to unplug the voice module X10, and turn on the back-up heat, and go back to bed.. ~~~ Start delay 5001 mul ch 60 ram8 add ram8 cm var8 set var1 t1 set var2 t2 set var3 t3 set var5 t4 set var4 h1 tsteq var4 0 set var4 707 set ram7 0 set var7 0 add var1 20 var6 callsub caller2 callsub caller1 end caller1: Delay 100 tstle var8 480 ret tstgt var8 960 ret tstle var5 var6 callsub fan_off tstle var5 var6 ret tstgt var4 80 callsub fan_off tstle var4 80 callsub fan_on ret fan_on: Delay 1000 x10 2 7 1 delay 1000 x10 2 7 1 set op1 1 set op2 0 set ram7 900 callsub time10 set ram7 0 ret fan_off: Delay 1000 x10 2 7 0 delay 1000 x10 2 7 0 set op1 0 set op2 1 set ram7 900 callsub time10 set ram7 0 ret caller2: Delay 1000 tstle var3 121 callsub heat_on ret heat_on: Delay 1000 x10 2 1 1 delay 1000 x10 2 1 1 set op3 1 set op4 0 set ram7 45 callsub time10 set ram7 0 delay 1000 x10 2 1 0 delay 1000 x10 2 1 0 set op3 0 set op4 1 ret time10: Set var7 0 midee: Delay 1000 tsteq var7 ram7 ret inc var7 goto midee
__________________
My hobby is installing & trying to repair mini-splits EPA 608 Type 1 Technician Certification ~ 5 lbs or less.. |
03-04-14, 10:57 AM | #38 | |
Supreme EcoRenovator
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 724 Times in 534 Posts
|
Quote:
I admire your tenacity in trying to make your Sanyos do what you want them to do in spite of their limitations. However, jeff5may has identified a model of Mitsubishi that will continue to work well down into the temperature range that is proving to be so vexing for you. You have accumulated a lot of knowledge about just what conditions you are facing, and exactly how much heat you are losing. Apparently, seriously upgrading your insulation will never be an option for you, so... Perhaps it is time to upgrade your heating system with more modern Mitsubishi(s) and sell your Sanyos to someone who is in a slightly warmer climate. -AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker... |
|
03-04-14, 06:57 PM | #39 |
Lex Parsimoniae
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
|
I really like the idea of upgrading to the low temp Mitsubishi units.
It would be a lot less fuss when it drops really low. These Sanyos had been working just fine during 99% of the heating season.. It's only during this horrible winter that our use of oil heating has jumped so much. I don't mind using oil once in a while, it makes me keep up the maintenance routine on the old boiler. One of these dark days, we might end up burning wood to keep warm. Hey, this might be one of those Once every 100 year winters.. And things will get better. Now my part-time job is gone, we just might be eligible for state fuel assistance. And there's one program that just gives entitled folks 100 gallons for free. I think we could get by on 100 gallons pretty easy. At least during most winters.
__________________
My hobby is installing & trying to repair mini-splits EPA 608 Type 1 Technician Certification ~ 5 lbs or less.. |
|
|