EcoRenovator  

Go Back   EcoRenovator > Improvements > Geothermal & Heat Pumps
Advanced Search
 


Blog 60+ Home Energy Saving Tips Recent Posts


Reply
 
Thread Tools Display Modes
Old 11-19-16, 04:03 AM   #21
b420ady
Helper EcoRenovator
 
Join Date: Nov 2016
Location: Romania
Posts: 47
Thanks: 19
Thanked 0 Times in 0 Posts
Default

Thanks Jeff for your answer, another question I still did not found an answer is that I ve seen that all the pipes are cut so short .... is that normal to cut them so short ???Can they be blazed ? Do I need to flush it because as you see in the photos it looks like it could of got contaminated with moisture as it was stored in the yard

b420ady is offline   Reply With Quote
Old 11-19-16, 07:23 AM   #22
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,431
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

Nope, not normal...the butcher got to it. Looks like the work of a carpenter and his helper. Person one suspended the unit close to the wall, person two hacked with a saw in one hand and a knife in the other. Maybe some wire cutters were involved, maybe not. I imagine all the copper got scrapped immediately with the rest of the demolition. I would just cut the pipes off square where they are not crushed and put flare nuts and unions on the ends. Less chance of burning something and easy to experiment with.

It's safe to say the unit has been exposed to atmosphere for quite a while. I would check the ends of the tubes for bugs or their remains after flaring the ends. Yes, you can still buy pipe cleaners cheaply at the smoke shop. For larger tubing, gun barrel cleaning tools do the trick. Then a double or triple wash with solvent and shop air or welding nitrogen or argon. I like acetone or brake cleaner. Finally, a double rinse and blowout with whatever oil your compressor likes. Any tiny residue of solvent or moisture will come out with a vacuum pump when the plumbing is sealed. Make sure installer uses a vacuum pump and micron vacuum gauge.
jeff5may is offline   Reply With Quote
Old 11-20-16, 08:49 AM   #23
b420ady
Helper EcoRenovator
 
Join Date: Nov 2016
Location: Romania
Posts: 47
Thanks: 19
Thanked 0 Times in 0 Posts
Default

I ve got home the outdoor unit
More photos later
Attached Thumbnails
Click image for larger version

Name:	20161120_133922.jpg
Views:	471
Size:	494.1 KB
ID:	7387  
b420ady is offline   Reply With Quote
Old 11-20-16, 05:15 PM   #24
b420ady
Helper EcoRenovator
 
Join Date: Nov 2016
Location: Romania
Posts: 47
Thanks: 19
Thanked 0 Times in 0 Posts
Default

I was planning to show you the inside of the unit today but apparently some of the screws are to rusted and I could not get them out. I used sume WD40 but still I did not had any luck yet....
Anyway maybe there is someone here that can identify the real brand of this unit
Attached Thumbnails
Click image for larger version

Name:	1.jpg
Views:	490
Size:	270.0 KB
ID:	7389   Click image for larger version

Name:	20161120_210906.jpeg
Views:	490
Size:	389.6 KB
ID:	7390   Click image for larger version

Name:	20161120_210707.jpeg
Views:	481
Size:	380.5 KB
ID:	7391   Click image for larger version

Name:	20161120_210930.jpeg
Views:	494
Size:	237.3 KB
ID:	7392   Click image for larger version

Name:	20161120_210943.jpeg
Views:	507
Size:	422.2 KB
ID:	7393  

Click image for larger version

Name:	20161120_211039.jpeg
Views:	492
Size:	374.5 KB
ID:	7394   Click image for larger version

Name:	20161120_211638.jpg
Views:	542
Size:	512.4 KB
ID:	7395   Click image for larger version

Name:	20161120_211645.jpg
Views:	495
Size:	496.3 KB
ID:	7396   Click image for larger version

Name:	20161120_211655.jpg
Views:	497
Size:	547.7 KB
ID:	7397  
b420ady is offline   Reply With Quote
Old 11-20-16, 08:00 PM   #25
b420ady
Helper EcoRenovator
 
Join Date: Nov 2016
Location: Romania
Posts: 47
Thanks: 19
Thanked 0 Times in 0 Posts
Default

I ve seen some interesting heat exchangers that I think I can replicate, please let me know what you think about them and if you have other ideas or which one do you think I should chose.
For sure I will have to buy a torch and begin building some skill with those pipes.

https://www.alibaba.com/product-deta...093599136.html

https://www.olx.ro/oferta/pahlen-ab-...tml#66f8c215e6


and there are other designs that use multiple pipes, smaller in diameter, but can someone here help me get the correct sizing for it and maybe some other tips.
b420ady is offline   Reply With Quote
Old 11-20-16, 08:32 PM   #26
b420ady
Helper EcoRenovator
 
Join Date: Nov 2016
Location: Romania
Posts: 47
Thanks: 19
Thanked 0 Times in 0 Posts
Default

I ve found a webstore from my country were I can get for 40 USD a 25 METERS roll of Cu pipe 6 mm diameter , 1 mm thick
What do you think ? this will do ?

How do I calculate how big my heat exchanger should be ??? or I just match the volume of the actual pipes in the air heat exchanger from the outdoor unit ???

I know the COP of a water source heat pump is greater than a air source water pump .... so my unit will pump more BTU/h than in the actual air feed setup .... do I have to oversize the final volume of the pipes in order to get more BTU/h ?? This might be a stupid question (sorry if so)

please if someone can explain me how much of it do I need for one heat exchanger that will suit my unit

Teava Cupru moale Ø 6 x 1,0mm, Colac de 25 m, Sanha / Diversi producatori

Some info on shell and tubes heat exchanger:
http://www.wermac.org/equipment/heat...ger_part2.html
http://www-unix.ecs.umass.edu/~rlaur.../exchanger.pdf
http://webserver.dmt.upm.es/~isidoro...exchangers.pdf
http://www.piping-engineering.com/he...gn-guide.html#
http://web2.clarkson.edu/projects/su.../shelltube.pdf
https://en.wikipedia.org/wiki/Shell_...heat_exchanger
http://www.hcheattransfer.com/shell_and_tube.html
http://homepages.wmich.edu/~leehs/ME..._corrected.pdf

I want to find a design that won t request to much skill out of my hand with the torch as I never did it befor , so I ll have to use somehow longer tubes lengths

PS: I have a huge archive of files and a lot of websites bookmarks that I should share with you that I ve gathered in my research about geothermal heat pumps ... but please let me know if any of you is interested in it because I have a slow 3g connection and takes a lot of time.


I ve found in the specs of a pool heat pump the next specs:
NTTP125-B1 12.5 KW 9 METERS of Φ12.7mm Cu tube inside a PVC pipe ) Φ200*500 50mm

here is the link: https://www.alibaba.com/product-deta...026150680.html

Last edited by b420ady; 11-20-16 at 10:02 PM.. Reason: PS:
b420ady is offline   Reply With Quote
Old 11-20-16, 09:25 PM   #27
b420ady
Helper EcoRenovator
 
Join Date: Nov 2016
Location: Romania
Posts: 47
Thanks: 19
Thanked 0 Times in 0 Posts
Default

Ok, the outdoor unit has about 30 pipes in that radiator , so the total length will be pretty big so I think I sould buy Cu tube of the same dimension as the unit already have and make a nice shell and tube design...at first I was thinking to use tube smaller in diameter so I have a better heat transfer but I don t think I can do it as it will mean that I ll use a lot of meter ...

Prices of Cu tubes around here:
http://frigmania.ro/index.php?route=...h=64_65_91_139

The shared PDF files folder just became bigger
https://www.dropbox.com/sh/3owy0iq7o...jQSVmrC-a?dl=0
b420ady is offline   Reply With Quote
Old 11-21-16, 09:57 AM   #28
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,431
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

Not that simple. The air source outdoor exchanger must have much more surface area, since air has less heat capacity and thermal conductivity than water. Unless your water flow rate is super high, the water source exchanger will be more compact. I already posted a few links to point you in the right direction. I recommended a coaxial exchanger with turbo tube inside for a reason.

Plate heat exchangers that will stand up to refrigeration pressure aren't the same as the common ones found on the used market. Most of these are rated for maybe 10 bar, you need better pressure rating. The common units are also rated at a higher temperature difference than a heat pump can provide. Depending on specs, you will need to oversize the hx by a large factor. Plus the fouling issue.

A coaxial exchanger made with smooth tubing will need more overall length than one with ribbed or corrugated center tubing, which will drive up the materials cost. The issues of pressure drops, turbulence and spacing between the tubes make more difference for the worse as well. If you have a cheap supply of smooth (inside and shell) tubing and don't mind the extra bulk, go for it. But the easily copied designs pretty much all use high performance inside tubing to save weight and bulk.
jeff5may is offline   Reply With Quote
Old 11-21-16, 08:11 PM   #29
b420ady
Helper EcoRenovator
 
Join Date: Nov 2016
Location: Romania
Posts: 47
Thanks: 19
Thanked 0 Times in 0 Posts
Default

From were I can buy that ribbed or corrugated center pipe at a decent price ?
b420ady is offline   Reply With Quote
Old 11-22-16, 09:31 AM   #30
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,431
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

That depends on what you call a decent price... In your location (Romania), finding a local metal supplier who will sell you small pieces will be the challenge. To mail order the material, international shipping comes into play. For the few meters of tubing you seek, shipping could cost more than the material. I live in the USA, so mail ordering the tubing would be much less expensive.

It may be worthwhile for you to make your own. If you can find inexpensive soft copper tubing, the process is not super difficult. You have to make a tool to do it, though. I'm always short on money, so if I was in your location, I could definitely justify the time and labor to do it myself. Knowing someone with a lathe would save lots of time, but with this type of tubing, you could do it by hand.

Here is a super industrial version of the method:


Straight off the top of my head, I would probably make something resembling a pipe threader head with wheels instead of thread dies in it:

jeff5may is offline   Reply With Quote
Reply



Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 08:09 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design