EcoRenovator  

Go Back   EcoRenovator > Improvements > Solar Heating
Advanced Search
 


Blog 60+ Home Energy Saving Tips Recent Posts


Reply
 
Thread Tools Display Modes
Old 01-13-21, 06:10 AM   #11
solarhotairpanels
Helper EcoRenovator
 
Join Date: Mar 2012
Location: Warwick, Rhode Island
Posts: 92
Thanks: 22
Thanked 29 Times in 18 Posts
Default

Quote:
Originally Posted by Acuario View Post
Have you measured the entry/exit temperatures of the water passing through the tank? And the temperature at the lowest point of the heat exchanger?

What is the delta across the heat exchanger? The water from the panels should enter at the top of the tank heat exchanger (I assume this is what you have).

If the exit temperature is the same as the temperature at the lowest point of the heat exchanger then you have removed all the heat somewhere in the heat exchanger. Try increasing the pump speed until the exit temperature is slightly higher, then reduce it a little, then you know that you have the maximum possible flow rate to get the maximum transfer from the heat exchanger.
Thanks for the response..
NO, I have not measured temps to/from tank heat exchanger but I will now that you mentioned this..

Water from collector enters heat exchanger at lowest point I believe then returns to collector out the higher side of the heat exchanger. I'll double check that.. next time I go down to the basement.

I like your idea about testing temps at higher pump speed to neutralize in/out temps.. makes sense I'll give that a try. Thanks again for your input.

__________________
Pat from Warwick, RI

Please Note:
Comments and/or suggestions I make here at the forums on 'your' projects as well as my own have all been carefully and scientifically calculated by 'the seat of my pants'
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
solarhotairpanels is offline   Reply With Quote
Old 01-13-21, 06:27 AM   #12
Acuario
Apprentice EcoRenovator
 
Join Date: May 2011
Location: Tortosa, Spain
Posts: 221
Thanks: 2
Thanked 81 Times in 46 Posts
Default

If your connections are as you say then they are the wrong way around.
Heat always travels from hot to cold, never the reverse.

You need to feed the hottest water to the hottest point of the tank for it to transfer otherwise you will find the water leaving the top of the heat exchanger may well be the temperature of the hottest water in the tank.
Acuario is offline   Reply With Quote
Old 01-13-21, 07:07 AM   #13
solarhotairpanels
Helper EcoRenovator
 
Join Date: Mar 2012
Location: Warwick, Rhode Island
Posts: 92
Thanks: 22
Thanked 29 Times in 18 Posts
Default

Quote:
Originally Posted by Acuario View Post
If your connections are as you say then they are the wrong way around.
Heat always travels from hot to cold, never the reverse.

You need to feed the hottest water to the hottest point of the tank for it to transfer otherwise you will find the water leaving the top of the heat exchanger may well be the temperature of the hottest water in the tank.
Everything is good.. just checked.
Water from collectors goes to the top connection of heat exchanger / returns from the bottom of heat exchanger.

Been so long since I looked at it.. couldn't remember.
You pursuaded me into putting my fresh coffee down to go check.

good to go!
__________________
Pat from Warwick, RI

Please Note:
Comments and/or suggestions I make here at the forums on 'your' projects as well as my own have all been carefully and scientifically calculated by 'the seat of my pants'
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
solarhotairpanels is offline   Reply With Quote
Old 01-28-21, 06:17 PM   #14
dremd
Need More Eco
 
dremd's Avatar
 
Join Date: Sep 2008
Location: Scott, La
Posts: 172
Thanks: 2
Thanked 6 Times in 6 Posts
Send a message via AIM to dremd
Default

I’m in no way an expert here, but my guess is you are drawing max out of your collectors by keeping them cooled by your tank thus maximizing collection, maybe some math involving tank outlet / inlet temp and electric cost to run pump is in order. That way you are also taking into account losses in plumbing. Again, I’m no expert.
dremd is offline   Reply With Quote
Old 01-29-21, 08:06 AM   #15
solarhotairpanels
Helper EcoRenovator
 
Join Date: Mar 2012
Location: Warwick, Rhode Island
Posts: 92
Thanks: 22
Thanked 29 Times in 18 Posts
Default

Quote:
Originally Posted by dremd View Post
I’m in no way an expert here, but my guess is you are drawing max out of your collectors by keeping them cooled by your tank thus maximizing collection, maybe some math involving tank outlet / inlet temp and electric cost to run pump is in order. That way you are also taking into account losses in plumbing. Again, I’m no expert.
Thanks for your input...

so far so good where I have it set right now.

The 2 - 20 evac tube collectors are heating the storage tank water up above ground water temp which is my main goal.

Pump isn't running constantly.. shuts down and cycles now and then.

12 degrees here today and it's coming on then off to accomplish the mission.

I love it.

__________________
Pat from Warwick, RI

Please Note:
Comments and/or suggestions I make here at the forums on 'your' projects as well as my own have all been carefully and scientifically calculated by 'the seat of my pants'
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
solarhotairpanels is offline   Reply With Quote
Reply



Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 07:09 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design