would this work for a 1 ton system?
Looking at starting a small scale water to water heat pump. Would be a 1 ton compressor. I feel like its of acceptable size but i just wanted to get another opinion..
https://www.ebay.com/itm/Alfa-Laval-...n/293412708504 |
06-08-20, 03:34 PM | #2 |
Supreme EcoRenovator
|
Looks like that heat exchanger is a desuperheater or a radiant floor / driveway melting size. Conservative rating is a half ton of water cooling as an evaporator, about 3/4 ton of heating as a water cooled condenser or desuperheater, and about 10 tons of water heating capacity being fed 180 degF boiler water.