Old 02-19-19, 11:42 AM   #11
Murdock
Lurking Renovator
 
Join Date: Aug 2017
Location: Essen (Belgium)
Posts: 4
Thanks: 1
Thanked 0 Times in 0 Posts
Default

Nice build, professional look

Can you comment a bit on your start-up and shutdown procedure?

Murdock is offline   Reply With Quote
Old 02-19-19, 05:42 PM   #12
pavel
Lurking Renovator
 
Join Date: Jan 2019
Location: Czech Rep.
Posts: 14
Thanks: 0
Thanked 4 Times in 3 Posts
Default

There are three sequences controlled by the software:

START:
- turn both circulation pumps ON
- close EEV by 500 steps, open EEV by 150 steps
- ramp compressor SSR up from 50% to 100% in 800ms
- switch compressor coil relay ON
- switch compressor SSR OFF
https://github.com/burgrp/nanook-js/...r.js#L218-L243

STOP:
- switch compressor SSR ON
- switch compressor coil relay OFF
- switch compressor SSR OFF
- close EEV by 500 steps
- turn both circulation pumps OFF
https://github.com/burgrp/nanook-js/...r.js#L252-L280

MEASURE:
Is a simple sequence launched every 5minutes when HP turned off. It just turns output circulation pump ON for 30seconds, measures water temperature, and then turns the circulation pump OFF. This way there is no need for external temperature sensor.
https://github.com/burgrp/nanook-js/...r.js#L327-L338
pavel is offline   Reply With Quote
The Following User Says Thank You to pavel For This Useful Post:
Geo NR Gee (02-20-19)
Old 02-26-19, 11:55 AM   #13
Murdock
Lurking Renovator
 
Join Date: Aug 2017
Location: Essen (Belgium)
Posts: 4
Thanks: 1
Thanked 0 Times in 0 Posts
Default

looks like you have 3 speed-circulator pumps; Have you allready experimented with the speed of these pumps? I guess you could control the speed via 2 relays
Murdock is offline   Reply With Quote
Old 02-27-19, 04:49 PM   #14
pavel
Lurking Renovator
 
Join Date: Jan 2019
Location: Czech Rep.
Posts: 14
Thanks: 0
Thanked 4 Times in 3 Posts
Default

It could be controlled, but it seems to be not necessary. The secondary side is switched to minimum which is enough to transport the heat to accumulator tank. The primary side is switched to maximum, while the temperature drop is a bit higher then it should be - so I probably need more powerful pump here.
pavel is offline   Reply With Quote
Old 03-24-19, 02:34 PM   #15
pavel
Lurking Renovator
 
Join Date: Jan 2019
Location: Czech Rep.
Posts: 14
Thanks: 0
Thanked 4 Times in 3 Posts
Default

Git repositories have been moved under DEVICE.FARM organization:
https://github.com/device-farm?utf8=...ype=&language=

pavel is offline   Reply With Quote
Reply


Tags
diy, gwhp, heat pump, heat pumps


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 09:01 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design