Can someone explain what the voltage on one lead (+ or -) of a solar panel is?
Obviously testing voltage from one lead to the other is Voc.
From experience, testing voltage from one lead to ground shows a small initial voltage which quickly dissipates to 0. Does this mean that touching the bare conductor from one lead of a panel (or string) presents no shock hazard?

ttpvt1 is offline   Reply With Quote
Old 10-30-18, 06:26 PM   #2
philb
Apprentice EcoRenovator
 
Join Date: Nov 2010
Location: Oklahoma City
Posts: 155
Thanks: 58
Thanked 17 Times in 14 Posts
Default

You should not get any voltage on a solar panel from only touching one lead (+ or -) to ground unless it's grounded somewhere. I do check this because I don't want there to be any voltage. If there is, I could get electrocuted when I have to work on my panels.

Some charge controller companies tell you specifically not to ground the panels. NEC also has exclusions for not grounding the negative lead but does ground the panel frames.

"From experience, testing voltage from one lead to ground shows a small initial voltage which quickly dissipates to 0. " This could be due to a small amount of static electricity or the VOM self calibrating.

Last edited by philb; 10-30-18 at 06:59 PM..
philb is offline   Reply With Quote
Old 11-02-18, 11:45 PM   #3
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,431
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

The momentary reading is indeed static electric charge. In every electric circuit, there exists a small amount of capacitance between the live circuit and everything else. When you probe the circuit, the measurement will not stabilize until the capacitance is discharged. A more sensitive (high impedance) instrument will take longer than a less sensitive instrument to drain the charge.

jeff5may is offline   Reply With Quote
Reply



Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 01:40 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design