EcoRenovator  

Go Back   EcoRenovator > Improvements > Renovations & New Construction
Advanced Search
 


Blog 60+ Home Energy Saving Tips Recent Posts


Reply
 
Thread Tools Display Modes
Old 03-19-17, 05:09 AM   #21
Fionn
Lurking Renovator
 
Join Date: Aug 2015
Location: Ireland
Posts: 25
Thanks: 3
Thanked 6 Times in 2 Posts
Default

Hi Toby, no problem.
150mm of PUR is just about minimum here to meet code.
You'll find that you'll probably end up in the same place in terms of minimum R value as us eventually, just takes years for things to change.
Also another point. If you ever intend to run the underfloor heating from a heat pump you want the tightest possible pipe spacing throughout - generally 100mm.
This improves the thermal transfer to the slab allowing you to run lower flow temperatures, which in turn increases the COP of your HP.

Fionn is offline   Reply With Quote
Old 03-21-17, 08:44 AM   #22
stevehull
Steve Hull
 
Join Date: Dec 2012
Location: hilly, tree covered Arcadia, OK USA
Posts: 826
Thanks: 241
Thanked 165 Times in 123 Posts
Default

Let's all recall that we are in vastly different climates with code (or rational engineering) being different in Ireland vs Oklahoma where I live.

In general, the further north toward the respective pole (north or south) you go, means that a thicker underconcrete foam layer is needed and has a quick return on investment.

In Oklahoma, our deep soil temp, which become the underslap temp, is about 60 F, whereas Ireland is likely some 20 degrees less.

Even here in Oklahoma, I would put in some subslab insulation, especially if I do the labor (which is minimal. But maybe only 1 inch - ~ 25 mm. But guess, what - code here does not even address subslab insulation.

I tip my hat to the Irish, with their colder soil temperatures, for insisting (code) on at least 150 mm subslab insulation. Not only does this save money, but the slab floor is just SO much more comfortable!


Steve
__________________
consulting on geothermal heating/cooling & rational energy use since 1990
stevehull is offline   Reply With Quote
Old 04-30-17, 11:07 PM   #23
buffalobillpatrick
Master EcoRenovator
 
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
Default

I'm building a new house in climate zone 5 dry.

Average air temperature here is 41*F (5*C) so that is also the 10' deep soil average temperature.

I'm using 6" of EPS type 2 under my radiant slab and running down the inside of my foundation stem walls.

180' 1/2" pex-A loops 7” OC using constant circulation with Grundfos Alpha pumps on low, with Erie BB3000 injection Outdoor Reset controller.

Thermostats are Tekmar PWM type, that learn, with slab sensors.

Last edited by buffalobillpatrick; 03-06-18 at 11:36 AM..
buffalobillpatrick is offline   Reply With Quote
Old 11-12-17, 04:53 AM   #24
asif22
Lurking Renovator
 
Join Date: Nov 2017
Location: punjab
Posts: 11
Thanks: 1
Thanked 0 Times in 0 Posts
Default

You also need spray for foam insulation,its mechanical systems that heat and cool buildings are continuously operating; reducing extreme temperature variations saves on the overuse of mechanical systems and leads to lower energy bills

asif22 is offline   Reply With Quote
Reply



Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 09:28 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design