Safety sealing switch contacts comes to mind here. Just like start/stop controls on industrial equipment of all sorts. Closely related to e-stop circuit. I'll look it up once i'm coherent and post a circuit.

jeff5may is offline   Reply With Quote
Old 03-02-16, 03:55 AM   #12
ronbo
Lurking Renovator
 
Join Date: Oct 2015
Location: Kansas City, MO USA
Posts: 3
Thanks: 0
Thanked 0 Times in 0 Posts
Default

Combining Grid Tie Inverters and Off-Grid Inverters apparently can work, but there are some basic rules from what I've gathered... as this has been an area of keen interest to me.

For starters, it's best to use an Off Grid Inverter (pure sine wave only!) that's of the "low frequency" design... they utilize large toroidal output transformers, and can better handle "odd" conditions... such as overloads.

Side note: a Low Freq. (LF) inverter can usually handle 5x its rated load for "short term overloads", whereas a High Freq. (HF) inverter (also called "transformerless") can only handle 2x overload at best.

USA specifics: ALL inverters involved should be 240V split-phase (no 120V), to balance the whole load/grid or pseudo-grid. I would consider this a "must".

The Off Grid Inverter should be rated for 5 times (or more) of the total of the Grid Tie Inverters, to keep the Off Grid Inverter stable. This over-rating makes sure the Off-Grid Inverter is able to protect itself... so to speak. If you want to use 1kW worth of grid-tie inverters, better consider at least a 5kW LF off grid inverter.

Grid Tie Inverters will try to push power into your "grid", whether it's real or pseudo. However they have limits... they will not (should not!) push more than the "allowable maximum AC line voltage"... if you're in the USA, that's normally 252V (twice 126V, which is 120V +5%). Before this point they are supposed to shut OFF as a safety measure. (though I've seen some that allow the full "maximum short-term peak Voltage" rating of 264V)

I can't see a condition where this would happen, unless there was a no-load condition on your "local grid"... therefore you should probably make sure there's always some load, even by plugging an AC operated battery charger to run the excess solar grid-tie-inverted power back into your off-grid battery bank.

With an AC Line-Load sensing switch, you could enable a relay to connect the battery charger AC power to a "pre-sense" position of your local-grid under low-load conditions. (to prevent the low-load sense circuit from sensing the battery charger AC load, and turning it right back off... it should only sense "low local-grid load" conditions on everything EXCEPT the battery charger... confused yet? hey... it's almost 4am, I'm allowed to ramble)


The US Standard for Utility Power is ANSI C84.1 - but it's never been strictly enforced from what I can tell.

powerqualityworld.com/2011/04/ansi-c84-1-voltage-ratings-60-hertz.html

powerstandards.com/tutorials/VoltageRegulation.php

I can't find it right now, but I recently watched a YT video of one gentleman who had a 3-5KW off-grid battery pure sine wave inverter (NO outside grid on at the time), connected to multiple solar grid-tie inverters, and when he switched his solar array ON, the output load on his battery-powered off-grid inverter slowly went down to less than 10 watts output, but was still providing the "local-grid" with the 60Hz sine wave to keep the grid-tie inverters synchronized and running. I'll keep looking and post it if I find it... but I found these in the search:

youtube watch?v=R9uK_mDFzmM

youtube watch?v=GzCRKawk-Ag


OR...

There's a product called PowerRouter that supposedly takes on all these functions... but is likely very expensive.

powerrouter.com/en/powerrouter/howitworks-2.html
ronbo is offline   Reply With Quote
Old 03-02-16, 04:44 AM   #13
ronbo
Lurking Renovator
 
Join Date: Oct 2015
Location: Kansas City, MO USA
Posts: 3
Thanks: 0
Thanked 0 Times in 0 Posts
Default

More to the point of the OP situ...

If it's a "normal" standby gas powered generator, it uses a normal magneto-inductive generator (alternator, to be exact) - which is just a small version of what power companies use... right?

There's nothing to "burn up", and as long as the grid-tie inverters are pushing slightly more AC voltage back "towards" the generator/alternator (and it will certainly be in-phase), it should do nothing but reduce the apparent load presented to the gas powered generator. It should see a "no load" condition, throttle back enough to maintain 60Hz output, and never know any difference.

However... some high-end standby generators are now utilizing variable speed, high efficiency alternators, which send their power through an electronic pure-sine-wave off-grid inverter - inside the standby generator itself. This allows them to perform SERIOUS throttle control, ignoring the gas engine RPM completely... such that it can essentially idle down, while still generating 60Hz "local grid" power - when the Mains-grid is offline.

These are an "unknown", because they are inverter-based... but it'd be cool to know the DC input voltage to the onboard inverter..... with a little work, it might be fairly simple to add Solar input to supplement the gas-powered generator.

Look up the Generac SYNERGY series.... and ECOGEN series of Alternative Energy compatible generators.

Youtube watch?v=q7doYZbqwmA
ronbo is offline   Reply With Quote
Old 03-02-16, 10:07 AM   #14
virginiajim
Lurking Renovator
 
Join Date: Sep 2010
Posts: 3
Thanks: 3
Thanked 0 Times in 0 Posts
Default

I have a problem with the PV attachment upstream of the transfer switch so it stays connected to the grid when the grid goes down. Doesn't this allow the PV's to feed (backfeed) the dead grid which energizes it and poses a problem for anyone working on it?
virginiajim is offline   Reply With Quote
Old 03-02-16, 10:06 PM   #15
where2
DIY Geek
 
Join Date: Apr 2013
Location: Sunny Florida
Posts: 401
Thanks: 74
Thanked 83 Times in 73 Posts
Default

Quote:
Originally Posted by virginiajim View Post
I have a problem with the PV attachment upstream of the transfer switch so it stays connected to the grid when the grid goes down. Doesn't this allow the PV's to feed (backfeed) the dead grid which energizes it and poses a problem for anyone working on it?
NO! If the inverter is attached to the "dead" grid side of the transfer switch, and the inverter is a grid-tie UL 1741 approved inverter, then the inverter will remain inactive until the grid comes back online and the grid STAYS online for a period of time. In the case of my Enphase microinverters, that period is ~5 minutes of stable 60hz with voltages inside a set range. If either the frequency, or the voltage goes out of range, the 5 minute timer resets and doesn't start counting down again until the out of range issue is resolved. UL 1741 approved inverters require NO human interaction to shut them down when the grid goes down. They shut down automatically in fractions of a second. It is sometimes referred to as "Anti-islanding". You can use your favorite search engine with the "UL 1741 and Anti-Islanding" to read about this feature.

where2 is offline   Reply With Quote
Reply


Tags
emergency generator, grid power, pv system


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 10:59 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design