Thanks Jeff! I'm going with 24VDC, just ordered it!
I found awesome news! People I'm talking with say that a 1-2 ton oil separator will work just fine on this build. So I ordered this beauty! Q E HVAC R Refrigeration Oil Separator 1 2" ODS New | eBay

Parts come in! First off is 20 on 316 stainless steel for the coil in the fish tank and 2 sizes of cap tube. (Might not need them for this build, but just wanted to be sure.)

Next is 5x SUD115 and 45% silver braze

And finally the 2 Inkbird Thermostat/relays


This build is going to have all the bells and whistles because I need to be able to really test it out to see if the 4 ton build will work as planned.

Attached Thumbnails
Click image for larger version

Name:	KIMG0194.jpg
Views:	1798
Size:	359.7 KB
ID:	5911   Click image for larger version

Name:	KIMG0195.jpg
Views:	1739
Size:	428.3 KB
ID:	5912   Click image for larger version

Name:	KIMG0196.jpg
Views:	1767
Size:	340.8 KB
ID:	5913  
MEMPHIS91 is offline   Reply With Quote
Old 09-23-15, 07:23 AM   #12
MEMPHIS91
Journeyman EcoRenovator
 
MEMPHIS91's Avatar
 
Join Date: Apr 2015
Location: Oxford, MS USA
Posts: 496
Thanks: 69
Thanked 87 Times in 61 Posts
Default

I found some interesting data on R600a. Looks like higher temps at lower pressure. I might shoot for a blend.

http://www.tecumseh.com/~/media/Nort...A-and-R290.pdf
MEMPHIS91 is offline   Reply With Quote
Old 09-24-15, 06:29 PM   #13
MEMPHIS91
Journeyman EcoRenovator
 
MEMPHIS91's Avatar
 
Join Date: Apr 2015
Location: Oxford, MS USA
Posts: 496
Thanks: 69
Thanked 87 Times in 61 Posts
Default

I reworked the fan and figured out the crazy chinese wiring.


The copper came in!


I ordered the cheapest I could find. So I was happy to see some really well made tubing.


Digging has been pushed til NEXT sunday.
Attached Thumbnails
Click image for larger version

Name:	KIMG0199.jpg
Views:	2274
Size:	359.6 KB
ID:	5935   Click image for larger version

Name:	KIMG0200.jpg
Views:	1764
Size:	377.4 KB
ID:	5936   Click image for larger version

Name:	KIMG0201.jpg
Views:	1761
Size:	345.0 KB
ID:	5937  
MEMPHIS91 is offline   Reply With Quote
Old 09-25-15, 06:26 AM   #14
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,431
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

I guess this means you're not using the OEM power supply or onboard relays to control the fan or compressor any more. Make sure to fuse everything correctly.

As to the r600 (butane) issue, it has a vapor pressure a little less than r134 or r12. At evaporator saturation temps below freezing water, your suction pressure is going to be near 0 psig. At seawater freezing temp, evaporator pressure is below atmosphere. I doubt your compressor could move enough mass to keep its motor cool.

Since your compressor is made for r410a, it needs to see a suction pressure in that range to keep cool within its operating envelope. Discharge pressure is not so much an issue as far as the compressor is concerned. All it really cares about is temperature.

What I would do is install some piercing valves on the stock unit and run it like they built it. Slap some gauges on it and log suction and discharge pressure for both sides. Choke the airflow on each side separately and observe pressure changes. Run the bad boy at all speeds and measure away. This will give you a detailed snapshot of the operating envelope it was designed to survive within.

After a decent approximation is made, you can blend propane and butane together to get a mixture that will satisfy your suction pressure range while giving you good discharge and condensation temperature. Raw high-side pressure will be lower than that of r410a, which in my mind is a good thing. Less pressure means less stress on everything.

Last edited by jeff5may; 09-25-15 at 07:03 AM.. Reason: more theoretical ramblimg
jeff5may is offline   Reply With Quote
Old 09-25-15, 09:41 PM   #15
MEMPHIS91
Journeyman EcoRenovator
 
MEMPHIS91's Avatar
 
Join Date: Apr 2015
Location: Oxford, MS USA
Posts: 496
Thanks: 69
Thanked 87 Times in 61 Posts
Default

Jeff, yes I have decided to not use the control board for the fan. I will be sure to have fuses where needed and everything on a gfci.

That is a very good point about the butane. I will be careful on how I use it, if any at all. This system is mainly for heating anyway.
Sadly the unit was out of 410a when I got it. The unit had fallen out of a window and on some trash below that busted a hole in the condenser.

When I charge I am going to do like I did with the water heater and charge by outlet temp, BUT I will keep a close eye to make sure the suction side is high enough to provide needed cooling, that is the main reason I went with 3/8 instead of 1/4. Thank you for that advise, changing the "perfect" blend only matters if the system works right.

As far as cooling the compressor goes, I plan to place it right before the condenser coils so the cooler air is drawn over it. I need to post the diagram soon, but for now MORE STUFF CAME IN!

A couple cheap temp sensors to constantly measure discharge and suction temp.

A few relays


The awesome and amazing QOS-12 Oil Separator!


And just for fun, a shot with the inspection camera down the inlet! The outlet looks the exact same way.


The building begins soon. I post some final diagrams and numbers soon as well.
Attached Thumbnails
Click image for larger version

Name:	KIMG0205.jpg
Views:	1526
Size:	377.8 KB
ID:	5945   Click image for larger version

Name:	KIMG0206.jpg
Views:	1508
Size:	341.7 KB
ID:	5946   Click image for larger version

Name:	KIMG0204.jpg
Views:	1654
Size:	319.9 KB
ID:	5947   Click image for larger version

Name:	KIMG0203.jpg
Views:	1451
Size:	293.8 KB
ID:	5948  
MEMPHIS91 is offline   Reply With Quote
Old 09-26-15, 11:34 AM   #16
marx290
Vapor Compression Goon
 
marx290's Avatar
 
Join Date: Mar 2013
Location: Portland, OR
Posts: 63
Thanks: 11
Thanked 22 Times in 11 Posts
Send a message via Yahoo to marx290
Default

Quote:
Originally Posted by MEMPHIS91 View Post
I found some interesting data on R600a. Looks like higher temps at lower pressure. I might shoot for a blend.

http://www.tecumseh.com/~/media/Nort...A-and-R290.pdf
Check out the ASHRAE series of books, especially the Fundamentals years. My early nineties copy, lists many properties of propane, butane, isobutane, and many others. They also have beautiful log(p)-h diagrams of each refrigerant saturation curve. Here is a a link to a pdf version. I'm not sure if it is still good, but I know there is one out there.

Ashrae Handbook Standards Download

Go to Abebooks.com for a hard copy. They make a lovely reference.
__________________

To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
marx290 is offline   Reply With Quote
Old 09-26-15, 11:46 AM   #17
marx290
Vapor Compression Goon
 
marx290's Avatar
 
Join Date: Mar 2013
Location: Portland, OR
Posts: 63
Thanks: 11
Thanked 22 Times in 11 Posts
Send a message via Yahoo to marx290
Default

Quote:
Originally Posted by jeff5may View Post
You can use a bullet strainer as an oil separator. Supco no. SUD 115 is the common one. Two Tubes facing up, single tube facing down. Bottom tube feeds long, small diameter cap tube back to suction line.
That is great! I wasn't sure if it would work. My best plan of attack for a oil return, was a sort of vortex separator on the discharge of the compressor, where oil would tend to fall to the bottom. A capillary tube would carry oil back to the compressor suction. I figure some sort of strainer would be advisable, in order to avoid plugging the capillary oil return line. I suspect that even a well designed system would compromise volumetric efficiency slightly, but would certainly be necessary for compressor health in some instances. Then again, keeping the heat exchanger walls cleared of oil, could improve thermal transfer too.

That's interesting. Thank you
__________________

To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
marx290 is offline   Reply With Quote
Old 09-26-15, 06:06 PM   #18
MEMPHIS91
Journeyman EcoRenovator
 
MEMPHIS91's Avatar
 
Join Date: Apr 2015
Location: Oxford, MS USA
Posts: 496
Thanks: 69
Thanked 87 Times in 61 Posts
Default

marx290, thanks for the links, the link was down, but I did find a google drive through that same site with a GOLD MINE of info.
https://drive.google.com/folderview?...DQ&usp=sharing

I am just now fully learning the P-H diagrams. I was always a try try try try til it fails then try try try again til it work kinda guy. But I am putting tons of research into this build. So I knew I needed to start with some basics of the math/science behind it all.
MEMPHIS91 is offline   Reply With Quote
Old 09-29-15, 06:19 PM   #19
MEMPHIS91
Journeyman EcoRenovator
 
MEMPHIS91's Avatar
 
Join Date: Apr 2015
Location: Oxford, MS USA
Posts: 496
Thanks: 69
Thanked 87 Times in 61 Posts
Default

Progress has been made!
So I started just loose fitting things. First the discharge on the compressor to the intake on the oil sep, not the best idea I know, see below. -1/2"-

And the discharge of the oil sep into the reversing valve -1/2"-
.
I knew the discharge from the compressor would have too much vibration to have a straight run to the oi sep, so I fixed it with a big loop.

The evap(now the condenser) had 2 cap tubes, so 2 intakes, I saved the cap tube and brazed some 1/4" onto them.

Then I ran the 1/2" from one side of the discharge of the reversing valve to the 2 1/4" intakes on the condenser.

The 2 1/4" tubes fit perfectly inside the 1/2". BEFORE

Brazed thoroughly. DURING

I was going to clean it up and take another picture, but I decided to move it into place first, and of course picked up the still super hot 1/2" line...... needless to say I am pecking with 2 fingers in between icing the burns in between typing...

Any way, next question, how much oil do I add and do I add it to the oil sep or the compressor? All to poe was drained. I have been looking for a while for the answer, still searching now.
Also I'm think 1/4" is to large for oil return. Would 1/8" be better?
Attached Thumbnails
Click image for larger version

Name:	KIMG0207.jpg
Views:	1844
Size:	389.3 KB
ID:	5965   Click image for larger version

Name:	KIMG0208.jpg
Views:	1848
Size:	373.0 KB
ID:	5966   Click image for larger version

Name:	KIMG0210.jpg
Views:	1828
Size:	331.9 KB
ID:	5967   Click image for larger version

Name:	KIMG0211.jpg
Views:	1853
Size:	349.5 KB
ID:	5968   Click image for larger version

Name:	KIMG0212.jpg
Views:	1804
Size:	357.0 KB
ID:	5969  

Click image for larger version

Name:	KIMG0213.jpg
Views:	1638
Size:	314.5 KB
ID:	5970   Click image for larger version

Name:	KIMG0214.jpg
Views:	1679
Size:	339.8 KB
ID:	5971  
MEMPHIS91 is offline   Reply With Quote
The Following User Says Thank You to MEMPHIS91 For This Useful Post:
jeff5may (02-21-16)
Old 10-02-15, 07:37 AM   #20
MEMPHIS91
Journeyman EcoRenovator
 
MEMPHIS91's Avatar
 
Join Date: Apr 2015
Location: Oxford, MS USA
Posts: 496
Thanks: 69
Thanked 87 Times in 61 Posts
Default

Howdy guys I got a lot more done thanks to the help of a GOOD friend.

First I swagged the 3/8" lines, its SO much easier than 1/4"


Then I laid out the line, brazed it all up, pulled a vaccum for several hours, made sure I had NO leaks, then zip tied about 20 bricks to the end that is going in the water.



Then the digging started, I got down to 9 feet deep in some places, but never less than 6 feet. When we got close to the pond the machine tried to slip and almost went for a swim, so I will have to dig about a 4 foot spot by hand.




I insulated 2 feet down as it came into the green house.

Attached Thumbnails
Click image for larger version

Name:	KIMG0216.jpg
Views:	1734
Size:	356.8 KB
ID:	5990   Click image for larger version

Name:	KIMG0217.jpg
Views:	1627
Size:	306.6 KB
ID:	5991   Click image for larger version

Name:	KIMG0219.jpg
Views:	1771
Size:	465.4 KB
ID:	5992   Click image for larger version

Name:	KIMG0220.jpg
Views:	1705
Size:	363.8 KB
ID:	5993   Click image for larger version

Name:	KIMG0221.jpg
Views:	1591
Size:	434.5 KB
ID:	5994  

Click image for larger version

Name:	KIMG0222.jpg
Views:	1631
Size:	387.8 KB
ID:	5995   Click image for larger version

Name:	KIMG0223.jpg
Views:	1660
Size:	391.9 KB
ID:	5996   Click image for larger version

Name:	KIMG0224.jpg
Views:	1636
Size:	425.9 KB
ID:	5997   Click image for larger version

Name:	KIMG0225.jpg
Views:	1711
Size:	334.9 KB
ID:	5998   Click image for larger version

Name:	KIMG0232.jpg
Views:	1580
Size:	327.6 KB
ID:	5999  

MEMPHIS91 is offline   Reply With Quote
Reply



Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 01:10 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design