02-19-15, 01:26 AM | #41 | |
It looks like you are handling the equation correctly, although I do believe that there is an exponentiation operator that is available to you.
Other than that, I must assume that you are using the floating point precision appropriate to this application. Multiple Polynomial Regression Analysis. Quote:
If the process you are trying to address, primarily functions in only part of that range, I can recalculate, for maximum fit over that specified range, which will give you much greater accuracy within that specified range but would be a less accurate fit in the rest of the range (that you will not use). BTW, I replicated the equation I gave to you, on a high-quality spreadsheet, without Arduino limitations, and got the very same results, when rounded. You did good. Best, -AC P.S.: if your input pressure variable was called "psi", and your calculated output temperature variable was called "degF", then your one-line formula would be: Code:
degF=-40.3085122205+(1.81496452942*psi)+(-0.0101201804003*psi^2)+(3.05234258195e-005*psi^3)+(-3.37963005786e-008*psi^4) Good luck! %%%%%%%%%
The Following User Says Thank You to AC_Hacker For This Useful Post: | buffalobillpatrick (02-19-15) |
02-19-15, 11:36 AM | #42 |
Thanks A/C
float degF=-40.3085122205+(1.81496452942*psi)+(-0.0101201804003*psi^2)+(3.05234258195e-005*psi^3)+(-3.37963005786e-008*psi^4); Nope, don't compile: sketch_subcool_3.ino: In function 'float calc_R290_Saturated_Temp(float)': sketch_subcool_3:214: error: invalid operands of types 'double' and 'int' to binary 'operator^' sketch_subcool_3:215: error: invalid operands of types 'double' and 'int' to binary 'operator^' sketch_subcool_3:215: error: invalid operands of types 'double' and 'int' to binary 'operator^' Code:
float calc_R290_Saturated_Temp(float psi) { double a = -4.03085122205E+001; double b = 1.81496452942E+000; double c = -1.01201804003E-002; double d = 3.05234258195E-005; double e = -3.37963005786E-008; return (a + (b * psi) + (c * psi*psi) + (d * psi*psi*psi) + (e * psi*psi*psi*psi)); } // end calc_R290_Saturated_Temp The above code generates exactly same object code as when data type float is used. Last edited by buffalobillpatrick; 02-19-15 at 12:09 PM.. |
02-19-15, 11:46 AM | #43 | |
BBP, if you are interested in pursuing this route, and want me to work on an equation for a more precise fit, for operating over a more limited range, let me know. -AC
02-19-15, 12:15 PM | #44 |
Thanks A/C
I'm only interested in 30-> 300PSI range if it won't be too much trouble. My table lookup method works accurately & only produces 2% more object code. |
02-19-15, 12:39 PM | #45 | |
Code:
MMF Model: y=(a*b+c*x^d)/(b+x^d) Coefficient Data: a = -6.63511955666E+001 b = 6.30623048298E+001 c = 7.72874234743E+002 d = 5.32503085812E-001 -AC
02-19-15, 12:52 PM | #46 |
A/C, Thanks
Works Damn great. At 30PSI results are -.07*F At 300PSI results are -.04*F Code:
float calc_R290_Saturated_Temp(float psi) { //MMF Model: y=(a*b+c*x^d)/(b+x^d) //Coefficient Data: float a = -6.63511955666E+001; float b = 6.30623048298E+001; float c = 7.72874234743E+002; float d = 5.32503085812E-001; float p; p = pow(psi,d); return (((a * b) + (c * p)) / (b + p )); } return (((a * b) + (c * p)) / (b + p ) + .05); //.05 is fudge factor Last edited by buffalobillpatrick; 02-19-15 at 01:39 PM.. |
02-19-15, 01:19 PM | #47 |
Glad I could help.
Best, -AC
02-19-15, 02:45 PM | #48 |
BBP,
Yeah, hit it pretty close. 1st column is P-T chart pressure 2nd column is P-T chart temperature 3rd column is calculated temperature 4th column is % change Best, -AC Code:
PSIG TempF TempF % change 30 7.93 7.86 0.887% 31 9.1 9.05 0.552% 32 10.26 10.22 0.408% 33 11.39 11.37 0.210% 34 12.51 12.49 0.124% 35 13.61 13.60 0.043% 36 14.7 14.70 0.028% 37 15.76 15.77 -0.066% 38 16.82 16.83 -0.051% 39 17.86 17.87 -0.061% 40 18.88 18.90 -0.095% 41 19.89 19.91 -0.102% 42 20.88 20.91 -0.136% 43 21.87 21.89 -0.105% 44 22.84 22.86 -0.107% 45 23.8 23.82 -0.097% 46 24.74 24.77 -0.119% 47 25.68 25.70 -0.092% 48 26.6 26.63 -0.100% 49 27.51 27.54 -0.103% 50 28.42 28.44 -0.067% 51 29.31 29.33 -0.066% 52 30.19 30.21 -0.064% 53 31.06 31.08 -0.063% 54 31.92 31.94 -0.063% 55 32.77 32.79 -0.064% 56 33.62 33.63 -0.039% 57 34.45 34.47 -0.047% 58 35.28 35.29 -0.030% 59 36.1 36.11 -0.018% 60 36.91 36.91 -0.012% 61 37.71 37.71 -0.011% 62 38.5 38.51 -0.016% 63 39.29 39.29 -0.001% 64 40.07 40.07 0.007% 65 40.84 40.84 0.008% 66 41.6 41.60 0.002% 67 42.36 42.35 0.013% 68 43.11 43.10 0.016% 69 43.86 43.85 0.034% 70 44.59 44.58 0.021% 75 48.19 48.17 0.051% 80 51.63 51.61 0.045% 85 54.95 54.92 0.059% 90 58.13 58.11 0.035% 95 61.23 61.19 0.061% 100 64.21 64.18 0.054% 105 67.1 67.06 0.053% 110 69.9 69.87 0.046% 115 72.62 72.59 0.041% 120 75.27 75.24 0.043% 125 77.84 77.81 0.032% 130 80.35 80.33 0.030% 135 82.79 82.77 0.019% 140 85.18 85.16 0.019% 145 87.51 87.50 0.014% 150 89.78 89.78 0.001% 155 92.01 92.01 0.000% 160 94.19 94.19 -0.004% 165 96.32 96.33 -0.012% 170 98.41 98.43 -0.017% 175 100.5 100.48 0.019% 180 102.5 102.49 0.005% 185 104.4 104.47 -0.068% 190 106.4 106.41 -0.011% 195 108.3 108.32 -0.015% 200 110.2 110.19 0.010% 205 112 112.03 -0.026% 210 113.8 113.84 -0.033% 215 115.6 115.62 -0.015% 220 117.3 117.37 -0.058% 225 119.1 119.09 0.008% 230 120.8 120.79 0.011% 235 122.4 122.46 -0.047% 240 124.1 124.10 -0.003% 245 125.7 125.72 -0.020% 250 127.3 127.32 -0.018% 255 128.9 128.90 0.001% 260 130.4 130.45 -0.040% 265 132 131.98 0.012% 270 133.5 133.50 0.003% 275 135 134.99 0.010% 280 136.5 136.46 0.030% 285 137.9 137.91 -0.009% 290 139.4 139.35 0.038% 295 140.8 140.76 0.026% 300 142.2 142.16 0.026%
The Following 2 Users Say Thank You to AC_Hacker For This Useful Post: |
02-19-15, 08:02 PM | #49 |
Thanks A/C for graph, I removed the fudge_factor after looking at it.