Default My HRV design

Hello Ecorenovators, I'm new to this forum and it's my first post.

I'm reading this forum for a while, was looking for ideas for my HRV project.
But finally ended up with my own design, as I'm a bit sceptical about using plastic for heat exchanger.
My inspiration for HRV is ecorenovator's forum, so I wanted to share with you what I came up with.
The heat exchanger is made from 0,5mm aluminium sheets, 1 meter x 0,33 meter. It's around 13 square meters of usefull surface area. Spacers between sheets are made from sheet rubber, 1 cm width, 4mm thick. One usually used for gaskets.
HRV housing is made from moisture resistant medium density fibreboard. Every inner corner is sealed with silicone.
In pictures you can see two white fans, it's simple, AC type, 70 W each, plastic housing fans with affordable price tag. I decided to mount them outside HRV housing as it is too big to fit inside.
As controls for unit I temporary use two speed regulators for fans and a simple timer. It turns on and off my HRV few times a day. As I said it's temporary, I really really wanted to test how my unit is performing.
And finally, performance. A few days ago it was -16 degrees C outside, and I got +8 degrees C air blowing into my living room and it the result AT FULL POWER. So, I'm quite happy. I'm planning to measure all four IN and OUT temperatures soon and calculate COP. If I only find a formula for it...
And I have a few questions for you guys.
How should I set the fans to work, a slight pressure or vacuum in house is better? As it's hard to make neutral.
I'm thinking in making some electronics with PWM and differential pressure sensor to control the fans work. But is it worth doing it? To have a moisture sensor in house would be nice too.













Attached Thumbnails
Click image for larger version

Name:	DSC00548.JPG
Views:	1298
Size:	313.8 KB
ID:	3916   Click image for larger version

Name:	DSC00549.JPG
Views:	1241
Size:	330.8 KB
ID:	3917   Click image for larger version

Name:	DSC00559.JPG
Views:	1286
Size:	323.6 KB
ID:	3918   Click image for larger version

Name:	DSC00612.JPG
Views:	1269
Size:	324.2 KB
ID:	3919   Click image for larger version

Name:	DSC00614.JPG
Views:	1295
Size:	313.1 KB
ID:	3920  

Click image for larger version

Name:	DSC00615.JPG
Views:	1269
Size:	280.5 KB
ID:	3921  

Last edited by Daox; 01-28-14 at 08:44 AM..
angstrom is offline   Reply With Quote
Old 01-28-14, 08:48 AM   #2
Daox
Administrator
 
Daox's Avatar
 
Join Date: Aug 2008
Location: Germantown, WI
Posts: 5,525
Thanks: 1,162
Thanked 374 Times in 305 Posts
Default

Welcome to the posting side of the site angstrom! Its great to see lurkers post.

That looks like a very nice design. I'm sure some of the guys will have some more tips for you.
__________________
Current project -
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.



To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
&
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
Daox is offline   Reply With Quote
Old 01-28-14, 08:48 AM   #3
mrd
Apprentice EcoRenovator
 
Join Date: Feb 2010
Location: Milford, DE
Posts: 106
Thanks: 5
Thanked 9 Times in 9 Posts
Default

With cold outdoor temperatures, a slight vacuum in the house is better. Your warm indoor air holds more moisture per volume, so if pressurized you'd have greater potential for in-wall condensation.

HRV performance figure calculations: Heat Recovery Efficiency

According to this, 0.5mm is about .020", 25 gauge. Are these sheets expensive? I've never priced aluminum sheet. How many layers do you have there?

From the photos, it appears to be a high quality build! Very nice work. I'm interested to hear your efficiency numbers.
mrd is offline   Reply With Quote
Old 01-29-14, 03:01 AM   #4
angstrom
Lurking Renovator
 
Join Date: Jan 2014
Location: Vilnius, Lithuania
Posts: 3
Thanks: 0
Thanked 0 Times in 0 Posts
Default

Yesterday I did some additional performance testing. And according to the calculation tool here is the results. At full fan power (fan specification says 700 m3/h) COP is 59%, at half power - COP 69%. So I happily left it running at half power...
This result satisfy my expectations, I only invested 1/4 of a factory-made HRV price
I think I could improve COP by somehow improving air distribution between each layer. I suspect that majority of air is traveling through middle part of the core. Maybe by adding air filter in the chamber where air enters core...
The cost for aluminium sheets was ~100 USD. From these sheets I got 40-45 layers seen in photos.
angstrom is offline   Reply With Quote
Old 01-29-14, 02:45 PM   #5
kostas
Helper EcoRenovator
 
Join Date: Dec 2012
Location: Venice, Italy
Posts: 89
Thanks: 15
Thanked 41 Times in 19 Posts
Default

Excellent work! I guess that at -16 degrees incoming air will almost certainly make some dew, have you placed a collecting plate?
kostas is offline   Reply With Quote
Old 01-29-14, 03:23 PM   #6
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 724 Times in 534 Posts
Default

Good job, good photos, respectable efficiency.

It looks like your HRV is counter flow... it's a little hard to tell from the photos. Is counterflow correct?

Where I live, the moisture is pretty high and condensation is always a problem.

Are you running into any condensation problems?

Great post.

-AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
Old 01-30-14, 03:41 AM   #7
angstrom
Lurking Renovator
 
Join Date: Jan 2014
Location: Vilnius, Lithuania
Posts: 3
Thanks: 0
Thanked 0 Times in 0 Posts
Default

My HRV is counter-flow. Only because this type of HRV tend to be more efficient.

In core, fresh air is coming from one end, "polluted" air is coming from another, so I think it's right.

Sure there is some condensation, you can see it in photo, but I simply drilled 2 mm hole for drainage. It doesn't have any effect on performance.


Attached Thumbnails
Click image for larger version

Name:	Untitled.jpg
Views:	1129
Size:	123.0 KB
ID:	3928  

Last edited by Daox; 01-30-14 at 10:00 AM..
angstrom is offline   Reply With Quote
Reply


Tags
diy hrv


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 02:38 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design