EcoRenovator  

Go Back   EcoRenovator > Improvements > Geothermal & Heat Pumps
Advanced Search
 


Blog 60+ Home Energy Saving Tips Recent Posts


Reply
 
Thread Tools Display Modes
Old 03-24-13, 10:41 PM   #1421
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 724 Times in 534 Posts
Default What do you want to use your home made heat pump for?

Quote:
Originally Posted by cbearden View Post
AC, I just wanted to take the time to say thank you for all of your hard work and being willing to put all this incredible info on here for so many people to benefit from...
Music to my ears!

Thank you, and welcome to a very interesting world.

There are a growing number of people here with experience to share. We all want to see you stay safe and to succeed.

If there's anything you're not clear on, don't hesitate to ask. There are enough of us here that you'll be sure to get an answer in quick order.

The Manifesto thrives on good photos and descriptions, so keep your camera close by while you're working.

I'm familiar with that dehumidifier, too. What do you want to use your home made heat pump for? Do you want water-in-water-out? Do you want Air-in-Air-out? This could influence how you disassemble your dehumidifier.

By the way, don't be too hasty about chucking out the controller and the sensor that goes with it. They might be usable later, either whole or for parts.

When the refrigerant compressor runs it needs lubricant and it needs cooling. The compressor gets it's lubrication from the oil/refrigerant mix that is circulating. It gets it's cooling from the refrigerant & oil that is returning from the evaporator HX.

If your refrigerant circuit is intact and still pressurized (no leaks), it will not harm your compressor to run it as you have described. But, the compressor depends on the circulation of lubricant which is mixed in with the refrigerant, to be able to continue safely running for longer than a few seconds. It need the cooling of the evaporator to be able to run more than several minutes.

Best,

-AC

__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...

Last edited by AC_Hacker; 03-24-13 at 10:49 PM..
AC_Hacker is offline   Reply With Quote
Old 03-24-13, 11:08 PM   #1422
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 724 Times in 534 Posts
Default

Quote:
Originally Posted by cbearden View Post
...I was also curious why there are multiple cap tubes involved here...
I have noticed multiple cap tubes on medium to large sized units. I have some 1/4 Ton units and they have single cap tubes. I have some that are around 1/2 Ton and they have two. I had an evaporator unit in the back yard that was 3 Ton and it had several. I think it is done for efficiency.

If you're going to try to reuse your cap tubes, you could choose to build two smaller HXs with a cap tube for each one. Or you might try to braze up some kind of two-into-one manifold. Most of the more experienced HVAC guys seem to prefer using a TXV metering device.

I used a cap tube on my #1 proof of concept machine and it worked great and I learned a lot from the experience.

I bought a TXV, for my first experience with TXV, to use in my next machine (ASHP air-in-water-out) that will be used for hydronic floors.

-AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
Old 03-25-13, 07:01 AM   #1423
cbearden
Helper EcoRenovator
 
Join Date: Aug 2011
Location: AR
Posts: 39
Thanks: 11
Thanked 4 Times in 2 Posts
Default

I'm planning to use this unit for water-to-water, as you've described in your first machine. my plan is to hook one side into my hydronic floor and the other side into either solar panels or loops in ground. Both the solar panels and the loops in the ground I plan on building later on. Since I can't be on-site much during construction, and we've had a lot of rain lately, I'm working on this particular part of it for now.
I'm still looking around for other donors to use for this project, in case this one doesn't work out. I have a larger 230v 18000 btu unit that someone gave to me and doesn't work. I haven't dug into it as of yet. but from reading your previous posts on here, I was trying to use something smaller to learn/test this initially.
the hydronic floor part of our house is about 1000 sq ft.
it's a 2-story house, but I only have this in the first floor.
I've calculated the heat load of my entire house to be in the area of around 18000-22000 btu, with the added insulation we'll be installing.
cbearden is offline   Reply With Quote
Old 03-25-13, 07:08 AM   #1424
cbearden
Helper EcoRenovator
 
Join Date: Aug 2011
Location: AR
Posts: 39
Thanks: 11
Thanked 4 Times in 2 Posts
Default

And thanks for the encouragement! I was wondering if the 2-cap tubes were for efficiency. def planning on using the cap tubes as it is in this system for now, at least until I learn more about how all of this works. I think your idea of the TXV is interesting, but I'm trying to take this one step at a time.
I have a small microcontroller called a Rasperry Pi, that I'll be using to monitor and control as much of my system as I can. For $35, it's pretty impressive what all it can do.
So far, I can hook up as many 1820 temp sensors as I want into a network of temp sensors, accessed all from a single data line. This will all be translated into a web page that I can surf to on this same microcontroller box. I'll also be using this to control one of the relays from this old control board off the humidifier that will switch the compressor on and off. And I'll still have more i/o room on this to control my water pump for my hydronic floor, the water pump for my water storage heat tank, and the water pump for my solar panels.
cbearden is offline   Reply With Quote
Old 03-25-13, 10:54 AM   #1425
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 724 Times in 534 Posts
Default

Quote:
Originally Posted by cbearden View Post
I'm planning to use this unit for water-to-water, as you've described in your first machine. my plan is to hook one side into my hydronic floor and the other side into either solar panels or loops in ground. Both the solar panels and the loops in the ground I plan on building later on.
This all sounds just great!

The solar idea is good. At some point you'll need to do a site analysis to see how much solar energy you can realistically expect during the heating season. Also you might need to decide if you want your solar to play a primary part in meeting your heating requirements and have the GSHP fill in the rest, or the other way around. Keep in mind that solar temperatures can get very high, so high that it could have a disruptive effect on your heat pump if used directly, but if the temperatures were moderated by a very large heat storage system (using the earth or a very large tank of water or massive concrete slab), you could make it work.

Quote:
Originally Posted by cbearden View Post
...reading your previous posts on here, I was trying to use something smaller to learn/test this initially.
Yes, that's the best way to go...

Quote:
Originally Posted by cbearden View Post
the hydronic floor part of our house is about 1000 sq ft. it's a 2-story house, but I only have this in the first floor.
I've calculated the heat load of my entire house to be in the area of around 18000-22000 btu, with the added insulation we'll be installing.
18000-22000 btu...

Well, let's look at the specs you posted on your de-humidifier:

Cooling Capacity - 7250 BTU/hr (2125 Watts)
Motor Input - 671 watts
COP - 3.16

Looking just at the motor input of 671 watts. and the COP of 3.16, we can do a rough calculation of what the output might be:

671 * 3.16 = 2,120.36 watts

Since 1 watt = 3.412 BTUs,

2120.36 * 3.412 = 7,235 BTU, which roughly corresponds to the output stated on the label.

The heating requirements you supplied were 18000-22000 btu

So your experimental project could supply...

(7,235/18000) * 100 = 40%

(7,235/22000) * 100 = 33%

...between 33% and 40% of your maximum heating needs.

As you can see, your experiment could not only be a learning experience, but also a very significant contribution to your heating needs. You are on the right track.

But don't make this whole thing too 'precious'. You are learning, you will make mistakes and might destroy your unit in the process (hopefully learning all the while). NOT A PROBLEM. I just wanted to do some calcs for you so that you had some idea of the potential you are working with.

Quote:
Originally Posted by cbearden View Post
...I have a larger 230v 18000 btu unit that someone gave to me and doesn't work. I haven't dug into it as of yet...
This could be the donor for your final heat pump.

But I think a more interesting way to go would be to build two smaller heat pumps that together would supply somewhat less than your total heat needs.

So if you could locate a 1-Ton unit, it could supply about 12,000 BTU of your needs, and a unit like the one you have could supply 7,235 BTU...

Total = (7,235 + 12,000) = 19,235 BTU

You could run them as needed, first the smaller one in the beginning of the heating season, then switch to the larger one as weather got colder, then run them both in the coldest part of the season, and finally add some axillary heat on the days when the extreme weather days were upon you.

Your micro-controller could switch the units in and out as required.

But the success of this whole scheme will depend on the accuracy of your heat load analysis.

I know that it is easy to get carried away with over-estimating the effects of future projects, so it is very important that you are realistic with your heating needs analysis, because the success of the heat pump(s) you build will be determined by by the load. And much more to the point, your earth work, the extent of your loop field which is a BIG DEAL will depend on your heating analysis.

Best,

-AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...

Last edited by AC_Hacker; 03-25-13 at 11:01 AM..
AC_Hacker is offline   Reply With Quote
The Following User Says Thank You to AC_Hacker For This Useful Post:
cbearden (03-25-13)
Old 03-25-13, 12:15 PM   #1426
cbearden
Helper EcoRenovator
 
Join Date: Aug 2011
Location: AR
Posts: 39
Thanks: 11
Thanked 4 Times in 2 Posts
Default

That's an interesting analysis.
My watt meter only measured 330-430 watts when the compressor was running for a few minutes. I noticed that it gradually increased the watts reading the longer I had it on. Granted, I only kept it on for maybe 4-5 minutes.


Also, the heat load figures I had for my house were for the entire house, both floors. My hydronic flooring is only going to be on the first floor, roughly 1000 sq ft of space. I know that whatever heat is generated from the floor will slowly rise to the ceiling and possibly up to the 2nd floor. And I'm not sure yet what kind of insulation (if any) will be in-between our two floors. I think they are planning on installing the duct-work for our normal air heat-pumps.
(everything I'm building is completely separate and aside from the normal heating/cooling they are building on my house. I'm simply trying my best to augment or replace some of that usage with energy to/from the ground and/or to/from the sun.)
That being said, wouldn't my heating load need to be done on just the 1st floor only? Or am I making too many assumptions about how the heat will travel/act on the 1st floor and how long it will stay there?
I reran the heatload calc online using just my 1st floor, but changing my ceiling insulation from R38 to R10. This is a rough estimation, I know, but I needed to put something in there.
I started with about 22000 before I made these changes.
I'm getting about 15000 Btu/hr. with just one floor.
And if I take away ceiling loses since it's not exposed to outside temps,
I get about 11000 Bu/hr.

Comments? Anyone throwing tomatoes or eggs at me over this??
haha.
cbearden is offline   Reply With Quote
Old 03-25-13, 12:42 PM   #1427
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 724 Times in 534 Posts
Default

Quote:
Originally Posted by cbearden View Post
...wouldn't my heating load need to be done on just the 1st floor only? Or am I making too many assumptions about how the heat will travel/act on the 1st floor and how long it will stay there?
I've been heating only my downstairs living room, and keeping the doors closed to the other rooms, but I have been temperature monitoring all the rooms. So heat from your 1st floor room will go up to the second level, even with the doors closed... The will not be as warm, but they will not be as cold as if your house was not heated at all.

There's something called Exergy Analysis, where the path of heat is examined as it makes it's way to the great heatsink in the sky. The intent of the analysis is to attempt to find ways to use the lower temperature heat, also.

So my bedroom is on the second floor, and I don't heat it unless I'm doing some extended work there. At night, I warm the bed with an electric blanket before I get in, then I turn it off. But the heat from down stairs will warm the upper rooms to some extent.

-AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
Old 03-25-13, 03:22 PM   #1428
randen
Uber EcoRenovator
 
Join Date: Apr 2011
Location: Strathroy Ontario Canada
Posts: 657
Thanks: 9
Thanked 191 Times in 129 Posts
Default Heating second floor with Hydronic first floor

CBearden

Your going in the right direction. I know from experience that it can be difficult to get good information. Alot have read about it. "It should work"

Yes indeed the heat will radiate to the second floor. Our first floor heated concrete slab warms the second floor no problem. BUT for air-conditioning you will need ducts in the second floor to allow the cold dense air to fall to the lower. If at all you will need a little blast of heat to the second floor you can get a little blast up there with the air-conditioning ducts. But I doubt you will ever require heat to be forced up to the second floor by what we experience here. For sure air con.

Insulation between the first & second floor totally not nessisary. Put that insulation in the second floor ceiling/roof. Min. code maybe R38 but R50-60 would really be the best investment. The greatest heat loss is through the roof.

If you have good sun fraction for your location the solar hot water can be a large portion of you heating load. But you require close to 30% of panel vs. floor area. And you can DIY. It will work.

Yes you can hack your own heat-pump it will work and work well but:: numerous units with seperate HX or to add up to the total load for each zone could get expensive. Brazed plate heat-exchangers are not cheap. One unit sized correctly or just slightly smaller as AC Hacker had mentioned for your total load would be the ticket.

Randen
Attached Thumbnails
Click image for larger version

Name:	install1.jpg
Views:	1052
Size:	62.5 KB
ID:	3099  
randen is offline   Reply With Quote
Old 03-25-13, 03:30 PM   #1429
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,431
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default Solar Insolation Lookup

Quote:
Originally Posted by AC_Hacker View Post
The solar idea is good. At some point you'll need to do a site analysis to see how much solar energy you can realistically expect during the heating season... And much more to the point, your earth work, the extent of your loop field which is a BIG DEAL will depend on your heating analysis.

Best,

-AC
I found a lookup tool that realistically finds your annual insolation by location:
Annual Insolation (U.S.)
This value is very accurate, using factual data all the way back to 1961. It measures insolation per square meter assuming zero shade. For hobby purposes, a 4 x 8 sheet of plywood has very close to 3 square meters of surface area.

another page has a chart of monthly insolation, but with fewer lookup points:
Solar Insolation Levels - Apricus Solar Water Heater

Happy hunting!
jeff5may is offline   Reply With Quote
Old 03-25-13, 03:55 PM   #1430
randen
Uber EcoRenovator
 
Join Date: Apr 2011
Location: Strathroy Ontario Canada
Posts: 657
Thanks: 9
Thanked 191 Times in 129 Posts
Default Heating second floor with Hydronic first floor

CBearden

Your going in the right direction. I know from experience that it can be difficult to get good information. Alot have read about it. "It should work"

Yes indeed the heat will radiate to the second floor. Our first floor heated concrete slab warms the second floor no problem. BUT for air-conditioning you will need ducts in the second floor to allow the cold dense air to fall to the lower. If at all, you should need a little blast of heat to the second floor you can get a little blast up there with the air-conditioning ducts. But I doubt you will ever require heat to be forced up to the second floor by what we experience here. But for sure air con.

Insulation between the first & second floor totally not nessisary. Put that additional insulation in the second floor ceiling/roof. Min. code maybe R38 but R50-60 would really be the best investment. The greatest heat loss is through the roof.

If you have good sun fraction for your location the solar hot water can be a large portion of you heating load. But as mentioned earlier you require close to 30% of panel vs. floor area. And you can DIY. It will work. This season for us so far for solar fraction has been very poor as we ve had no sun but in the past its been an amazing asset.

Yes you can hack your own heat-pump it will work and work well but:: numerous units with seperate HX or to add up to the total load for each zone could get expensive. Brazed plate heat-exchangers are not cheap. One unit sized correctly or just slightly smaller as AC Hacker had mentioned for your total load would be the ticket.

For our installation I was a control freak, each zone is on its own control. (temperature sense of slab) {1700 sq ft of slab}Un-nessisary with the exception of the attached garage. All the zones are set the same so one t-stat could have been fine. The slab heating is sooo uniform seperate controls are over kill. But since you have it better more control than not enough. The outside temp. sense is a good idea for the slow response for the slab but it will still take about 2 hrs for a 1 deg C change in slab temp.

We have had so many compliments on our heated floors from visitors we are very pleased.

My appologies guys, should have been in In-floor heating thread.

Randen

randen is offline   Reply With Quote
Reply


Tags
air conditioner, diy, gshp, heat pump, homemade


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments