Heat pump water heater modification.
Hi I have a GE geothermal heat pump water heater. I'm hooking up a water / freon heat exchanger to it. I'll be installing it in between the expansion valve and the evaporator. I noticed that the freon feeds into the evaporator at the bottom and exits out the top. Does anybody know if it matters if I mount the heat exchanger above or below the evaporator inlet line , and if it matters if the freon is fed into the top or bottom of the heat exchanger?
Thanks |
12-08-12, 06:50 PM | #2 |
Master EcoRenovator
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
|
Liquid should enter at the bottom as it becomes a vapour and you want to have a high quality vapour exiting without any liquid drops. I think it best to have the evap equal to or higher than comp but it may not be that critical.
|
12-30-12, 01:33 PM | #3 |
Administrator
Join Date: Aug 2008
Location: Germantown, WI
Posts: 5,525
Thanks: 1,162
Thanked 374 Times in 305 Posts
|
Any updates on this project Mark? Did it work out?
__________________
Current project - To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts. To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts. & To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts. |
|
|