Mikesolar,
This low temperature floor heating information is really great in many respects. Since it is wandering a bit off topic for a Dual compressor heat pump thread, but is especially relevant information for the DIY Hydronic Floor Heating thread, perhaps you could copy your response to THIS LOCATION. Quote:
Quote:
I must admit that I have never heard of an outdoor reset mixing valve before. I just googled the term and came up with THIS USEFUL PDF DOCUMENT. It would be very helpful if youu could go into a little more detail regarding the rationale and function of this type of valve. Quote:
I certainly see the reason behind why such close spacing is being used, my questions here, regard gaining a full understanding of how it is being done, specifically:
Lastly, it is very interesting that you are living in Toronto, where your average Heating Degree Days (F) = 7223 (assuming a base temperature of 68 degrees F) or Heating Degree Days (C) = 4010 (assuming a base temperature of 68 degrees C), that folks are successfully using ASHPs. Many of our readers live in HDD-challenged areas and have a great interest in ASHPs. Best, -AC_Hacker * * *
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker... |
|||
09-07-12, 08:22 PM | #272 |
Master EcoRenovator
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
|
I have bought a couple of those Taco valves but I don't like them. The orifice is so small that I could not run 5 loops of pex without the pump cavitating. The Cv is way too low. I changed them for some honeywell valves that give a much better performance. The point of the mixing valve is to reduce the temp swings in the floor that can come with using room stats. The lag is just too long.
About COP....Anyone can make a HP and claim a COP of 6, but at what conditions? Air temp of 10C and liquid temp of 25C? sure that is easy. Try air of -15C and liquid of 40C (the most you should ever need for floor heating). That is why SCOP is much better or at least state the output at various conditions so people can compare. I have a bias towards concrete and gypcrete. I have used heat emission plates but I believe the best LONG TERM performance and longevity uses lots of thermal mass. Yes, it doesn't respond as quickly but why should it? I also don't have more than one t-stat per floor unless there is a zone with very different heat needs. The 4" spacing still has a 6-8" loop at the end....oh well. The HPs we build do have electric elements for backup but we also have good off peak electrical pricing which is half of the peak price so I can build up heat in the slab at night to radiate out during the day, if I wanted to. Last edited by Mikesolar; 09-07-12 at 08:25 PM.. |
09-07-12, 08:42 PM | #273 | |
Supreme EcoRenovator
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 724 Times in 534 Posts
|
Quote:
How do you get your European radiant floor information? Are there blogs that you know of where this sort of thing is being discussed? Books? Web sites? -AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker... |
|
09-07-12, 08:54 PM | #274 | |
Master EcoRenovator
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
|
Quote:
Now, with solar and heat pumps, spacing becomes much more important. There is a lot more time through the heating season when you can get 30C from solar vs 40C so if your system is set up for 30C.........immediate benefit. With HPs it is all about the temp spread. The smaller the better. I will have to look at the books to see what the numbers say about 4" spacing as i haven't looked at them in a few years. |
|
09-08-12, 12:31 PM | #275 |
Supreme EcoRenovator
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 724 Times in 534 Posts
|
Thanks...
I guess I'm looking for more information regarding the bleeding edge of low-temperature heating. I spent some time with a Watts Radiant computer program and that was quite informative. I learned, as you have, that closer spacing makes lower temperatures possible. I also learned that at the bleeding edge, higher flow rates are required, which imply more attention to optimum tube sizing, optimum tubing length, and also pump optimization. I also learned that the computer tool did not allow spaces closer than 6". It was kind of like coming to the edge of the earth... So, the above approaches are not included in common practices in the US, as you said, 8" and 12" spacings have become the standard. But I'm not very interested in the standard, I'm much more interested in what exists beyond the standard. If you think about how long a radiant floor might last, and then consider this chart: ...here we see that the per gallon price of #2 heating oil went from about $0.65 per gallon in Jan 02 to about $3.15 in Jan 12 (as of today, the national average is $3.97). Would the rule of thumb from 2002, that close tube spacing were not worth the trouble when using a condensing boiler (15% greater efficiency, on average) still hold up when energy prices increase, as they have by 385%? So, you've been in the trade a while, when do you think that energy prices will come back down, and stay down? Or do you think that they will continue to rise like they have on the chart, hitting $10 per gallon around 2040? I'm in the camp that believes that energy prices will continue to go up, at an even faster rate, and that now is the very best time to prepare for a chilly future. It seems to me that too many folks in the US are asleep to the situation, and that folks in Europe understand and are engaging in appropriate upgrades to their homes & businesses. That's why I am so interested in finding out how Europeans are approaching radiant heating. BTW, you didn't explain the rationale behind using the outdoor reset mixing valve, you just said you didn't like the Taco... -AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker... Last edited by AC_Hacker; 09-08-12 at 05:22 PM.. |
09-15-12, 11:45 AM | #276 | |
Master EcoRenovator
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
|
Quote:
Look at the a graph of air temp vs time with an on off system. There is a lot of wasted gas or power just getting the heating source going so we will have a lot of peaks and valleys. If we are able to use a modulating boiler we can even out the curve easily and if that curve is based on a outdoor temp, we can adjust it further. Flat line indoor temp is the goal and gradual changes to water temps are desired. High HP is needed for starting but you only need 25% of that power for cruising. I have no idea where fuel rates will go and I never anticipated fracking. Technology changes have allowed horizontal drilling so peak oil production seems to have been pushed back a few years. Cheap gas is one of the few things that will allow us to get rid of coal for power production but with oil, I know it will go up, I just don't know by how much. Last edited by Mikesolar; 09-15-12 at 11:50 AM.. |
|
09-16-12, 01:46 AM | #277 | |
Apprentice EcoRenovator
Join Date: Aug 2010
Location: Windsor ON Canada
Posts: 229
Thanks: 4
Thanked 30 Times in 22 Posts
|
Quote:
I used taco 2 way outdoor reset valve and I love it. It works like thermostat in my system. The only difference it takes to account outdoor temperature and not indoor like thermostat. It is easily adjustable. http://ecorenovator.org/forum/21536-post204.html Check eBay for better pricing. I paid for my 200+ You have to follow instructions when it comes to plumbing this valve. You have to have bypass otherwise when it closes your pump will have a hard time to pump nothing Last edited by Vlad; 09-16-12 at 01:54 AM.. |
|
09-16-12, 02:07 AM | #278 | ||
Apprentice EcoRenovator
Join Date: Aug 2010
Location: Windsor ON Canada
Posts: 229
Thanks: 4
Thanked 30 Times in 22 Posts
|
Quote:
Quote:
Last edited by Vlad; 09-16-12 at 02:10 AM.. |
||
09-16-12, 06:16 AM | #279 |
Master EcoRenovator
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
|
I've been using reset mixing valves for almost 25 years. Until recently package ones were only available from Viessmann, called the Dekamatic HK1, or from Tekmar, who makes the control for Taco IIRC. (Honeywell may make a couple but they were not very popular here)
The Viessmann product is good because it comes in either a 3 way or a 4 way valve with a high Cv (high flow). We used 4 way valves before condensing boilers came along to provide low temp protection to cast iron or steel boilers when we used radiant floors. Dekamatik-HK1-ii.pdf Vlad, the 4 way incorporates the bypass and gives better return temp control. In the 3-way the hot goes directly into the valve and some of the return from the floor brings down the hot to floor temps. The rest goes back to the boiler. The output of the valve MUST be able to take the full flow needed by the loops without too much pressure drop and every situation is different. To me, just looking at the valve and its tiny port is a cause for concern as i believe it is fine for doing a few loops but not for a whole house. |
09-16-12, 04:17 PM | #280 | |
Apprentice EcoRenovator
Join Date: Aug 2010
Location: Windsor ON Canada
Posts: 229
Thanks: 4
Thanked 30 Times in 22 Posts
|
Quote:
http://ecorenovator.org/forum/renova...html#post21533 I have 10 zones and 10 loops and have never had a noise or vibration or anything else from pump. When outside is warm 2 way taco valve is mostly closed and water circulates through bypass which is basically return.... I did added this valve in return/bypass to create pressure difference: https://www.pexuniverse.com/store/pr...***-valve-3196 |
|