01-18-15, 08:16 AM | #11 |
Apprentice EcoRenovator
Join Date: Nov 2013
Location: Moore Oklahoma
Posts: 267
Thanks: 108
Thanked 23 Times in 21 Posts
|
I had to run a new flue when I upgrade my furance to a 90% model. The combined 4" flue never did draft properly with just the WH pilot light. Replaced with 3" flue and it drafts properly now.
|
01-19-15, 05:53 PM | #12 |
Less usage=Cheaper bills
Join Date: Nov 2010
Location: Minneapolis, MN
Posts: 940
Thanks: 41
Thanked 117 Times in 91 Posts
|
You say you have negative pressure because of the building code but don't have the required duct going into the vicinity of where a combustion burning appliance exists to break the negative pressure?
|
01-19-15, 08:31 PM | #13 |
Apprentice EcoRenovator
Join Date: Feb 2011
Location: Canada
Posts: 109
Thanks: 13
Thanked 13 Times in 11 Posts
|
I do have a fresh air inlet duct that leads into the boiler room on the lower storey of the building. My house is over 30ft tall, and the chimney (exhaust ducting) doesn't get warm enough for the exhaust gas to rise up (updraft).
Q. |
01-19-15, 09:25 PM | #14 |
Supreme EcoRenovator
Join Date: Sep 2012
Location: Vancouver Island,Canada.
Posts: 1,037
Thanks: 116
Thanked 100 Times in 87 Posts
|
Service tech may of provided your fix , It is worth looking into to , there may be a mathematical formula to find out if a smaller diameter pipe would fix the venting. Seems they have formula for near everything to do with ducts and Hvac.
|
01-19-15, 10:37 PM | #15 |
Apprentice EcoRenovator
Join Date: Feb 2011
Location: Canada
Posts: 109
Thanks: 13
Thanked 13 Times in 11 Posts
|
good stuff! I shall consider what servicetech has RE: calculations.
@servicetech: please advise. Q. |
01-20-15, 05:33 AM | #16 |
Steve Hull
Join Date: Dec 2012
Location: hilly, tree covered Arcadia, OK USA
Posts: 826
Thanks: 241
Thanked 165 Times in 123 Posts
|
Just looked over some old notes and paradoxically insulating the exhaust duct has a significant effect on venting. Metal pipe cools off quickly and, once cool, does not support temperature dependent draft.
Interesting that many high efficient water heaters require PVC as the vent pipe. Inherent insulation in PVC? Steve
__________________
consulting on geothermal heating/cooling & rational energy use since 1990 |
01-20-15, 08:08 AM | #17 |
Supreme EcoRenovator
Join Date: Sep 2012
Location: Vancouver Island,Canada.
Posts: 1,037
Thanks: 116
Thanked 100 Times in 87 Posts
|
Also might look into shorting the run , more math I suspect.
|
01-20-15, 06:55 PM | #18 |
Less usage=Cheaper bills
Join Date: Nov 2010
Location: Minneapolis, MN
Posts: 940
Thanks: 41
Thanked 117 Times in 91 Posts
|
GAMA venting tables
http://0323c7c.netsolhost.com/docs/gama%20venting.pdf I'm not certified or licensed in handling gas appliances, but I figure the Gas Appliance Manufacturing Association and American Gas Association should have it right. ..I noticed the revision is from 1991 but I figure you would at least know if you are way oversized with the vent and would therefore possibly require a duct sleeve to be added. Also be sure you have double-wall B-vent pipe and not a single wall pipe. Hope this helps. |
01-21-15, 08:37 PM | #19 |
Apprentice EcoRenovator
Join Date: Feb 2011
Location: Canada
Posts: 109
Thanks: 13
Thanked 13 Times in 11 Posts
|
|
01-21-15, 09:00 PM | #20 |
Supreme EcoRenovator
Join Date: Sep 2012
Location: Vancouver Island,Canada.
Posts: 1,037
Thanks: 116
Thanked 100 Times in 87 Posts
|
Those elbows and reducers are ridiculous .. in my opinion it should of been connected with more care to air flow, elbows and reducers by their nature cause large amounts of restriction.
If it was piped by a *talented* person you would not see such a contraption of fittings. talented workers are far and few between , even when safety is a factor you often end up with monkeys doing the Job.. quote: Every PVC fitting has an airflow resistance that is approximately equal to the footage given in the table below. For example each 4" 90 degree sweep elbow adds the equivalent of 6 feet of straight pipe resistance while a 4" 90 degree sharp edged elbow adds 15 feet of equivalent straight pipe resistance Pipe size restriction 4 inch Reducer cause the the vent to perform as if it is 30 ft longer 6 inch reducer causes the pipe to perform as if it is 60 ft longer How to measure airflow in PVC piping requires careful measuring of airflow with a pitot tube or calibrtated anenometer to determine CFM |