Old 11-15-16, 06:37 AM   #39
IdleMind
Helper EcoRenovator
 
IdleMind's Avatar
 
Join Date: May 2016
Location: SE Wisconsin
Posts: 55
Thanks: 3
Thanked 14 Times in 10 Posts
Default

Ron-thanks for the tip on the temp logger, I have some old computers that could be dedicated to this project so I should look into that. For now, I have a system that works good for me. I read and enter the data in the order it appears on the spread sheet. I have a lookup table in the spreadsheet so the TofP1 & TofP2 cells are filled with a lookup function. Then the SH, SC, and delta P cells are auto calculated. The COPstep4 is also calculated and gives a rough indication of how efficiency varies with time and tank temperature.

The odd temp results have been a puzzle to me for a long time. For example look at the 20 min data. The gas going from compressor to condenser is 130F at 292psi with a saturation temp of 140F. Seems to indicate that it is already starting to condense. The 16 F SC tells me the that it has fully condensed to liquid when it exits the condenser so that that seems about right.

It is possible that a bigger fan would raise the temp into condenser above the saturation temp which might help.
IdleMind is offline   Reply With Quote
 



Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 11:12 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design