Quote:
Originally Posted by Exeric View Post
I've been thinking about this and I just don't think this is close to right. I think you are leaving out something big - voltage drop/foot per gauge of wire.
Also you have to multiply 60' x 2 = 120' for up and back total length of homerun wire times that resistance. Also, though I didn't say it, I intend to have no more than a 1% V drop from the 240volts = 2.4 V. Finally, my plan is to have 14 panels not 12, which I think I stated. The .9A x 1.25 is correct.
Standard design for voltage drop is 5% max, 3% in a branch circuit and 2% in a service. I have been doing solar systems for 25 years and never had a problem following these rules.

17 inverters on a 12g wire is fine, use a 20A breaker but as I had stated, IF you were to use 12 inverters, a 14/3 wire would be just fine over that length. 14 inverters is definitely a 12/3 wire. Of course if you want a 1% drop, it certainly doesn't hurt.
Mikesolar is offline   Reply With Quote
 



Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 02:43 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design