Old 02-27-11, 09:52 AM   #11
mrd
Apprentice EcoRenovator
 
Join Date: Feb 2010
Location: Milford, DE
Posts: 106
Thanks: 5
Thanked 9 Times in 9 Posts
Default

The units conversion is a little confusing. Let's try it this way, with known values to test:

R = t/k
R: Thermal resistance
t: thickness
k: thermal conductivity coefficient

This lists foamed plastic insulation with k=0.03

we are looking for R-value per inch, so t in meters = 1/39.37 = 0.0254
R = (0.0254 m)/(0.03 W/m*K) = 0.847 m^2*K/W

to convert this SI R-value to US R-value, we multiply by 5.682
0.847 x 5.682 = US R-value of 4.81/inch of foam plastic.
This appears correct. Now we just need some k-values of soil to calculate with.

The same page lists dry & wet soil with a range from 0.15 to 4. This is a huge range, dependent on soil moisture. Let's first check these values, in units of US R-value per foot.

thickness, t, of one foot in meters: t = 12/39.37 = 0.3048
R = t/k = (0.3048 m)/(0.15 W/mK) = 2.03 x 5.682 = 11.5 US R-value/ft, best case
R = t/k = (0.3048 m)/(4 W/mK) = 0.076 x 5.682 = 0.43 US R-value/ft, worst case

Can we narrow our range of likely k-values?

IEEE 442-1981, Guide for Soil Thermal Resistivity Measurements
See Figure 3 on page 9. The Y-axis is in units of degreeC*cm/W. We can convert to k-value = 100/y.

I'm going to select two values, 200 and 80.
k = 100/200 = 0.5
R = (0.3048 m)/(0.5 W/mK) = 0.61 x 5.682 = 3.47 US R-value per foot
k = 100/80 = 1.25
R = (0.3048 m)/(1.25 W/mK) = 0.24 x 5.682 = 1.36 US R-value per foot

Now if we look at data listed here, units of thermal conductivity in Figures 5 & 6 are in Btu/(hr ft F), the reciprocal will give us R-value per foot..
1/0.52 = 1.92 US-R/ft for loam
to 1/0.96 = 1.04 US-R/ft for saturated silt/clay
to 1/1.44 = 0.7 US-R/ft for saturated sand

Soil type & moisture will make or break it..


Last edited by mrd; 02-27-11 at 09:59 AM.. Reason: Fixed my calculations, again..
mrd is offline   Reply With Quote
 


Tags
diy, heat pump, hydronic, pex, radiant


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 02:46 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design