Old 12-11-10, 07:28 AM   #21
Default I'm acclimated!!!
It was chilly yesterday but got up to 25F about noon time.
Weather history here. Weather Station History : Weather Underground
And it's stayed around 25F for the last 20 hours. However, it was movie night in the den.
I wanted to be warm to watch the new version of "Clash of the Titans".
So, we had the free-flow on early in the evening to take the chill out..
Once the storage water temp dropped down a bit, after the movie, I ran the oil a little more.
We had 170deg F hotwater at 10PM and the burner was back in the timer..
It was in free flow at bed time. Big mistake. I woke up this morning at 04:30 and
it was about 68 in the bedroom. A bit too warm. Need 65-66 now that I'm acclimated.
I looked at the meter, in 4.5 hours we had only used about 2 kWh!
It's after 8AM now, and it's reading 3.55 kwh (for 8 hours=444w per hour).
So, using the house as a Dump-Load for the extra water heat saves some power during the night..
And can make it a bit too warm to sleep with a lot of covers..
The timer came on at 7:30 to 8:00 this morning and ran the temp up from 70F to 142F.
Which should be fine. And we might even get some extra BTUs from the
new 400w PV today.. It will at least help counteract the hourly losses.
I never thought that I would ever want to sleep in 66F room at night..
And I never would have guessed, I would ever consider 25f mild weather..
Old 12-11-10, 09:46 AM   #22
Could you perhaps not open the valve all the way so the heat release is slower?
Old 12-11-10, 12:26 PM   #23
Yeah, you're right. That small piece of tape in the photo says "4.5 turns".
But, that's a really slow flow. Of course I was in a hurry and cranked it up about 8 turns..
I'll have to see if 4.75 turns gives us a happy medium..
Old 12-12-10, 08:18 PM   #24
collector
You may find this interesting:
(I copied and pasted as I could not post a link.)
Bottom Line: Yes, it saves energy, but not a huge amount.
Suppose you go on vacation one Saturday morning and return on Sunday evening a week later, which means you are away for a total of 8.5 days. Should you turn the water heater off or not? In reasoning this through I will use an electric water heater, but the same results apply to a water heater that runs on natural gas or propane. By the way, "turning off" an electric water heater generally means throwing the circuit breaker.
The easiest way to reason through this problem is to look at the cumulative heat lost in both cases. All the heat that was lost must be replaced by the electric resistance heater inside the tank.
Leave the Water Heater On:
If you leave the water heater on then the heating element cycles on and off occasionally to replace heat lost through the insulation.
The below graphic shows the rate of heat loss in btu/hr over 8.5 days for our 80 gallon R-16 hot water tank assuming the tank is left on. Because the thermostat in the water heater is keeping the water temperature roughly at a constant, then the rate of heat loss is constant over the entire 8.5 days. In the Hot Water Tank Heat Loss web page I computed this loss to be about 141 btu/hr.
Water Heater Loss When On
The "area under the curve" of this graph gives the total heat lost in btus over the 8.5 days. The calculation for total btu loss is:
BTU Loss on vacation = 141 btu/hr x 8.5 days x 24hr/day
= 28,764 btu
The only way to replace lost heat is by turning on the electric resistance heating element, so all of these btus are supplied by electricity. Divide the btus by 3,412 btu/kwh in order to convert the btu loss to kwh supplied by the electric company:
kwh supplied = 28,764 btu / (3,412 btu/kwh)
= 8.43 kwh
Multiply by $0.10/kwh to find the cost of replacing the lost heat:
Cost of kwh supplied = 8.43 kwh x $0.10/kwh = $0.84
So the cost of the electricity needed to keep the tank hot over this 8.5 day vacation is a little less than a dollar for our system.
Turn Off the Water Heater:
If you turn off the water heater then its temperature slowly coasts down according to Newton's Law of Cooling. No electricity is consumed while you are away, but once you return and throw the circuit breaker on again the heating element turns on and stays on until the tank is back up to temperature.
The below graphic shows the rate of heat loss in btu/hr over 8.5 days for our 80 gallon R-16 hot water tank assuming the tank is shut off. As the temperature slowly declines during those 8.5 days the rate of heat loss also declines.
Water Heater Loss When Off
The equation for this theoretical heat loss curve can be constructed as follows.
Start with the equation for the temperature over time:
T(t) = 60 + 60e-0.00351 t
(This equation is derived in the Sample Calculation at the bottom of the Newton's Law of Cooling web page.)
Next consider the equation for heat loss through the insulation:
H(t) = A(T(t)-TA)/R
where
H = Heat loss in btu/hr
A = Area of tank walls = 37.5 ft2 for our tank
T(t) = Temp of the hot water as a function of time
TA = Air temperature surrounding tank = 60 F
R = 16 ft2hrF/btu
(This equation is described in more detail in the Hot Water Tank Heat Loss web page.)
Substituting T(t) into the H(t) equation and simplifying:
H(t) = 141e-0.00351 t
This equation states mathematically what the above graph shows visually.
The "area under the curve" of the graph gives the total heat lost in btus over the 8.5 days. All of this lost heat is replaced at the end of the vacation when the electric resistance heating element turns on after your throw the breaker on.
To compute the area under this curve we take the integral of the H(t) equation from time = 0 to 204 hours (8.5 days).
Cumulative heat loss = ∫0204141e-0.00351 tdt
= 141*(e-0.00351*204-1)/(-.00351)
= 20,540 btu
Divide by 3,412 btu/kwh in order to convert the btu loss to kwh supplied by the electric company when we turn the breaker back on:
kwh supplied = 20,540 btu / (3,412 btu/kwh)
= 6.02 kwh
Cost of kwh supplied = 6.02 kwh x $0.10/kwh = $0.60
Conclusion:
So if we leave our hot water heater on it costs about $.84 of electricity to keep the water hot while we are away on an 8.5 day vacation, and if we switch the hot water heater off it costs about $.60 of electricity to heat the water back up to temperature when we return. The net energy savings is about 2.4 kwh, which translates into a cost savings of about $.24.
How might these results vary for other households? If you have a poorly insulated water tank, or lots of heat loss from the pressure relief valve and the hot water pipe, then you might save two or three times as much from turning off the breaker.
Does this result depend on the length of the vacation? The longer the vacation, the more you save. The only case in which turning off the water heater would not save energy and money would be a vacation so short (a few hours?) that the thermostat would not have turned on to top off the heat anyway.
So is it worth shutting off the breaker, then shutting it on again for a savings of $0.24? My immediate reaction was "No way". But wait. I would certainly stoop down to pick up a quarter that I saw on the sidewalk. Just how much effort would I be willing to expend to retrieve a quarter? If I saw a quarter at the bottom of a floor heating vent I would be willing to spend 30 seconds to remove the vent, pick out the quarter, then replace the vent. Thirty seconds is about how much time it takes me to turn off the breaker, then turn it on again when I get back from vacation, so logically I should be willing to do this.
What is the effective pay rate for shutting the breaker off and on again? To make the calculations easier, assume a savings of $.25 for 30 seconds of effort. That's $.50 per minute, or $30 per hour. But that is an after-tax rate of pay, which might translate to $40 per hour before tax, or a taxable salary of about $80,000/year. So for that brief 30 seconds I'm earning an implied salary of $80,000/year. Isn't math wonderful?
Possible Downside of Turning Off the Water Heater During Vacation?
Could the additional thermal cycling due to turning off your water heater tank during vacation cause it to fail sooner? If so, then the cost and energy savings of shutting off the tank may be entirely swamped by early tank failure. Early tank failure means that the purchase and installation cost of the tank is spread over fewer years, so you pay more per year for the tank. Building a water heater tank takes energy, so early tank failure means the energy embedded in making the tank is spread over fewer years, so the embedded energy use per year is higher.
Of course, if the tank were poorly insulated, then early tank failure might be a net positive.
The analysis of tank life will require some further research...
This site is still under construction…to be continued…
You can e-mail me at support(@ sign goes here)leaningpinesoftware.com.
He basically says that shutting off an electric water heater will have negligible savings and does the math to prove it.
I think you have the same setup I have, tank-less coil on the oil fired furnace.
One of the least efficient ways to make DHW.
I the summer with no heating requirement, I was using about 1 gal/day for DHW
about $90/mo. I switched to an 80 gal electric which should only cost about $25/ mo to run. It is less because I have a solar and wood stove pre heater.
collector is offline   Reply With Quote
Old 12-12-10, 10:45 PM   #25
Our boiler has a 76 gallon water jacket, and once it's heated up in the morning,
it can provide enough hot water for our daily needs. And it's even hotter
if there is some solar assist.
When things are going well, and the weather isn't too crazy, we use 1/2 gallon of oil a day typically.
During sunny weather, the timed 1/2 hour burns are sometimes actually about 20 minutes.
At our last fill up we paid $2.59 a gallon, so it's costing us about $39.39 per month.
The oil burner is our main backup heat, so we need to keep it in good shape.
We need to be confident that it will power up and heat the house when we need it.
So, running it 1/2 hour a day is about the best way I know to insure it's good to go.
I can't really justify buying an electric hot water heater, just for summer use.
As you know, sometimes we don't get much of a summer.. Like in 2009..
Yeah? wasn't 2009 the year when global warming gave us an 800 hour summer?
Although, I would really love one of those heat-pump hw heaters for summer use..
It would keep the basement air dry too.
Since we use GSW (Geo-Slab-Warmth) downstairs, I think our basement
is a little too cold in the winter time for much heat to be pulled out of it's air.
I want to be able to go down to my shop, without wearing a parka..
Cheers,
Rich
Old 09-04-11, 08:45 PM   #26
Home heating oil is around $4 a gallon right now, but since we are timed to be only burning
0.5 gal per day, $2 for hot water isn't that bad of a deal. But Solar HW is starting to look better and better!
About 15 gallons a month for the 8 warmer months, comes to 240 gallons.
Our typical fill-up in the early fall is normally around 200 gallons..
But, that might be way off base this year. The last bill I can find shows a fill-up on 02-02-11.
I just looked at our 275 gallon tank, and it looks pretty full.. Just under 3/4 full.
It goes up to 7/8 after a fill-up, so it only looks like we've used about 40 gallons during the last 7 months.
Should have been more.. 214 days * 0.5 gallons is 107 gallons (of burn per the timer).
I wonder if the new lower water temp setting (140F) has the Aquastat
shutting off the burner after 10 or 15 minutes.?.
I'm never up at 7AM when the timer starts it up..
Anyways, I'm looking forward to only needing about 60 or 70 gallons for our fall fill-up..
Even with the 140F water, we've never had any problems taking showers
in the evenings. I think the solar PV assist might be bigger help at low water temps..
I'm working on boosting the PV power to the heater. Got the parts,
just need to do some soldering etc..
Old 09-07-11, 01:02 AM   #27
guerciofernando
Guest
Posts: n/a
You really dug out some of my memories. I remember getting the same experience. Thanks for your post.
Old 09-08-11, 02:13 AM   #28
ThomSjay
A timer might help a little. Even with good insulation, it might turn on at 1AM
to keep the tank hot all night.
If you could keep it from coming on between 10 PM & 5 AM, you might save some money.
With super good insulation, the temperature isn't going to drop very low over night,
when no one is using hot water.. So, the 5AM turn on won't have to be a long cycle.
If you both work, does the hot water need to be on while you are both at work?
No one using it, temperature pretty stable.?. Turn it off between 8AM & 4PM..?.
IMHO, working people need a 7-day timer with a weekend program..
Mine is made for old retired folks..
Here in my area of Ontario, Canada we are on a pay-per-time-of use program.
.... ... ..... summer ....... winter
7-11AM .... mid-peak ..... on-peak
11-5PM .... on-peak ..... mid-peak
5-9PM.... .. mid-peak ..... on-peak
9-7AM ..... . off-peak ..... off-peak
So, a timer has to be worked around this as well, which could be beneficial in that one could use power during the off-peak times.
Edited for clarity
ThomSjay is offline   Reply With Quote
Old 09-08-11, 08:37 AM   #29
"9-7AM off-peak off-peak".. That's a big window of low cost power!
Working people who shower before bedtime could have it come on at 9PM.
Those who shower in the AM could have it come on early in the AM and go off by 7AM.
(That would be my choice, being retired)..
Old 09-08-11, 10:00 AM   #30
strider3700
I'm curious what is the cost/kwh for off-peak, mid-peak, and on-peak. They are still debating going to smart meters here but when it happens I expect to see this type of scheme looked into.
boiler, timer, water heater