Old 03-30-09, 10:11 AM   #1
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 724 Times in 534 Posts
Default The Homemade Heat Pump Manifesto

Hello all,

Quote:
Why is it that people who can afford to have a Ground Source Heat Pump system don't really need the low cost of operation, and people who really need the low cost of Ground Source Heat Pump operation can't afford to have one?

It is to attempt to remedy this dilemma that I have done the work which is illustrated in the pages you are about to read.

Regards,

-AC_Hacker
(I have been working on this project since 2009, and I am having great success and fun, but have yet to find anyone on the web doing similar work.)

* * *

I live in an older small house (< 1000 square ft.) built in 1892. I am going through the whole house, meticulously insulating it with expanded poly styrene board. I tore off the lath & plaster, increased the thickness of my walls, and I'm layering in 6 inches of rigid foam into the walls, ceiling, and under the floor.

So I'm thinking ahead to a highly efficient heating system. As best as I can determine, a Ground Source Heat Pump (AKA: GSHP) running warm water through a thin (1.5 inch), radiant concrete floor is my best bet.

[* NOTE: Subsequent study suggests that a 'sandwich' style hydronic floor with close-spaced aluminum spreaders will be easier to build and at least as efficient as a thin suspended concrete floor, but that comes much later in the story. *]

I don't have much money, but I am resourceful and very stubborn.

I have found out that the approximate size of a heat pump I'll require is slightly under 12,000 BTU/hr. In HVAC speak they call 12,000 BTU/hr a 'Ton' of Air Conditioning. Your mileage may vary.

I have also found out that here in Western Oregon (Portland), a GSHP will require a borehole about 200 feet deep. It could also be two boreholes about 100 feet deep, etc... Again, your mileage may vary.

I also found out that heat pumps are classed as Air-to-Air, Water-to-Air, and Water-to-Water.

The kind I need is Water-to-Water. The kicker is, that the smallest I have been able to find is four ton (48,000 BTU/hr). So this means that in order to proceed with the project, I'll have to build my own heat pump. In HVAC, bigger is not better... just slightly smaller than big enough is best, economically speaking.

I have built a proof of concept unit that works. Here's a photo:


I built this unit last summer and did some testing. Here's a performance graph:


The COP is calculated for each measurement period, and changes quite a bit, but the overall COP is quite good.

So, is anyone interested in such a project? I have already built a prototype heat pump, it is working and I have tested it and the test results are very encouraging. I have attached photos and performance data at the end of this post.

I am now in the hole drilling phase. I built an earth auger, which would have worked really well in other parts of the country, but in Oregon, where I live the drilling is not so easy. I have increased the power of my auger 20X and I'm getting ready to dive back in.


A properly designed system as I'm describing should be able to operate at an efficiency of over 300%. My prototype has actually shown efficiency over 400%. In HVAC, efficiency can go over 100%, because the electrical energy that is input is not directly converted to heat, but is being used to move heat from one place to another. Strange but true.

So, there are four parts to the project:

0. Determining your heating load.
Free software is available on the web for this. It is also possible
to measure directly, the energy you are using. I have done both.

1. The Ground source loop field.
Here in Oregon, where I live, an 80 foot long, three foot wide,
by four foot deep trench containing about 300 feet of slinky
loops of plastic pipe, per Ton (12,000 BTU/hr) is required.
(* or *)
Two hundred feet of borehole per Ton is required.

2. The Heat Pump.
I have found that air conditioners and de-humidifiers can serve
as a starting place for DIY heat pumps. These can be had for
cheap to free. German children are using Propane gas as a
refrigerant for cooling CPUs so they can play video games faster.
What a concept!

3. The radiant floor system.
From all I have read, nothing beats PEX in concrete for efficiency.
This is seriously messy, but the technology involved is very
straight-forward.

I'd really like to get other people interested in this kind of project. Commercial units installed run $15,000 to $45,000 and up. I'm estimating that I can get mine going for under $2,000. Maybe under $1,000. So far I've spent about $400.

So, let me know if there's interest... I have loads and loads of information I'd like to share.

If we are not the people who can re-purpose pieces of junk that are now headed to the scrap yards and turn them into state-of-the-art high-efficiency home heating systems, who's going to do it?

Humbly Yours,

- AC_Hacker

P.S.: Here's a link to a PDF which will serve as a good overview to our project:



%%%%%%%%%%%%%%%%%%%%%%%%%%%%%%%[/CENTER]

Attached Thumbnails
Click image for larger version

Name:	HP_small.jpg
Views:	141936
Size:	22.5 KB
ID:	143   Click image for larger version

Name:	Gearmotor-Auger(small).jpg
Views:	128967
Size:	25.1 KB
ID:	145   Click image for larger version

Name:	performance-big.gif
Views:	139168
Size:	21.4 KB
ID:	221   Click image for larger version

Name:	Heat-Pump-Manual.jpg
Views:	123640
Size:	24.7 KB
ID:	1393   Click image for larger version

Name:	heat-pump-man-1.jpg
Views:	63077
Size:	70.5 KB
ID:	1395  


Last edited by AC_Hacker; 09-11-17 at 04:14 PM.. Reason: in-line images, better performance graph
AC_Hacker is offline   Reply With Quote
The Following 15 Users Say Thank You to AC_Hacker For This Useful Post:
BillG (07-19-16), castlusion (03-02-13), cia (08-11-10), greenhouse (03-11-12), IamIan (10-28-12), Jim_UK (07-28-14), Mobile Master Tech (06-08-13), phreich (07-02-14), rhizomatic (07-03-12), sparkchaser (11-16-11), Spiv (06-22-16), Tom Brown (07-17-19), vann (10-04-13), where2 (10-17-13)
Old 03-30-09, 10:25 AM   #2
Higgy
The Gardener
 
Join Date: Oct 2008
Location: Manitoba - Canada
Posts: 492
Thanks: 17
Thanked 8 Times in 7 Posts
Default

Welcome AC_Hacker. I don't know if my city would let us do this where I live in Canada, but I'm really interested in what you've written so far. So, for those of us who may not be able to do something like this, please still keep us posted on your status, or if you've got any other ideas you'd like to share.

Where did you learn to invent stuff like this? I wish I knew how to put things like this together, but I wouldn't know where to start. I really commend you for building things like this.
Higgy is offline   Reply With Quote
Old 03-30-09, 11:00 AM   #3
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 724 Times in 534 Posts
Default

Higgy,

There is tremendous interest in GSHP in Canada. I learned a large part of what I know about GSHP from websites provided by your fair government. Thank you!

> Where did you learn to invent stuff like this?

Lots of reading, being willing to try something, welcoming failure as also a learning moment.

I have friends that like to sail. I've noticed that their best stories are all about near-disasters. Of course, they DID live to tell the tale.

Best of Luck in your own adventures!

Cheers,

-AC_Hacker
AC_Hacker is offline   Reply With Quote
Old 03-30-09, 12:46 PM   #4
Daox
Administrator
 
Daox's Avatar
 
Join Date: Aug 2008
Location: Germantown, WI
Posts: 5,525
Thanks: 1,162
Thanked 374 Times in 305 Posts
Default

Welcome to the site AC Hacker. I'm in a similar boat. I have an older 1800s house that I'm just starting to remodel to get additional insulation into the walls (also thickening them for added insulation). I was also planning on going with in floor radiant heat. One room of the house already has it and it is simply wonderful. Its currently running off the hot water heater (blah). I was thinking about going with a conventional high efficiency boiler as a backup for solar hot water heat. But, your heat pump is very fascinating and I'm excited to see where it goes! Feel free to bounce any ideas around on here. We'll do what we can.
Daox is offline   Reply With Quote
The Following User Says Thank You to Daox For This Useful Post:
AC_Hacker (08-17-10)
Old 03-30-09, 02:09 PM   #5
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 724 Times in 534 Posts
Default

Daox,

Thanks for your post.

Commercial GSHP + hydronic floor heat setups in Europe are claiming COPs as high as 5.5.

If you have the cash to hire it all done by experts, save yourself some grief.

If you're on a limited budget, like I am, then the fun begins...

> But, your heat pump is very fascinating and I'm excited to see
> where it goes!

Is there some aspect of my project you'd like to know more about? There's so much to it, I hardly know where to begin...

Best Regards,

-AC_Hacker
AC_Hacker is offline   Reply With Quote
Old 03-31-09, 01:11 PM   #6
Daox
Administrator
 
Daox's Avatar
 
Join Date: Aug 2008
Location: Germantown, WI
Posts: 5,525
Thanks: 1,162
Thanked 374 Times in 305 Posts
Default

Oh gosh, I barely know where to start too haha. How about explaining your drilling rig there? Did you make it yourself? How large of a diameter does the hole need to be? I'm really not familiar with how you do these things.
Daox is offline   Reply With Quote
Old 03-31-09, 05:42 PM   #7
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 724 Times in 534 Posts
Default Drill Rig #1

The drilling rig...

I started some notes on the thread over at EcoModding you might want to look there too. At some point, I'll put everything on one thread, probably here. See the EcoModder thread:

The Homemade Heat Pump Manifesto... - Fuel Economy, Hypermiling, EcoModding News and Forum - EcoModder.com

But here's the story...

A local farmer told me that he was able to drill a 35 foot well by using 2 friends an 2 cases of beer (smart farmer).

I started by making a T-handle test drill, that used a water hose, connected by a swivel coupling.


auger-T-handle-test(small).jpg - This is my first test drill, only with a shorter piece of drill pipe, so you can see what's going on. I actually used a 6 ft. section of pipe and when the auger advanced about 5 ft., I added an additional section of pipe. I was able to advance about 13 feet in about 35 minutes. One problem I encountered was that the hose kept kinking, so I had to hold it up with one hand and I turned the auger with the other hand. So I was able to advance 13 feet with only one hand. The other, and more serious problem was that because of the high sand content of the soil, I was having cave-in problems. I didn't know what was causing it, I just knew that my auger was getting stuck and was very hard to pull out of the ground. Later I would discover that drilling mud would solve the cave-in problem.


auger-T-handle-test_upper-detail(small).jpg - This is a detail of the swivel end of the auger. The swivel adapter is not eactly the same as 3/4 pipe thread, but by loading lots of teflon tape onto the threads, I got a satisfactory seal.


auger-T-handle-test_lower-detail(small).jpg - this is a detail of the business end of the auger. The water gushes through the pipe and flushes out the drill-cuttings. I have come to understand that the water is definitely part of the tool. It contributes more to the advancement of the drill than any effort on my part.

I live at the top of an 80-foot bluff and look down at a local river. I did notice that I was hitting rocks at about 12 to 13 feet. What I didn't realize at the time, but have come to know that every well driller understands very well, is that 14,000 years ago, an ancient flood deposited about a foot of clay mixed with basalt river gravel which over fourteen millenia has consolidated in what the locals know as 'hardpan'... it's tough stuff.

%%%%%%%%%%%%%%%%%%%%%%%%%%%%%%%%%%%%%%%%
AC_Hacker's Update, Sept 6, 2009:
At the time this was written, I thought I had, indeed hit hardpan. Later work, using tools that didn't obscure the nature of the soil I was digging through, revealed that I had actually hit an area of fist-sized rocks left from a 10,000 year old geological event. I developed a tool (the "steel claw"), shown later, that enabled me to remove the rocks and advance town to a depth of 17 feet where there was very wet, coarse black sand, very good for Ground Source Heat Pump work and worth the extra digging. At that depth, I was actually able to look down boreholes and the see the hardpan layer.
%%%%%%%%%%%%%%%%%%%%%%%%%%%%%%%%%%%%%%%%

You may not have anything like this where you live. In fact, a couple of blocks from here, thing might be much better, or much worse.


auger-base(small).jpg - This is the base of the gearmotor auger I put together. Based on my hand-drilling experience, I figured a small motor would do the job, so I got a 1/4 HP 25:1 permanent magnet gearmotor off ebay for $70. A 1/4 HP motor doesn't require a huge amount of structure to support and control, so fabrication was pretty easy.


auger-head(small).jpg - This is the gear motor head. I fabbed an 'L' bracket for the motor and used a 2" square tube for the vertical, and a close-fitting 2" inside receiver tube welded to the L bracket. it slides up & down well and doesn't have too much slop. You can see the hand cranked wench to raise and lower the gearmotor head. It's not optimum, but it works OK.

(By the way, I'm a terrible welder. I have a stick rig, which I have tried repeatedly to master, but it has won every time. So, I bought a crappy little wire-feed welder for $100 and it has worked wonders. Highly recommended.)

The gearmotor I chose is permanent magnet, so I can reverse the direction to unscrew pipe... very handy. I also have a bench test variac that I use to control speed. Works great.

Next post will detail the auger-head swivel... it's surprisingly important.

Best regards,

AC_Hacker
Attached Thumbnails
Click image for larger version

Name:	auger-T-handle-test(small).jpg
Views:	139703
Size:	15.8 KB
ID:	146   Click image for larger version

Name:	auger-T-handle-test_upper-detail(small).jpg
Views:	131366
Size:	89.5 KB
ID:	147   Click image for larger version

Name:	auger-T-handle-test_lower-detail(small).jpg
Views:	142108
Size:	85.8 KB
ID:	148   Click image for larger version

Name:	auger-base(small).jpg
Views:	125897
Size:	37.0 KB
ID:	149   Click image for larger version

Name:	auger-head(small).jpg
Views:	134389
Size:	41.2 KB
ID:	150  


Last edited by AC_Hacker; 09-06-09 at 11:59 AM.. Reason: AC_Hacker's Update, Sept 6, 2009
AC_Hacker is offline   Reply With Quote
The Following User Says Thank You to AC_Hacker For This Useful Post:
cia (08-12-10)
Old 04-01-09, 12:40 AM   #8
metroschultz
nail bender
 
metroschultz's Avatar
 
Join Date: Sep 2008
Posts: 9
Thanks: 0
Thanked 0 Times in 0 Posts
Send a message via AIM to metroschultz
Default

Here on the ocean front the HVAC companies are starting to sell Geo Thermal systems that are really pump and dump units.
They drill your back yard to around 150 foot and pump the water to a storage tank that is used to pre-cool or pre-heat your HVAC unit.
Ground water here flows out at around 55 degrees year round so this works really well in the summer and reasonably well in the winter. (We seldom see below 50 degree days and below 30 degree nights.)
Unbelievably expensive
Starting at $20,000 for the simplest of units.
There are , however, quite a few of them in my neighborhood. (The developer had a deal with the HVAC installers and the prices were financed into the original purchase price)
I have often wondered how hard it would be to make something like that on my own.
I would just bury some 55 gallon plastic drums in the yard about 50 foot down and use that as my storage facility, (removes them from the house and reduces the need for insulation) then move the water to the furnace as necessary.
So that being said, I am very interested in your project and will keep watching for stuff I think I might be able to implement.
S.
__________________
Electricity is really just organized lightning.

To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
metroschultz is offline   Reply With Quote
Old 04-01-09, 03:16 AM   #9
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 724 Times in 534 Posts
Default

metroschultz,

Pump & dump? I'm not so sure I follow what you mean...

I see this term in geothermal usually meaning that an 'open loop' system is being used, and water is being drawn from the ground or river or other water source then heat is extracted and the water is then pumped on to a lake or a river or a different well where it is absorbed back into the earth.

Is this how you mean the process works?

Regards,

-AC_Hacker
AC_Hacker is offline   Reply With Quote
Old 04-10-09, 10:15 PM   #10
metroschultz
nail bender
 
metroschultz's Avatar
 
Join Date: Sep 2008
Posts: 9
Thanks: 0
Thanked 0 Times in 0 Posts
Send a message via AIM to metroschultz
Default

Quote:
Originally Posted by AC_Hacker View Post
metroschultz,

Pump & dump? I'm not so sure I follow what you mean...

I see this term in geothermal usually meaning that an 'open loop' system is being used, and water is being drawn from the ground or river or other water source then heat is extracted and the water is then pumped on to a lake or a river or a different well where it is absorbed back into the earth.

Is this how you mean the process works?

Regards,

-AC_Hacker
Yes,
That is exactly what they do.
Pump fromthe ground water table (to an underground storage tank)
and dump back to the water table (through a leeching field).
Several of the units in my neighborhood have had their leeching field sink. (sinking field = mucho denero)
We live near the ocean and the water table is just below the surface..
__________________
Electricity is really just organized lightning.

To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
metroschultz is offline   Reply With Quote
Reply


Tags
air conditioner, diy, gshp, heat pump, homemade


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 02:07 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design