Newbie question regarding expansion valve
I understand the basic heat pump cycle and all of the components in the system (compressor, condenser, expansion valve, evaporator). I also understand how the basic cycle can be "turned around" (the evaporator turned into the condenser and vice versa) with some valves. My question has to do with the expansion valve.
Where, in a heat pump system, is the expansion valve and capillary tube placed relative to the various valves and other system components ? Pictures and diagrams would be helpful. |
10-31-14, 11:02 PM | #2 |
Apprentice EcoRenovator
Join Date: Oct 2014
Location: SE MI
Posts: 105
Thanks: 3
Thanked 12 Times in 9 Posts
|
|
11-01-14, 05:31 AM | #3 |
Supreme EcoRenovator
|
From yhe sticky:
Basic cycle geo heat pump |
The Following User Says Thank You to jeff5may For This Useful Post: | theoldwizard1 (11-01-14) |
11-01-14, 08:56 AM | #4 |
Apprentice EcoRenovator
Join Date: Oct 2014
Location: SE MI
Posts: 105
Thanks: 3
Thanked 12 Times in 9 Posts
|
The problem with those diagrams is that they only show the heat pump working in one direction. I knew there had to be some trick with the TXV for the heat pump to work in both directions, like the fact that there are 2 in my diagram, paralleled by one way check valves.
I am certain that there is "more than one way to skin the cat", but the solution I found looks pretty simple. |
11-01-14, 09:12 AM | #5 |
Apprentice EcoRenovator
Join Date: Oct 2014
Location: SE MI
Posts: 105
Thanks: 3
Thanked 12 Times in 9 Posts
|
Yet some more images
|
11-01-14, 10:39 AM | #6 |
Supreme EcoRenovator
|
The two expansion valves in the diagram can be switched out for a single cap tube or electronic expansion valve. The way of the diagram is the way of the old school split system. The idea behind the rig is you can swap either side of the unit with out the other. The check valves shunting the expansion valves are not there in a straight ac split unit.
|
The Following User Says Thank You to jeff5may For This Useful Post: | theoldwizard1 (11-01-14) |
11-01-14, 11:43 AM | #7 | ||
Apprentice EcoRenovator
Join Date: Oct 2014
Location: SE MI
Posts: 105
Thanks: 3
Thanked 12 Times in 9 Posts
|
Quote:
Quote:
Can you find a diagram showing only 1 TXV/EXV ? Last edited by theoldwizard1; 11-01-14 at 11:47 AM.. |
||
11-01-14, 12:13 PM | #8 |
Supreme EcoRenovator
Join Date: Oct 2008
Location: Austin, TX
Posts: 1,154
Thanks: 14
Thanked 257 Times in 241 Posts
|
In theory, it's possible to make a TXV that will work both ways. In practice, I don't know of any TXVs that are designed to work both ways.
That said, TXVs are cheap on the surplus market.
__________________
To my surprise, shortly after Naomi Wu gave me a bit of fame for making good use of solar power, Allie Moore got really jealous of her... |
11-01-14, 01:43 PM | #9 |
Apprentice EcoRenovator
Join Date: Oct 2014
Location: SE MI
Posts: 105
Thanks: 3
Thanked 12 Times in 9 Posts
|
|
11-01-14, 01:58 PM | #10 | |
Supreme EcoRenovator
|
Quote:
|
|
|
|