Old 03-22-13, 08:37 PM   #1
marx290
Vapor Compression Goon
 
marx290's Avatar
 
Join Date: Mar 2013
Location: Portland, OR
Posts: 63
Thanks: 11
Thanked 22 Times in 11 Posts
Send a message via Yahoo to marx290
Question Heat Pump TXV with 80 Degree Evaporator?

Ok, so I've never sized a thermostatic expansion valve for system, but I know how important it is to select the right one. Too small and the evaporator might starve, too large and it hunts to feed the appropriate amount of refrigerant. Other things like whether the TXV is internally or externally equalized, the type and placement of the sensing bulb, the pressure drop across the orifice, the evaporator itself, the type of refrigerant, so on and so forth. There are charts and engineering tables to help select the right valve and of course the knowledge and experience of seasoned technicians to go on.

The system I have in mind isn't really specific, but the general idea is a greywater sourced heat pump water heater. So, as far as the capacity of the system, compressor size and even the refrigerant used aren't really important to my question.

If a heat pump designed to recover heat from 100 degree F drain water and supply it to fresh, clean water at 120 degrees F; is there a thermostatic expansion valve capable of regulating superheat in an evaporator with a operating temperature range of 60-90 degrees F?

I'm wondering if TXVs designed for air to air or ground source heat pumps be able to properly feed and evaporator at those temperatures. Would a TXV work properly with a smaller pressure drop between the condensing pressure and suction? Are their any applications for a valve like this that there would exist sizing tables in this range?

This isn't something I'm planning on building anytime soon, just daydreaming.

__________________

To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
marx290 is offline   Reply With Quote
Old 03-24-13, 02:10 AM   #2
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,431
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

I believe what you are describing is known as a subcooling valve. It works the opposite way a normal TXV does. When the temperature is high, or temps are very close on both sides of the compressor, head pressure controls do a better job than suction pressure controls.

A Txv-metered system basically regulates the amount of liquid in the evaporator by maintaining constant superheat. When the system is started, the txv begins to open at a set pressure. As the evaporator temp drops, the txv responds by choking the flow to pull more heat out. This operation continues down to the lower limit of the valve. Below its limit, the valve acts on spring pressure, just like at start-up.

With subcooling valve controlled systems, the valve controls the amount of liquid in the condenser by maintaining constant subcooling. The evaporator is flooded, and maintains zero superheat. Mikesolar is in the process of building one of these, based on the design of a Westinghouse Hi-re-li heat pump from the 60's. Westinghouse was later bought by York, and sold the rights to this design to Paul Mueller. Mueller continues to make these units today, still based on the HiReLi design of 50 years ago. They renamed it the HiPerform and claim it to be the most energy efficient system in the world.

Last edited by jeff5may; 03-24-13 at 02:18 AM..
jeff5may is offline   Reply With Quote
Old 03-24-13, 02:48 AM   #3
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,431
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

Here's a brochure on the HiPerform unit, made for a flooded barrel chiller:
http://www.muel.com/pdfs/Literature/...rHiPerForm.pdf
A Sporlan Tech brief describing the problem you speak of:
http://sporlanonline.com/literature/90/90-198.pdf
Instead of using a subcooling valve, the sporlan guys do things the engineer way and the resulting kludge needs lots of controls to work.
jeff5may is offline   Reply With Quote
Old 03-24-13, 06:32 AM   #4
Mikesolar
Master EcoRenovator
 
Mikesolar's Avatar
 
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
Default

The problem with Mueller is that they bought it for their own use and not to resell, AFAIK. The guy I work with had an old relationship with the Sporlan guys and managed to secure some. I don't know if he can still get them but the last time he had to buy 100 or something.
Mikesolar is offline   Reply With Quote
Old 03-24-13, 10:33 AM   #5
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,431
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

After browsing the mueller website, I am convinced I would never be able to afford one of their units unless it was found in the scrap yard. High performance, high end industrial/commercial stuff aimed at bulk processing. Think dairy, fine wine/beer, big pharma, biotech. Set it and forget it stuff that don't break down. Brewmaster Bill has more important priorities than saving money on his wort chiller. Think Jurassic Park.
jeff5may is offline   Reply With Quote
Old 03-24-13, 12:36 PM   #6
marx290
Vapor Compression Goon
 
marx290's Avatar
 
Join Date: Mar 2013
Location: Portland, OR
Posts: 63
Thanks: 11
Thanked 22 Times in 11 Posts
Send a message via Yahoo to marx290
Default Flooded Evaporator - Low Side Float

That's kind of what I was afraid of. From what I read, TXVs are a really great way to regulate superheat in an evaporator, keep it in a flooded state and ensure high vapor density back to the compressor. But, there is that pesky issue of a minimum pressure drop across the valve to supply sufficient refrigerant for the cooling needs.

I read that Sporlan article on controlling head pressure to keep steady TXV operation. Maintaining a minimum condenser pressure needed for proper TXV operation is quite necessary, I'm sure; and partially flooding the condenser to do it is genius, I think. Much better and more consistent than cycling a fan or pump. What alarms me, is the intentional adulteration of one part of a system as a response to the limits of another.

I'm not an engineer, and it would probably be different if I were made responsible for improving the performance or reduce power consumption of these systems. I won't say much more about the TXV. It can be an extraordinarily good at flooding a dry type evaporator if it is selected right.

What does anybody know about Gravity Flooded Evaporators with Low Side Float?
__________________

To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
marx290 is offline   Reply With Quote
Old 03-24-13, 07:52 PM   #7
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,431
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

I found a source for the mystery valve in question!

Hamby Dairy Supply :: Milk Cooling Tanks, Plate Coolers & FreeHeaters :: Replacement Parts for Milk Tanks :: Mueller :: Refrigeration components, temperature controls & sensors :: SubCool Valve 3 HP OH HIPERFORM

Not super cheap like txv's on ebay, but still within tinkering budget. I will be test driving one of these in the not too distant future.
jeff5may is offline   Reply With Quote
Old 03-25-13, 04:59 AM   #8
Mikesolar
Master EcoRenovator
 
Mikesolar's Avatar
 
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
Default

Well, hit me on the head and call me shorty.........ya found one. Let the games begin.
Mikesolar is offline   Reply With Quote
Old 04-09-13, 02:31 PM   #9
jdrimm
Lurking Renovator
 
Join Date: Apr 2013
Location: KY, USA (deployed to Djibouti, Africa)
Posts: 8
Thanks: 3
Thanked 0 Times in 0 Posts
Default

Mueller is a big name in dairy equipment, you might try farm auctions or even asking the local extension office about dairy farms that have ceased operations. Local dairy equipment suppliers might have bad chillers hanging around, too.
jdrimm is offline   Reply With Quote
Old 04-09-13, 08:22 PM   #10
NiHaoMike
Supreme EcoRenovator
 
NiHaoMike's Avatar
 
Join Date: Oct 2008
Location: Austin, TX
Posts: 1,154
Thanks: 14
Thanked 257 Times in 241 Posts
Default

Quote:
Originally Posted by marx290 View Post
That's kind of what I was afraid of. From what I read, TXVs are a really great way to regulate superheat in an evaporator, keep it in a flooded state and ensure high vapor density back to the compressor. But, there is that pesky issue of a minimum pressure drop across the valve to supply sufficient refrigerant for the cooling needs.
Use an orifice a step larger (such as a 1.5 ton one for a 1 ton system) and it will flow more. But it then might not operate properly at high condensing temperature. Another possible solution is to have a cap tube in parallel with the TXV, switched in with a solenoid valve on the low side

__________________
To my surprise, shortly after Naomi Wu gave me a bit of fame for making good use of solar power, Allie Moore got really jealous of her...
NiHaoMike is offline   Reply With Quote
Reply



Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 05:37 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design